EvoHome: do I need to leave a single radiator in my house without HR92 or TRV?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts
  • top brake
    Automated Home Legend
    • Feb 2015
    • 837

    #16
    No problem
    I work for Resideo, posts are personal and my own views.

    Comment

    • The EVOHOME Shop
      Site Sponsor
      • Dec 2014
      • 483

      #17
      Originally posted by johnny View Post
      Great thanks for the help, it looks like I am slowly getting to the bottom of think thanks to you all.

      Final questions:

      (i) if I do install an external bypass in a combi boiler system without any water pumps, should I go for the Honeywell DU144 (or DU145), or should I go for the Honeywell V4044C? All these models are listed on the Evohome shop website.

      (ii) if I use a 'radiator bypass' with no TRV, say the radiator in the kitchen near where the boiler is located, does this mean that when I turn on a bedroom TRV at night, the kitchen radiator will heat up needlessly? Also, in this set up, how do I ensure the kitchen radiator turns itself on when I want it to? Could I use the internal thermostat of the EvoHome controller to do this?
      Pump over-run at the end of heating demand is something that needs to be seriously considered, especially on boilers with fully modulating pumps. Worcester Bosch offered guidance on this quite some time ago, hence we sell the V4044C1288 valve - https://www.worcester-bosch.co.uk/su...ownload/TB0074

      A sprung loaded automatic bypass valve (such as the DU144 or DU145) will not provide a pump over-run bypass solution due to the very nature of a modulating pumps (now common place due to ErP) and the boiler will very likely overheat should a 'bypass circuit' not be created.

      Comment

      • erik
        Automated Home Guru
        • Feb 2015
        • 244

        #18
        Good expert reply and help!

        Comment

        • johnny
          Automated Home Lurker
          • Oct 2015
          • 6

          #19
          Originally posted by The EVOHOME Shop View Post
          Pump over-run at the end of heating demand is something that needs to be seriously considered, especially on boilers with fully modulating pumps. Worcester Bosch offered guidance on this quite some time ago, hence we sell the V4044C1288 valve - https://www.worcester-bosch.co.uk/su...ownload/TB0074

          A sprung loaded automatic bypass valve (such as the DU144 or DU145) will not provide a pump over-run bypass solution due to the very nature of a modulating pumps (now common place due to ErP) and the boiler will very likely overheat should a 'bypass circuit' not be created.
          Many thanks for the advice. Would you happen to know if a Vaillant Ecotec plus 832 (which is a modern but small domestic boiler) has a fully modulating pump requiring a V4044C valve? Reading the Vaillant literature online, I was under the impression that only the Vaillant commercial range and the Valliant Ecotec Exclusive range were fitted with those fully modulating pumps, but it is quite likely that I didn't get this right.

          Great thanks
          Johnny

          Comment

          • top brake
            Automated Home Legend
            • Feb 2015
            • 837

            #20
            Very interesting

            Is this advice unique to WB?

            Originally posted by The EVOHOME Shop View Post
            Pump over-run at the end of heating demand is something that needs to be seriously considered, especially on boilers with fully modulating pumps. Worcester Bosch offered guidance on this quite some time ago, hence we sell the V4044C1288 valve - https://www.worcester-bosch.co.uk/su...ownload/TB0074

            A sprung loaded automatic bypass valve (such as the DU144 or DU145) will not provide a pump over-run bypass solution due to the very nature of a modulating pumps (now common place due to ErP) and the boiler will very likely overheat should a 'bypass circuit' not be created.
            I work for Resideo, posts are personal and my own views.

            Comment

            • The EVOHOME Shop
              Site Sponsor
              • Dec 2014
              • 483

              #21
              Originally posted by top brake View Post
              Very interesting

              Is this advice unique to WB?
              I am unsure if it is unique to WB but they obviously had issues with modulating pumps and S Plan at one point in time and this was their best solution.

              Comment

              • Jom
                Automated Home Jr Member
                • Aug 2015
                • 23

                #22
                Glad now that when having a new WB gas boiler and Evohome installed a few weeks ago that I left two small radiators and heated towel rail in the bathrooms without HR92's to keep down costs.

                Comment

                • emmeesse68
                  Automated Home Guru
                  • Dec 2014
                  • 103

                  #23
                  An open radiator could be a good thing, sure. Anyway, as I was saying before, my boiler gets loud when the embedded bypass kicks in, but the boiler itself shows there's a kind of overheating protection, so I don't think it could get damaged by overheating, because it just shuts the burner off and turns on fans and pumps to cool down the heat exchanger.

                  I guess most modern boilers show similar behaviour, so there's no big risk - except for the noise effects.

                  Yet I think my EvoHome is calling for heat when all valves are shut, thus hitting against the embedded bypass, and this, in my opinion, is a programming fault. If the EvoHome decides, based on the heating curve, that it's time to heat up some radiator, the procedure should be:
                  1 - OPEN some valve
                  2 - FIRE the boiler
                  3 - When enough heat has been provided, STOP the boiler
                  4 - WAIT a few minutes for the boiler overrun to finish
                  5 - CLOSE the valve


                  What I observe is different. Valves and boiler are driven independently, so sometimes the boiler is fired when all valves are actually shut. An open radiator or a spring-loaded bypass could take care of this but, computer-wise speaking... if you can fix it in software, what's the point of changing the hardware?
                  Last edited by emmeesse68; 30 October 2015, 09:51 AM.

                  Comment

                  • erik
                    Automated Home Guru
                    • Feb 2015
                    • 244

                    #24
                    Agree with emmeesse68. Is should be possible to make sure the boiler isn't fired anymore by the boiler-relay when all valves completed closing. And an extra safety margin of a minute or 2 to accomodate overrun should be built in as well.

                    Monitoring the relay and hr92-valve behavior shows that it's not currently the case. Especially right after turning off heating for the entire house. The hr92s all close pretty quickly afterwards, but the boiler relay might fire again 1 more time a few minutes later.

                    And then of course there's the seperate issue of HR92s fully closing water access to the radiator even when they're actually on 30% and shouldn't be closing it fully. I've seen this happening even on Honeywell-radiator-heads (V2000), both with the full-option on and off.
                    Last edited by erik; 30 October 2015, 08:39 AM.

                    Comment

                    • MrB
                      Automated Home Sr Member
                      • Oct 2015
                      • 80

                      #25
                      Just to add my tuppence here as just been through this.

                      I have a new W.B. Greenstar 30cdi (regular), Grundfos Alpha2L Pump (controlled by Boiler) and a Honeywell DU144 Automatic Bypass Valve (ABV).

                      Firstly, an ABV is now a Building Regs requirement. Cannot use a manual gate valve to restrict flow.

                      The Boiler, Pump and ABV all have to work as a team to make sure you have a small circulation loop for the boiler to lose heat at minimum flow rate, but not for the ABV to open too easily.

                      The Grundfos has 3 operating modes: Fixed Speed (the standarard plumber I,II,III), Constant Pressure (CP1,CP2) and Proportional Pressure (PP1,PP2).

                      The only ones that work with the W.B. and the ABV are CP1 and CP2 - they allow the ABV to open when all the 2-Way Valves are closed because the pressure from the pump, that is normally directed to the HW or CH, is now forced down the ABV pipe. The others either don't or are not reliable and the Grundfos tech manuals also advise against. Most definitely must not use PP1 or PP2 Proportionals as the pump slows down when the 2-way valves are closed and that means the ABV won't open.

                      Works very well here. It was all easy to check just by holding the pipes and switching everything in different permutations and feeling the temperature differences in all the pipes as the different valves opened and closed.

                      Comment

                      • electronicsuk
                        Automated Home Sr Member
                        • Sep 2015
                        • 55

                        #26
                        Originally posted by emmeesse68 View Post
                        What I observe is different. Valves and boiler are driven independently, so sometimes the boiler is fired when all valves are actually shut. An open radiator or a spring-loaded bypass could take care of this but, computer-wise speaking... if you can fix it in software, what's the point of changing the hardware?
                        Sounds good in principle, but I'm not sure it would work for everybody. For example, it's could have a nasty impact on temperature overshoot, especially for anyone with oversized radiators and/or a large system with a lot of water volume in the pipework. I'm not even sure it could be done without changes to the evo hardware - it doesn't seem to me that the communication between valves and the controller is regular enough.

                        Comment

                        • emmeesse68
                          Automated Home Guru
                          • Dec 2014
                          • 103

                          #27
                          Originally posted by electronicsuk View Post
                          Sounds good in principle, but I'm not sure it would work for everybody. For example, it's could have a nasty impact on temperature overshoot, especially for anyone with oversized radiators and/or a large system with a lot of water volume in the pipework. I'm not even sure it could be done without changes to the evo hardware - it doesn't seem to me that the communication between valves and the controller is regular enough.
                          Don't think letting the boiler overrun circulate through a radiator (when the flame is off) would cause temperature overshooting. Especially when large radiators are involved, hot water would already be in the radiators when the flame stops, regardless the valves being open or closed... thus overshooting in any case. I think the Evohome Learning technology is supposed to take care of this, after it learns the heating cuve...

                          Comment

                          • erik
                            Automated Home Guru
                            • Feb 2015
                            • 244

                            #28
                            Firing the boiler when valves are shut is never good practice. It has nothing to do with preventing overshoot either. If an overshoot is about to happen, just don't fire the boiler anymore.

                            Comment

                            Working...
                            X