Bed 3: 06:00 15C, 09:30 15C, 17:30 15C, 22:30 15C
Bed 4: 07:00 20C, 09:30 16C, 17:30 16C, 22:30 16C
Bed 4 is behaving much as I expect it. I don't understand why Bed 3 isn't subject to WWS.
Attachment 1541
Here’s an odd screen. Not really sure what to make of it.
It makes sense that leve’s room is heating up, and the radiator was hot, but the Setpoint is showing as 5c and cwb icon as well? The Setpoint should actually be 20c.
The other 5c rooms - no idea. No open window icon and not Wws as no off icon. No idea why they are showing the economy symbol either - they are not scheduled to have been heating so no reason for optimal stop to have activated, if anything they might have been in warm up mode.
Andy, I don't understand why you are referring to CWB.
the outside temperature is much higher than 15C.
Other zones that have higher setpoints are being turned off because of WWS.
My question is why is Bed 3 not subject to WWS, set to 5C (like every other zone) and switched off.
@Peter You are correct, sorry I didnt read the question properly. I will have to have a look at the system to know for sure but I think it is because the WWS decision is based on the learned fuzzy demand not just a simple OTC. I presume the zone is off based on room temperature?
Regards AtM
CWB been operating all day as outside temp being below 10C but with the bright sun there has been a lot of radiation energy. House is over heated. I do like the idea of the CWB but the 10c point is too blunt. I would like a user set figure or a more sophisticated set point that includes wind chill. I generally find I want to boost the inside temps when outside is 4C or less and a strong northerly