Hi all I have moved in to a new flat that has electric heating. Each room has Dimplex electric heats and these are controlled by a Dimplex programer. The heating is split into 2 zones for heating and a 3rd for hot water. I would like to replace the Dimplex programer with a smart thermostat that I can control with my iPhone / iPad. Would I be able to do thid with the Honeywell Evohome ?
Control of electric heating
Collapse
X
-
I have 2 x Dimplex EPL1000 controlled via BDR91 > evohome. (in loft)
Things to note
- At this time we make no use of the control wire on the electric heater (if there is one) - so don't use. Effectively what you need to do is leave E-Rad on and at Max, the BDR performs the 'switching'
- Within the room you will need a 'sensor' (DTS92 or SZT) which will act as the room sensor and will command the evohome
Then you can set this up as a zone.
Important things to note
- The BDR91 is only rated for loads 1000kwa - (it will do slightly more but officially this is the load)
- if the rest of your house is 'resting' and you make a call for heat in the electric zone only - this could (probably will) still make a demand call for heat from the boilier - so it will fire
This isnt an issue for me as normally the electric calls are at same time as either hotwater or another room needs it.
This is on our future's list to resolve.Last edited by Rameses; 18 March 2015, 08:22 PM.getconnected.honeywell.com | I work for Honeywell. Any posts I make are purely to help if I can. Any personal views expressed are my own
-
-
Ahh - well in that case. ok
Assuming each rad is 1000 rated?
Its easy wiring - even I did it myself. There is a really simple diagram here
fig 2.3 top left
You need some wire to loop around the back of the BDR92 to create the internal connection L>A
The BDR91 is a wireless switch - so effectively if the load is within tolerance you can switch anything.
Dont forget the sensors though #important
PS not sure how your hotwater is done suspect this will be a bigger load - so this might need to be left on timer?/programmer?Last edited by Rameses; 18 March 2015, 08:29 PM.getconnected.honeywell.com | I work for Honeywell. Any posts I make are purely to help if I can. Any personal views expressed are my own
Comment
-
-
Originally posted by Rameses View PostAhh - well in that case. ok
Assuming each rad is 1000 rated?
Its easy wiring - even I did it myself. There is a really simple diagram here
fig 2.3 top left
You need some wire to loop around the back of the BDR92 to create the internal connection L>A
The BDR91 is a wireless switch - so effectively if the load is within tolerance you can switch anything.
Dont forget the sensors though #important
PS not sure how your hotwater is done suspect this will be a bigger load - so this might need to be left on timer?/programmer?
Any questions at all, you can give me a call.
Comment
-
-
The BDR91 I have has a relay stating max load 10Amp. I am interested in controlling a 1400Watt electric heater via the evohome using the BDR91 which would consume 5.88 amps. I can get a 7amp BS1362 fuse for the isolation switch. Is there anything else in the BDR91 that wouldn't be able to handle that load?
Comment
-
-
Originally posted by SteveP View PostThe BDR91 I have has a relay stating max load 10Amp. I am interested in controlling a 1400Watt electric heater via the evohome using the BDR91 which would consume 5.88 amps. I can get a 7amp BS1362 fuse for the isolation switch. Is there anything else in the BDR91 that wouldn't be able to handle that load?I work for Resideo, posts are personal and my own views.