Hey! Not for me it isnt! :(
Clive, I see you suspect the BDR91 response but can I also check the basics as well please? Where is your sensor on the tank, is it the surface mounted version and how high on the tank is it? If not where is the insertion pocket (a pic on pm might help)? The sensors are very fast, and the CS92 adjusts its transmit rate depending how close it is to setpoint and has a time constant of a second so we think the system is capapable of catching fast cyclinders. An obvious question but is the copper full exposed and the sensor in good contact with the tank side, also is this a standard indirect cylinder or is it direct fed?
Ally will send you a pm asking for your MAC address so we can look at the BDR/Evo response.
Regards AtM
Are you sure you have the hot water relay bound correctly to the right function ?
There is no TPI cycle for the hot water relay, it is either 100% on when hot water needs to reheat, or 0% on when it doesn't. No in between or regular cycling.
So when the hot water temperature drops below the hysteresis window it will switch on continuously until the temperature goes above the hysteresis window.
AFAIK it doesn't matter whether you use OpenTherm or a relay for boiler control.
Hi Andy, The Problem is definitely not the CS92 as I use the reading from it in my external control. The sensor is not a surface sensor it is the pocket type and deep inside the cylinder with heat sink compound. I can’t fault the CS92 performance. FYI I use an HG180 and Domoticz to capture the Evohome data which includes the HW temperature from the CS92 and then from this trigger an external relay in place of the BDR91 to switch the CH/DHW valves it works flawlessly. As a double proof that the CS92 is Ok the Evohome Opentherm Signal fires the boiler in response to it perfectly in conjunction with my bodge it’s just the lag in the BDR91. I have an opentherm Bridge that records the OT data I also record the signal to the BDR91 via the HG180. The BDR works when it is called as I see the signal to it on the HG180.
The CS92A can have some lag (which means the reported temperature on the controller can sometimes be behind) but I have never seen any lag between the controller and the hot water relay. It updates as soon as the temperature reading on the screen changes. (Slightly before actually)
Are you sure you don't have hot water overrun enabled ?
Hot water overrun adds a delay from the time the set point is reached until the hot water relay goes off. If you set this too long you can experience temperature overshoots. On a system that heats fast I would set hot water overrun to zero.
I have a slow heating cylinder and have hot water overrun set to 1 minute to allow latent heat to be removed from the boiler heat exchanger and even then I see a 1-2C overshoot in the hot water temperature if there is no heating load to soak up the excess latent heat, as there often isn't at this time of year.
I leave it enabled to keep my boiler happy though as it is very old and a little prone to kettling if it is suddenly switched to 100% flow through the ABV at a high flow temperature.
Looks to me like my system has just updated with the latest BETA Firmware...