    Hi there,

    Can we get some definition on the 3 parameters for the Hot Water kit please ? There is no Help text for any of them.

    Thanks,
    Roy.

  2. #2
    Automated Home Legend top brake's Avatar
    Join Date
    Feb 2015
    Location
    the edge of the cloud
    Posts
    827

    Default

    Hot water overrun
    Specifies how long the valve for the hot water is open or the hot water pump is running to extract all the heat to avoid blocking the heat source.

    Needs to be Figure 4 installation 'hot water single valve' with boiler relay for this to work


    Hot water differential

    Setting the switching differential of the domestic hot water control.

    Standard is 10 degrees, what this means is that the hot water temperature needs to drop to 50 degrees before the hot water relay (valve) will open again to heat the cylinder. I usually trim to to 7 degrees on a vented tank and 5 degrees on an unvented tank

    Hot water temperature

    Setpoint for the hot water temperature, typically adjusted to 60 degrees in UK to ensure legionella disinfection




    hope this clarifies

    no reason why these parameters are not covered in the manual, just an omission