pumping over
have a potterton kingfisher floor standing boiler, gavity hot water, pumped heating . when hot water selected within ten minutes the system is pumping over to f/e tank. have checked to see if any blockage in f/e tank but seems to be filling system fine. any ideas would be grateful.
-
5th October 2006, 07:31 PM
#2
Moderator
Re: pumping over
If it's gravity hot water it won't be pumping over on hot water only,
Is the water coming out of the expansion pipe hot?
If so your boiler stat has gone.
-
5th October 2006, 07:54 PM
#3
Automated Home Lurker
Re: pumping over
hi ya.yes hot water only thats what i thought strange. when i went to customers home to check to find boiler boxed in in cupboard with little access. i managed to check pump working ok. turned of heating selected water only then found water to be gravity fed. by the time i got to loft it was pumping over red hot and banging it head off. so had to turnoff.now removed all the boxing in that kitchen fitter had done, so it can get some air. she has messaged me tonight saying it hasn't been banging, but il have to check myself to see if its pumping over.
sunbeam .would you still say faulty stat
-
5th October 2006, 08:02 PM
#4
Moderator
Re: pumping over
kitchen fitters eh :twisted:
I would say faulty stat, just make sure first that the stat end is in the boiler pocket, sometimes when you push the stat end into the boiler it comes out the other side.
-
5th October 2006, 08:05 PM
#5
Automated Home Lurker
Re: pumping over
give that a check weekend let you no. cheers