Thread: Evohome HR92 Installation issue with pin travel

  1. #1
    Automated Home Sr Member
    Join Date
    Oct 2008
    Posts
    78

    Default Evohome HR92 Installation issue with pin travel

    I have just bought four HR92 units, and fitted them (i think well) with the adapters fully clicking down the valve head. The units were fitted with a full anti clockwise set of the black drive wheel before mounting the head, and they cycle with no errors.

    But when set to off on all four radiators they fail to shut off the supply. I think they restrict it, the radiators SEEM a little less hot, but definitely still being heated.

    I have checked valve pin travel and they seem to move some 5-7 mm. Is this normal? I have tried the hammer approach and this has not helped, so am a bit stuck,. I know that the valves are not that expensive, but don't want to replacement them if there are any other suggestions?

    Thanks in advance.

    ...Jon.

  2. #2
    Automated Home Legend
    Join Date
    May 2014
    Posts
    988

    Default

    You can change the stroke. Parameter 6 - I think. Before doing so, it might be helpful if you posted your TRV type.

    From the HR92 Manual

    Check the Radiator Controller is properly installed on the radiator valve and adaptor.
    Check that the valve can be manually opened and closed (see Emergency operation on page 17).
    Remove the blockage or replace seized valve.
    Change the valve stroke parameter to full-stroke mode (Parameter 6).
    Last edited by HenGus; 7th December 2015 at 08:32 PM. Reason: Addtl info

  3. #3
    Automated Home Sr Member
    Join Date
    Oct 2008
    Posts
    78

    Default

    OK, set actuator to full stroke on two radiators, same lack of shutting off. Not cross threaded, adapter firmly on valve. Pictures attached.image2.jpgimage1.jpgimage3.jpgimage4.jpg

  4. #4

    Default

    You have not fitter the adapter properly and it is sitting too high in the valve body. If you open the adapter up and push it down it will seat fully on the valve you will find the actuator will operate correctly.

  5. #5
    Automated Home Guru
    Join Date
    Jan 2013
    Location
    Glasgow
    Posts
    186

    Default

    That's the exact same problem I had when I initially fitted my HR92's. The adaptor ring needs to fit fully down, however, when you first fit them, it feels like they are going to break. You need to fit them to the radiator without the screw/nut in place to allow the adaptor to open fully. I found that if I pushed them down, then took a flat blade screwdriver, inserted this in the slot where the adaptor opens at the screw and then twisted this slightly to open the adaptor up a little more, it would then slip over and fit securely to the radiator. You then put the screw and nut in place to hold it. Once, I did this, they controlled the radiators perfectly.

    Just be careful doing it, as I snapped one adaptor doing this. But, they do go one.

    Roy.

  6. #6
    Automated Home Sr Member
    Join Date
    Oct 2008
    Posts
    78

    Default

    Brilliant advice folks, thanks so much. I was being too careful. Perfect fit as I rushed to do this whilst leaving for work today. Much better fit and sure thus will solve the issue!