I understand that is is the case but why would you want to do it. Presumably the CH zone valve is configured to control the boiler/pump through its relay. In which case any BDR91 configured as a boiler relay would be redundant.
Quick question - can the Evohome controller control one CH zone valve, one DHW zone valve and have a boiler relay too (ie: Three BDR91's)?
Thanks
i have identified a way to configure this, however are you sure this is what you need?
what function will the CH zone valve provide if there are HR92 on the radiators?
I work for Resideo, posts are personal and my own views.
There are no HR92's on any radiators at present. To start, I will simply be using the Evohome to allow independent hot water / central heating control (not possible at present). Unfortunately, (due to location of expansion pipe) it's looking like the DHW zone valve will have to be located well away from the boiler, close to the water cylinder.
So I thought it may be easier to have a separate boiler relay instead of long run of twin and Earth between the zone valve and the boiler.
There are no HR92's on any radiators at present. To start, I will simply be using the Evohome to allow independent hot water / central heating control (not possible at present). Unfortunately, (due to location of expansion pipe) it's looking like the DHW zone valve will have to be located well away from the boiler, close to the water cylinder.
So I thought it may be easier to have a separate boiler relay instead of long run of twin and Earth between the zone valve and the boiler.
understood
so you need 3 relays installed bound as follows:
boiler relay wired to fire boiler/pump
hot water valve relay (single valve) wired to open hot water zv
zone valve relay (heating type zone valve) wired to CH zone valve
so get a base pack, factory reset
guided config
hot water config/single valve
zoning config/ yes to boiler relay/ add heating zone type 'zone valve'
that's it
make sense?
I work for Resideo, posts are personal and my own views.