    Default Constant PCA failing / reset - PC build issue?

    I'm still building / tweaking my Cortex PC to drive to as low-consumption as possible. It's an EPIA EN1200, currently in an available ATX chassis.

    Till now, it's been powered by a spare 400w ATX PSU but I am trying to change this to a silent 60w PSU set, complete with laptop-style brick, from linitx (this one).

    But, either Cortex, the motherboard or PCA fails whenever I try it.

    It continually reports hardware errors and tries resetting the PCIF then cycles... and cycles. Swap the 400w ATX PSU back and it's all fine again.

    The power source is the ONLY thing that's different. The only other device drawing power from the active PSU is a 2.5inch SATA HD, so I can't be overloading the PSU.

    My best guess is that is a ground-related issue causing the PCD problems , but I'm at a loss to work out why - I've even tried leaving the ATX PSU in the chassis with mains cable connected in case the chassis needed a route to mains earth maintained. The rest of the Idranet connected parts are either idranet-only or supposed to be isolated so the change of PC PSU shouldn't affect it.

    Below is the output that cortex shows... sorry it's long, but you'll get the idea that it just repeats....

    Has anyone got any ideas or seen anything similar ?

    Edit: I'm using UNshielded twisted pair for the Idranet bus

    ----------------
    16:55:10 PCIF hard reset
    16:55:11 RS232 Purge buffers
    16:55:11 The hardware detected a break condition
    16:55:11 RS232 Purge buffers
    16:55:11 PCIF hard reset
    16:55:11 RS232 Purge buffers
    16:55:12 The hardware detected a break condition
    16:55:12 RS232 Purge buffers
    16:55:12 PCIF hard reset
    16:55:12 RS232 Purge buffers
    16:55:12 The hardware detected a break condition
    16:55:13 RS232 Purge buffers
    16:55:13 PCIF hard reset
    16:55:13 RS232 Purge buffers
    16:55:13 The hardware detected a break condition
    16:55:13 RS232 Purge buffers
    16:55:13 PCIF hard reset
    16:55:14 RS232 Purge buffers
    16:55:14 The hardware detected a break condition
    16:55:14 RS232 Purge buffers
    16:55:14 PCIF hard reset
    16:55:14 RS232 Purge buffers
    16:55:16 Invalid nmf 00
    16:55:16 Invalid nmf 60
    :: :: ::
    16:55:17 Invalid nmf E0
    16:55:17 Invalid nmf F8
    16:55:19 The hardware detected a framing error
    16:55:19 RS232 Purge buffers
    16:55:19 PCIF hard reset
    16:55:20 RS232 Purge buffers
    16:55:20 The hardware detected a break condition
    16:55:20 RS232 Purge buffers
    16:55:20 PCIF hard reset
    16:55:20 RS232 Purge buffers
    16:55:21 The hardware detected a break condition
    16:55:21 RS232 Purge buffers
    16:55:21 PCIF hard reset
    16:55:21 RS232 Purge buffers
    16:55:21 Invalid nmf 06
    16:55:21 Invalid nmf 78
    :: :: ::
    16:55:22 Invalid nmf 1E
    16:55:22 RS232 CHECKSUM ERROR 18E01E1898
    16:55:22 RS232 Purge buffers
    16:55:22 PCIF hard reset
    16:55:22 RS232 Purge buffers
    16:55:23 The hardware detected a break condition
    16:55:23 RS232 Purge buffers
    16:55:23 PCIF hard reset
    16:55:23 RS232 Purge buffers
    16:55:24 The hardware detected a break condition
    Last edited by jpdw; 1st November 2008 at 06:19 PM. Reason: Added not about UTP

  2. #2
    Automated Home Legend Karam's Avatar
    Join Date
    Mar 2005
    Posts
    819

    Default

    The problem appears to be at the RS232 side. I think it probably is a grounding issue or rather floating 0V line. Try common grounding of 0V on IDRANet supply and EPIA sides. Unshielded twisted pair for IDRANet bus should not have an adverse effect on IDRANet communications.

  3. #3
    Automated Home Jr Member KirasHome's Avatar
    Join Date
    Oct 2006
    Location
    Hampshire
    Posts
    37

    Default

    Hi jpdw,

    I'm using the same motherboard are you (EPIA EN12000G), in a Travla C158 Mini-ITX Case but with an External 120W Universal 110/240V 19V AC adapter and internal 120W 19V DC converter. My HDD is a 3.5in Samsung SATA. I've not seen any problems with it.

    Just a follow on thought from your comment about the earth, I'm wondering if the brick PSU is just struggling slightly to supply the power you need and that's affecting the RS232 voltages (http://en.wikipedia.org/wiki/RS232#Voltage_levels). Can you get a power meter on the setup? Or check the voltages on the RS232.

    Jamie.

  4. #4
    Moderator toscal's Avatar
    Join Date
    Oct 2005
    Location
    Near Alicante Spain
    Posts
    2,014

    Default

    Certain models of EPIA mini-itx boards have had known grounding issues. My mini-itx is an MII 12000. I solved it by running a ground wire between the PSU board, its running on a brick style 80W PSU and converter board , and the motherboard. The problems I had was bad RS232 coms or continuous com chatter on the serial port, and also I had problems booting the machine up. Since adding this wire the machine has been OK.
    It might be worth checking the earth in the mains socket.
    Also the EPIA EN15000G I know uses about 30W to 50W depending on the type of power supply used, with just a hard drive connected. So I guess you should get similar figures with your 12000. It should be OK but it could be on the limit. What is the internal DC to DC PSU converter board rated at.
    Good luck
    Last edited by toscal; 3rd November 2008 at 10:19 AM.
    IF YOU CAN'T FIX IT WITH A HAMMER, YOU'VE GOT AN ELECTRICAL PROBLEM.
    www.casatech.eu Renovation Spain Blog

  5. #5
    Automated Home Guru jpdw's Avatar
    Join Date
    Oct 2007
    Posts
    168

    Default

    Thanks all for the many comments....

    Quote Originally Posted by Karam View Post
    The problem appears to be at the RS232 side. I think it probably is a grounding issue or rather floating 0V line. Try common grounding of 0V on IDRANet supply and EPIA sides. Unshielded twisted pair for IDRANet bus should not have an adverse effect on IDRANet communications.
    Indeed, using UTP should definately not be the cause - I was only mentioning it so it was clear I wasn't using STP and grounding the shield all over the place (as noted in one of your guide documents)

    Comparing the 0v on the idranet bus with the 0v line on the PC shows virtually no difference between the two PSUs (~1.x mV for the ATX, ~2.2mV for the fanless set). Linking the two, similarly, seemed to make no difference (admitidly this test was done with a flying lead rather than making proper connections, so maybe it really would have worked -- all have another go at this one).

    Is the "common ground" pin of the RS232 connector used on the PCD? Isn't that supposed to make this ground connection?

    Quote Originally Posted by KirasHome View Post
    Just a follow on thought from your comment about the earth, I'm wondering if the brick PSU is just struggling slightly to supply the power you need
    It's supposed to be a 60w. Reading the wattage drawn from the mains, it's 26w with the ATX PSU and ~18w with the fanless set, so well within the 60

    Quote Originally Posted by KirasHome View Post
    and that's affecting the RS232 voltages (http://en.wikipedia.org/wiki/RS232#Voltage_levels). Can you get a power meter on the setup? Or check the voltages on the RS232.
    Only thing I can check at the moment is the levels on the ATX supply. The 5v is 4.88 and the -12v is -11.31 . I wonder if this is bit too low. (I assume the chipset will use the available -12v rather than synthesise it from the -5v).

    Quote Originally Posted by toscal View Post
    Certain models of EPIA mini-itx boards have had known grounding issues. My mini-itx is an MII 12000. I solved it by running a ground wire between the PSU board, its running on a brick style 80W PSU and converter board , and the motherboard. The problems I had was bad RS232 coms or continuous com chatter on the serial port, and also I had problems booting the machine up. Since adding this wire the machine has been OK.
    Sounds exactly like what I'm seeing. Isn't this what the various GND pins in the ATX cable should be doing? Can you be more specific about where on the motherboard you connected it (shield of the RS232? Common GND pin of the RS232 etc...?)

    Quote Originally Posted by toscal View Post
    It might be worth checking the earth in the mains socket.
    Ha ha.. I have a couple of concerns about the sockets in this room since I discovered the circuitous route the circuit takes... BUT I dont that this would be the cause of this problem... If the earth was dodgy / missing, wouldn't this affect BOTH the ATX PSU and the fanless?


    To investigate further I need to haul the PC up to my desk... but currently there's no idranet there, so I need to wait till it's warm enough that I can down the network and "borrow" the PSU/MPD and setup a mini test network. Give me an excuse to "play" at the weekend instead of feeding the babies... :-)

    Meanwhile it'll be back to burning the additional 10w of power to run the ATX PSU :-(

  6. #6
    Moderator toscal's Avatar
    Join Date
    Oct 2005
    Location
    Near Alicante Spain
    Posts
    2,014

    Default

    This is what I did.
    1. I cut a length of wire, about 10cm.
    2. Crimped a round terminal on to each end. Make sure the hole is large enough to fit the screws that attach the motherboard to the chassis.
    3. Attach one end to the screw nearest to the PS2 connector.
    4. Attach the other end to the ground on the DC to DC converter board, normally one of the screws attaching the board to the chassis will do.

    If I can I will see if I can get a photo or two for you.
    IF YOU CAN'T FIX IT WITH A HAMMER, YOU'VE GOT AN ELECTRICAL PROBLEM.
    www.casatech.eu Renovation Spain Blog

  7. #7
    Automated Home Guru jpdw's Avatar
    Join Date
    Oct 2007
    Posts
    168

    Default

    Quote Originally Posted by toscal View Post
    This is what I did.
    1. I cut a length of wire, about 10cm.
    2. Crimped a round terminal on to each end. Make sure the hole is large enough to fit the screws that attach the motherboard to the chassis.
    3. Attach one end to the screw nearest to the PS2 connector.
    4. Attach the other end to the ground on the DC to DC converter board, normally one of the screws attaching the board to the chassis will do.

    If I can I will see if I can get a photo or two for you.
    Okay, that makes sense - I see now what you are commoning -- making sure the chassis ground is good.

    I'll give that a go later on.

  8. #8
    Automated Home Guru jpdw's Avatar
    Join Date
    Oct 2007
    Posts
    168

    Default

    Quote Originally Posted by Karam View Post
    Try common grounding of 0V on IDRANet supply and EPIA sides.
    Quote Originally Posted by toscal View Post
    This is what I did.
    1. I cut a length of wire, about 10cm.
    2. Crimped a round terminal on to each end. Make sure the hole is large enough to fit the screws that attach the motherboard to the chassis.
    3. Attach one end to the screw nearest to the PS2 connector.
    4. Attach the other end to the ground on the DC to DC converter board, normally one of the screws attaching the board to the chassis will do.

    If I can I will see if I can get a photo or two for you.
    Unfortunately it seems that neither of these (either separately or in combination) solves the problem.

    The bus voltages out of the DC/DC board are marginally below those from the ATX PSU -- but only by ~0.2v. (Measured under the load of the motherboard).

    I'm not sure what to try next. If I had a 'scope I'd be looking at the levels on the serial cable but I don't :-( . It's still bugging me that the only difference to the setup between working and not working is the PSU.

  9. #9
    Moderator toscal's Avatar
    Join Date
    Oct 2005
    Location
    Near Alicante Spain
    Posts
    2,014

    Default

    Can you try another brick type psu. As you may have a faulty one. OR try one of a higher wattage, at least then you will know if its the PSU.
    IF YOU CAN'T FIX IT WITH A HAMMER, YOU'VE GOT AN ELECTRICAL PROBLEM.
    www.casatech.eu Renovation Spain Blog

  10. #10
    Moderator Gumby's Avatar
    Join Date
    May 2004
    Location
    Gloucestershire
    Posts
    437

    Default

    Maplin do an ATX PSU checker device, may be this would help. If you are anywhere near Gloucestershire I can lend you one.
    ----------------------