Originally Posted by
DBMandrake
What kind of boiler do you have, and does it have an automatic bypass valve installed, or a bypass radiator that is never turned off ? Does your system have pump overrun ? I had to add a pump overrun timer to our old (20yr) boiler because the TPI modulation of the BRD91 switches the boiler on and off frequently, if the pump stops at the same time the boiler goes off then you can get micro-boiling of the water in the boiler heat exchanger which after a while leads to steam bubbles building up and circulating noisily around the system. If only one or two radiators are open and the automatic bypass valve is flowing this steam bubble generation can get out of control as they tend to circulate right back into the heat exchanger instead of passing through radiators to cool and condense back into water.