    Virtual Temperature Object large -ve readings

    I've got 2 "virtual" DTS modules (1 for each floor of the house), that have each room's temp sensor connected to the "alternative temp source", giving me an average temperature per floor.
    I also have the same setup for average outside temperature with 3 x LTH-X.

    The problem I'm seeing is on cortex network start/stop and spur re-powering, the 2 virtual DTS that show average floor temp will drop to -1000, when graphed it cortex it shows it dropping to around -99.
    The same thing DOESN'T happen on the virtual DTS that represents the outside temperature.

    I've double checked the DTS connections and can't see anything wrong.
  • Viv
    Automated Home Ninja
    • Dec 2004
    • 284

    #2
    A value of -1000 is used as a un-initialised value within Cortex. That is, decisions based upon this temperature should not made until a real reading has been received.
    It may be the 'alternative temp source' input is not considering this and we will need to check.

    Viv