    Default Vaillant Turbomax VUW 242E not firing

    I took a shower yesterday morning and the boiler fired up as usual. Later in the day I flicked the time clock to constant for central heating and it failed to ignite. It no longer worked for just hot water either.

    The electronic ignition is working fine; the fan kicks in; the water pressure is where it should be; the problem is, there doesn't seem to be any gas reaching the boiler.

    Any suggestions?

    Nick

  2. #2
    Moderator sunbeam's Avatar
    Join Date
    Feb 2006
    Location
    lancs
    Posts
    261

    Default

    the first thing i would do is see if there's any gas getting through to the pilot.

  3. #3
    Automated Home Lurker
    Join Date
    Jan 2007
    Posts
    4

    Default

    I don't think there is a pilot: it's electronic ignition. No, there's no gas getting there, that's the problem. Whatever opens to allow gas to flow to the ignition isn't opening. What that is, though, I don't know!

  4. #4
    Moderator sunbeam's Avatar
    Join Date
    Feb 2006
    Location
    lancs
    Posts
    261

    Default

    the electronic ignition will light a pilot which will then bring on the main burner,

  5. #5
    Automated Home Lurker
    Join Date
    Jan 2007
    Posts
    4

    Default

    In that case, since the electronic ignition is working okay, I would say there is definitely no gas reaching the pilot. Is there an obvious cause for this?

  6. #6
    Moderator sunbeam's Avatar
    Join Date
    Feb 2006
    Location
    lancs
    Posts
    261

    Default

    if i was stood in front of the boiler the first thing i would do, is clean the pilot out.

  7. #7
    Automated Home Lurker
    Join Date
    Jan 2007
    Posts
    4

    Default

    I'll try that. Thanks.

  8. #8
    Automated Home Jr Member
    Join Date
    Dec 2006
    Posts
    14

    Default

    From the sounds of things it doesnt fire up for heating OR hot water now which makes it look like a problem in the startup sequance.
    If everything else is doing what it should then there's no gas there to ignite, likely causes;
    1. pcb isn't powering the solenoid to open the gas valve to allow gas to pass to ignite (least likely but possible, beware of anyone just wanting to put in a new board without following a fault flow diagnostic as they're v expensive and many people just blame the board when they aren't too sure only then to tell u it's also the "Xpart" is faulty)
    2. gas valve is faulty
    3. solenoid is faulty (most likely & cheapest of the 3)

    There are solenoid testers available from trade centres such as Plumb Centre (Regin make 1) which aren't too expensive if you or someone you know are competant to use them