Originally Posted by
Fursty Ferret
Hi Bill,
You shouldn't use a G/Y insulated conductor without adding brown sleeving to both ends (or some other way of identifying it as live). This is common sense (and also a legal requirement), and while I'd run new four core cable as an alternative to doing this it's not explicitly forbidden by regulations.
Looking at your picture - if it's a combi boiler, why is there even a connection to the DHW terminal in the first place? Disconnect and terminate the green/yellow wire safely in a chock-block (you don't need it).
Basically, you've got it wired wrong. On the BDR91, the two "L"s are linked internally. Connect a link of wire from the second L to A, connect the wire for CH to B, and leave C empty.
If it still doesn't work, temporarily link the live and CH terminals - the boiler should fire. The reason it didn't work is because the CH terminal never received a call for heat from the BDR91.
Cheers,
Dave.
Edit: Though if it still doesn't work after that, call a heating engineer.