I've come down to zone valve on each room with rad valve as remote temp sensor. Have now lost the rad valve control options though and cannot lock them out etc???? I've also now got a solid red light with two flashes of green on the CH BDR. ???? Replace one problem with another it seems.
Multiple BDR's
Collapse
X
-
Make sure you cleared binding on all devices. Factory reset and reboot evohome. Go through guided config. If you're still stuck please draw your system and wiring, take pictures and I will advise. ThanksI work for Resideo, posts are personal and my own views.
Comment
-
-
Same issue??
Originally posted by top brake View PostI think you need to reassign your HEATING relay as a BOILER RELAY
then the heat demand from any zone will energise the BOILER RELAY
the radiator zones should be configured as ZONE VALVE heating zone types
make sense?
I now want to add individual control to some radiators. So if I add a zone upstairs I need the TRV to open the upstairs v/v and downstairs, the downstairs v/v.
After reading this, I think I need to rewire the v/vs so they operate together with one BDR and use it as a boiler relay? Or, is it possible to have two boiler start relays?
Cheers,
Dave
Comment
-
-
I've gone back to factory. The evo home was full of actuator errors this morning. When I try to bind each zone/room (there are 8 rad controllers) with the BDR it throws the solid red with flashing green after the fourth bind. I'm rapidly regretting this purchase and I've invested heavily.
Comment
-
-
I'll look at your drawing later.
Sounds like you need to simplify your system.
You don't need to multiple bind the BDR only needs binding once. either at boiler relay, or heating valve or as a heating zone. There's a fundamental misunderstanding here that will be best be resolved by going through the youlearn.I work for Resideo, posts are personal and my own views.
Comment
-
-
I've been through the you learn, you suggested I drop the 8 rooms with rad controllers down to the zone level. I've reset and gone through guided config. It asks how many zones. I've got 8 rad controllers and one wireless stat for underfloor so selected 9. It then asks the remote sensor to be bound which has to be the rad controller, it then wants the zone valve which must mean BDR as there is nothing left. By the time I get to zone/room 4 the BDR shows red.
Comment
-
-
Ok your drawing is overcomplicati g it. You're turning a wireless control system into a wired hybrid? There is a wiring diagram in the appendix of the evohome installation manual that show splan wiring so you don't need to reinvent. Your underfloor heating needs a separate BDR91.
I think the only way to resolve is to grab a pot of coffee and go through the youlearn and the manual. If you're still stuck on Monday can arrange for a support agent to call you.I work for Resideo, posts are personal and my own views.
Comment
-
-
Originally posted by top brake View PostOk your drawing is overcomplicati g it. You're turning a wireless control system into a wired hybrid? There is a wiring diagram in the appendix of the evohome installation manual that show splan wiring so you don't need to reinvent. Your underfloor heating needs a separate BDR91.
I think the only way to resolve is to grab a pot of coffee and go through the youlearn and the manual. If you're still stuck on Monday can arrange for a support agent to call you.
Comment
-
-
http://www.honeywelluk.com/documents...stallation.pdf See fig 9 in appendix. He orange wire from ufh zone valve not needed. When ever there is a heat demand from any zone the heating relay will energise and open the heating zone valveI work for Resideo, posts are personal and my own views.