Its a 'red herring' for the UK (unless you just fancy looking at the weather onscreen and happen to have one of the hometronic sensors) - but for other regions outside weather function is useful for other countries like the German market where boiler control is directly performed this way - with no radiator demand and different system altogether. Thanks for posting up my previous post on this.getconnected.honeywell.com | I work for Honeywell. Any posts I make are purely to help if I can. Any personal views expressed are my own
Comment
-
-
-
Originally posted by top brake View PostHere's what the carbon trust say about optimisation
https://www.carbontrust.com/media/13...rt_control.pdf
Comment
-
-
Originally posted by G4RHL View PostUseful article. I note it talks of an external sensor. Do Honeywell do an external sensor that links wirelessly to Evohome?
Comment
-
-
Originally posted by jonstatt View PostThey do, and the system will even let you link it in, but as Rameses says above, it does absolutely nothing for the EVOHOME system for UK users.
Anyway... since I'm using the R8810 OpenTherm boiler gateway, I'm sure my EvoHome is asking my boiler for this parameter value - and my boiler answers with the actual reading. I might try checking again, but I did it a few days ago and I couldn't find an option in the installer menu to show external temperature.
EvoHome asking my boiler the temperature makes me think it's using it to some point...
Comment
-
-
Optimisation.
Continuing a check on what is happening this morning I monitored what happens in my Living Room. It is set to be 20c at 06:40 but I have done that on the basis that with optimisation on it will come on around 05:40 when I will be using the room. The following was recorded:
Heating came on at 05:40, TRV temp 16, thermometer temp at desk height 16.5
05:50 TRV read 17, thermometer 17.5
06:09 TRV 18, thermometer 18
06:18 TRV adjusted self, heating went off, initially TRV read 19 for short period then 20, pump still on
06:29 TRV reading 20 heating off, pump off, thermometer reading 19.5
06:40 TRV reading 21.5, thermometer 20
It therefore took 49 minutes to lift the room temperature from 16 to 20. It seems to show the system making allowances for the fact heat is still coming through to be utilised and switching off because of that. Indeed this is evident by the fact that it shut off the boiler at 06:29 but at 06:40 the temperature was 21.5 although it should have been 20.
On this basis optimisation should have brought the heating on at 05:51 and not 05:40 but I always know it comes on 60 minutes before hence the settings I have. Optimisation is set to come on no sooner than one hour before
What was interesting is that although I had a separate thermometer alongside it was an HR92 which is not bound, just left there whilst we complete the conservatory, throughout it consistently read the same as the TRV on the radiator.
So yes, optimisation works but it is not that efficient for it comes on 11 minutes sooner but that might be part of the inbuilt tolerances.
Comment
-
-
If you would use a simple old Honeywell Round, it would probably be easily able to heat the room to exactly 20 instead of over-shooting to 21.5. Because, in my experience, the over-10-year-old Honeywell Round acts smarter than the new Evohome system. Even though it's 20x cheaper too.
Comment
-
-
Test result of the heating behavior of the Honeywell Round Wireless (connected to my boiler through BDR91 relay). I've been monitoring the temperature reading on the Round Wireless and on my own thermometer. Also, I've been monitoring the BDR91 and boiler through a webcam.
Setpoint was set to 17.5.
It takes about 1.5 hours to heat up the room from (according to my own thermometer): 17.1 to 18.2 degrees, it's requesting heat for a minute or two or three from the boiler every 10 minutes. The closer it gets to 18.2, the shorter the requests for heat become.
Then, after reaching 18.2 it totally stops requesting heat for about 2 hours, during wich the room cools down to 17.1 again.
Then it starts requesting heat again, every 10 minutes, taking about 1.5 hours to reach 18.2 again.
Then it cools down again to 17.1, taking 2 hours.
Then it starts heating up to 18.2 again, taking 1.5 hours.
And so forth and so forth... During all this, the Round Wireless is continuously showing a reading of 17.5.
So: pretty bad behavior, just like when using Evohome. Temperature going up and down by at least 1 degree. Heating going on for 1.5 hours, and then off for 2 hours. Etc. etc. Very uncomfortable.
Again: when using a simple old skool Honeywell Round on/off, the temperature stays way more constant, to a precision of about 0.1 degree up/down. The old Round on/off skips a 10-minute heating cycle sometimes. Sometimes even 2 in a row. But it never stays off for 2 hours. And it never goes go way above setpoint. It's near perfect. If only it could do schedules and zoning...Last edited by erik; 1 March 2015, 12:20 AM.
Comment
-
-
I repeated the check I did yesterday and posted above, this morning. The boiler fired up exactly one hour before the set point. Start temperature was 16c and it took the same time to get up to temperature, with similar readings. I note that whilst the TRV reads 21.5 when the setting is 20, and the boiler is not then on, the actual temperature at living height, as opposed to virtually floor level, is 20C. Am happy with that. Indeed the room is prefectly comfortable within 10 minutes of the system firing up. The set point for 08:00 is 18C, it is now 07:24 and I note optimisation has checked in, the app reads 18C in readiness obviously happy with what heat is now in the system.
Also nice last night when out for a meal to turn up the heat in the bedroom (now that sounds interesting!) from the restaurant for when I get home.
Still puzzled about balancing and the need for it. Without Evohome I can understand it, but if in any event all radiators heat up at similar times and/or if only one zone wants heat, is it that important?
Comment
-
-
Originally posted by G4RHL View PostI repeated the check I did yesterday and posted above, this morning. The boiler fired up exactly one hour before the set point. Start temperature was 16c and it took the same time to get up to temperature, with similar readings. I note that whilst the TRV reads 21.5 when the setting is 20, and the boiler is not then on, the actual temperature at living height, as opposed to virtually floor level, is 20C. Am happy with that. Indeed the room is prefectly comfortable within 10 minutes of the system firing up. The set point for 08:00 is 18C, it is now 07:24 and I note optimisation has checked in, the app reads 18C in readiness obviously happy with what heat is now in the system.
Also nice last night when out for a meal to turn up the heat in the bedroom (now that sounds interesting!) from the restaurant for when I get home.
Still puzzled about balancing and the need for it. Without Evohome I can understand it, but if in any event all radiators heat up at similar times and/or if only one zone wants heat, is it that important?
Comment
-
-
Originally posted by jonstatt View PostYou mentioned that the heating was coming on exactly 1 hour before. This makes me wonder what would happen if you had the maximum optimisation time set to 3 hours. The fact it comes on "exactly" means in it's own little ideal world, it would possible come on even sooner!! (I.e. it's hitting the hard limit you set of 1 hour) Would you try this to satisfy my curiosity? If it comes on at 3 hours, then something is really wrong here.
Comment
-
-
Originally posted by G4RHL View PostI repeated the check I did yesterday and posted above, this morning. The boiler fired up exactly one hour before the set point. Start temperature was 16c and it took the same time to get up to temperature, with similar readings. I note that whilst the TRV reads 21.5 when the setting is 20, and the boiler is not then on, the actual temperature at living height, as opposed to virtually floor level, is 20C. Am happy with that. Indeed the room is prefectly comfortable within 10 minutes of the system firing up. The set point for 08:00 is 18C, it is now 07:24 and I note optimisation has checked in, the app reads 18C in readiness obviously happy with what heat is now in the system.
Also nice last night when out for a meal to turn up the heat in the bedroom (now that sounds interesting!) from the restaurant for when I get home.
Still puzzled about balancing and the need for it. Without Evohome I can understand it, but if in any event all radiators heat up at similar times and/or if only one zone wants heat, is it that important?
The optimal system is one that is correctly sized and commissioned. Controls can work all sorts of witchcraft these days, controlling systems to accuracy and stability levels skin to industrial process control.
But putting it simply why make the controls work harder than they need to? All you will accomplish is to make the overall control less responsive and stable. And wear out batteries in HR92
Hope this helps give a perspective from a controls engineer and a practical real world view?I work for Resideo, posts are personal and my own views.