Evohome replace existing dial thermostat

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts
  • elite
    Automated Home Lurker
    • Oct 2015
    • 1

    Evohome replace existing dial thermostat

    I think I have settled on evohome over heat genius - the one question I have is, can I replace my existing dial thermostat with evohome and set just set my heating to continuous or do I need to replace the controller on the boiler?

    I would happily replace the controller on the boiler, however it is a Stanley and also controls the oven...

    System is oil powered BTW as no gas here - hot water is on separate system and not part of this project
  • mikey8156
    Automated Home Jr Member
    • Dec 2011
    • 37

    #2
    Set your heating to continuous. Either remove your old dial thermostat of turn it to maximum temperature, not needed anymore.

    Comment

    • paulockenden
      Automated Home Legend
      • Apr 2015
      • 1719

      #3
      Or you could mount the Evohome controller there. The existing wires can be used for the power feed, just put the transformer in your airing cupboard )or wherever the other end of the wire is).

      P.

      Comment

      • jonboy
        Automated Home Jr Member
        • Aug 2015
        • 22

        #4
        I don't want to high-jack this thread but I have related questions.

        I have a newly installed gas c.h. and direct hot water condensing boiler system. There is a Danfoss dial thermostat on the wall in the hall with a digital timer/controller on the wall next to the boiler housing unit.

        Changing the thermostatic valves seems straightforward enough. Do I simply remove the Danfoss wall thermostat and simply wire the ATP921R3100 into the 240 V supply only?

        How do I swop the BDR91 for the timer controller? Is it just the case of swopping a few wires from the timer/controller? There is no hot water tank so I just need to control the central heating.

        The BDR91 would then be located outside the boiler housing kitchen cabinet on the wall just about 200mm from the side of the boiler. Is this far enough away, considering the boiler housing cabinet is about 44mm thick?

        Other than ensuring a good wifi connection, is there any other particularly onerous technical installation procedure to consider?

        Comment

        • Fursty Ferret
          Automated Home Sr Member
          • Oct 2014
          • 84

          #5
          Don't think that'll work.

          You'll need to remove the programmer and rewire to provide permanent live to thermostat location. This will power the Evohome controller, but because you've stolen what was a switched live for the thermostat the BDR91 will have to control the valve directly. You might have sufficient cabling to the programmer to do this (especially if the system used to do hot water through a tank or something) but in reality it'll be easier to have the BDR91 near the valve and just stick a blanking plate where the programmer used to be.

          Alternatively, you could replace the programmer with the BDR91 and then remove the existing thermostat, using the Evohome controller on it's stand and supplied mains adapter.

          Comment

          • jonboy
            Automated Home Jr Member
            • Aug 2015
            • 22

            #6
            Thanks for your reply.

            Although I am fairly proficient in DIY, I am not very knowledgeable about your suggestions. I don't know what you mean by 'the valve' and controlling it directly.

            Our c.h. system is just a year old with a condensing boiler. There has never been a hot water tank. The h.w is direct and on demand.

            Can you elaborate on your explanation or direct me towards a manual or instructions?

            I don't want to purchase the system until I know I can fit it without any problems

            Comment

            • Fursty Ferret
              Automated Home Sr Member
              • Oct 2014
              • 84

              #7
              Oh, right. If it's a combi boiler then there's no farting around with valves.

              You can remove the existing programmer and replace it with the BDR91, switching the boiler directly without going through the old thermostat. You're probably going to have to spend some time identifying some of the wiring behind your programmer, but it shouldn't be too difficult.

              You'll have a two or three core cable to the existing thermostat which you can appropriate to send 240v to the wall mount to power the controller.

              Wiring diagrams in the installation manual. You might also want to check if your boiler is OpenTherm compatible, as that'll make the heating more efficient and you won't need the BDR91.

              Comment

              • paulockenden
                Automated Home Legend
                • Apr 2015
                • 1719

                #8
                Originally posted by Fursty Ferret View Post
                You'll have a two or three core cable to the existing thermostat which you can appropriate to send 240v to the wall mount to power the controller.
                I wouldn't do it like that. I'd mount the transformer at the 'junction box' end of the cable, and just send low voltage DC down the existing cable to the wall mount. That way you don't need a wall-box behind the controller (to house the transformer), you can just mount the plate flush on the wall.

                P.

                Comment

                • Fursty Ferret
                  Automated Home Sr Member
                  • Oct 2014
                  • 84

                  #9
                  True, but if there's an existing thermostat there's probably already a wall box fitted in a convenient bit of the house, and the wall mount bit comes with a dinky transformer that fits perfectly.

                  Comment

                  • jonboy
                    Automated Home Jr Member
                    • Aug 2015
                    • 22

                    #10
                    Thanks to you both for your further replies.

                    The condensing boiler is a Viessmann Vitodens 100W. I note that Viessmann produce Open Therm compatible boilers, but I would have to check if my specific model comes into this category. Can you please explain how I can discard the BDR91 and how this would be more efficient? If it was possible to dispense with the BDR91 does this mean a more complicated installation procedure?

                    The Danfoss wall thermostat in the hall is fitted to a plastic wall box so can I assume that this would be a straightforward installation by simply connecting to the existing 240V cable?

                    If the BDR91 is utilised I assume it can be simply substituted for the controller with the appropriate wires swopped over, or is it more complex than this?

                    Comment

                    • electronicsuk
                      Automated Home Sr Member
                      • Sep 2015
                      • 55

                      #11
                      Originally posted by jonboy View Post
                      The condensing boiler is a Viessmann Vitodens 100W. I note that Viessmann produce Open Therm compatible boilers, but I would have to check if my specific model comes into this category. Can you please explain how I can discard the BDR91 and how this would be more efficient? If it was possible to dispense with the BDR91 does this mean a more complicated installation procedure?
                      Honeywell are a bit light on the details when it comes to the OpenTherm bridge, but the general premise behind OpenTherm is that it hands a lot more control of the boiler over to the thermostat. Rather than simply turning the boiler on or off, the thermostat can modulate flow temperatures and such, keeping the boiler in condensing mode for as long as possible and thereby increasing the efficiency of the system. Exactly how much of a difference this all makes I have yet to tell, but I am using the OpenTherm bridge on my system. Installation is very simple, just two wires to connect to the boiler.

                      Originally posted by jonboy View Post
                      The Danfoss wall thermostat in the hall is fitted to a plastic wall box so can I assume that this would be a straightforward installation by simply connecting to the existing 240V cable?
                      If there's a continuous supply there then yes, it should be pretty easy. If not, you may need to make some changes to the wiring at the other end. You'll also want to get the wall-mount kit for the EvoHome controller.

                      Originally posted by jonboy View Post
                      If the BDR91 is utilised I assume it can be simply substituted for the controller with the appropriate wires swopped over, or is it more complex than this?
                      Shouldn't be much more to it than that, especially as you don't need to worry about hot water control.

                      Comment

                      • jonboy
                        Automated Home Jr Member
                        • Aug 2015
                        • 22

                        #12
                        Thanks for your reply electronicsuk.

                        When you say "the thermostat can modulate flow temperatures" do you mean each individual radiator thermostat?

                        You say "Installation is very simple, just two wires to connect to the boiler". Can you please elaborate? Where do the wires come from if there is no BDR91? Can you refer me to instructions on how to do this?

                        Comment

                        • The EVOHOME Shop
                          Site Sponsor
                          • Dec 2014
                          • 483

                          #13
                          Originally posted by jonboy View Post
                          Thanks for your reply electronicsuk.

                          When you say "the thermostat can modulate flow temperatures" do you mean each individual radiator thermostat?

                          You say "Installation is very simple, just two wires to connect to the boiler". Can you please elaborate? Where do the wires come from if there is no BDR91? Can you refer me to instructions on how to do this?
                          OpenTherm was developed by Honeywell and basically allows the evohome system to adjust an OpenTherm compatible boilers heat output based on the heating demand requirements of the evohome system.

                          The R8810 OpenTherm Bridge has two terminals and you basically use low voltage wires that attach the OT Bridge to the two OpenTherm terminals on the boiler. The boilers OpenTherm connection will power the R8810 OpenTherm Bridge.

                          Bear in mind there is specific system design criterion for 'system boilers' using OpenTherm with evohome - no motorised zone valve on heating side of the system and HR92's fitted to all radiators is one such requirement. Combi boilers are simpler, but if you have motorised zone valves fitted for a two zone heating system the previous statement applies also.

                          Comment

                          • jonboy
                            Automated Home Jr Member
                            • Aug 2015
                            • 22

                            #14
                            Originally posted by The EVOHOME Shop View Post
                            OpenTherm was developed by Honeywell and basically allows the evohome system to adjust an OpenTherm compatible boilers heat output based on the heating demand requirements of the evohome system.

                            The R8810 OpenTherm Bridge has two terminals and you basically use low voltage wires that attach the OT Bridge to the two OpenTherm terminals on the boiler. The boilers OpenTherm connection will power the R8810 OpenTherm Bridge.

                            Bear in mind there is specific system design criterion for 'system boilers' using OpenTherm with evohome - no motorised zone valve on heating side of the system and HR92's fitted to all radiators is one such requirement. Combi boilers are simpler, but if you have motorised zone valves fitted for a two zone heating system the previous statement applies also.
                            Thank you for your reply.

                            It would appear that our Viessmann Vitoden 100-W is Opentherm capable as the company produces the Vitotrol 100 open therm controller for use with the boiler.

                            It is a new combination boiler with no motorised zone valves as far as I am aware. Hot water is on demand with no storage system.

                            Is there a significant benefit to installing the R8810 rather than the BDR91?

                            Can R8810 be more or less problematic once installed?

                            Is the R8810 easier to install?

                            Can the Evohome controller be purchased more cost effectively as a stand alone unit?

                            I am still trying to get a handle on all this.

                            Comment

                            • top brake
                              Automated Home Legend
                              • Feb 2015
                              • 837

                              #15
                              Originally posted by jonboy View Post
                              Thank you for your reply.

                              It would appear that our Viessmann Vitoden 100-W is Opentherm capable as the company produces the Vitotrol 100 open therm controller for use with the boiler.

                              It is a new combination boiler with no motorised zone valves as far as I am aware. Hot water is on demand with no storage system.

                              Is there a significant benefit to installing the R8810 rather than the BDR91?

                              Can R8810 be more or less problematic once installed?

                              Is the R8810 easier to install?

                              Can the Evohome controller be purchased more cost effectively as a stand alone unit?

                              I am still trying to get a handle on all this.
                              using the R8810A1018 will allow the boiler to modulate rather than being switch 0 or 100% using TPI on a cycle/minimum run time basis

                              the benefits of modulating the boiler include lower gas use, more efficient operation and closer more stable control

                              R8810A1018 is powered from the OpenTherm terminals on the boiler so no mains supply needed

                              regarding purchasing all the parts are available separately so if you don't need a BDR91 to control boiler you can buy the (spare) controller, R8810A1018 and either desk or wall mount

                              parts list on back of brochure
                              Last edited by top brake; 16 October 2015, 10:49 AM.