    This is my first post and, first of all, I would like to thank you for writing and maintaining this forum. I learned a lot on the use of the EvoHome system here.
    Unfortunately, I found the official documentation really poor for such a kind of expensive system.

    I have installed the evohome wifi (a controller, 10 HR92 valves, a gateway and a BDR91 relay box) since October but I noticed a strange behavior.
    It seems that the Optimum Start feature is not working when the difference between the current temperature and the next one is less than two degrees.

    For example, I have 17 degrees for the night and 18 from 7:00. In this case the Optimum Start not works (no icon on the controller before 7:00) and the Evohome is like a normal thermostat or even worst. Because it turns on the boiler at 7:00 but not at the maximum power, it continues to turn on and off every like 10 minutes more o less and the valves are open at 50% more o less (lukewarm radiator). I would expect always on with valves opened at 100 until the new temperature is reached.
    This is a problem because after one hour, let say at 8:00, the temperature in that room is still 17,5 degrees.
    To solve it I have to leave the temperature constantly at 18, but is not so smart...
    This behavior is the same for all the rooms/areas.
    As soon as the difference is higher that 2 degrees the optimum start starts (icon appears) and works fine.

    I have already tried to reset the full system.

    Any of you have noticed this or can make a test?
    Thanks

  2. #2
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,625

    Default

    can you really tell the difference between 17 and 18 degrees? I'm not sure I could.

    The two temperatures are so close that Evohome will be operating in the TPI band, which is why you are seeing the boiler cycling. It's very hard to accurately get from 17 to 18, and if everything came on full-blast you'd almost certainly overshoot. As you'll have seen from other posts here, people don't like temperature overshoots.

    I suspect it's quite unusual to schedule such very subtle changes.

    P.

  3. #3
    Automated Home Lurker
    Join Date
    Jan 2016
    Posts
    3

    Default

    I think you are right...
    What I have is a big room with two radiators/valves linked to the central controller and I am trying to understand how to best manage the temperature in term of gas consumption.
    I would like to have low temperature at night (16), warm in the morning (18), then it could go down and up again in the evening (20).
    Doing like that I noticed that the boiler was always running at full blast during the changes. And, even with optimization on (with start set at 3 hours before), it was never able to reach the desired temperature on time. That is why I was trying to change the temperature of one degree only.
    But at the end I had to set always the same temperature (19). It seems that maintaining the same temperature is less expensive that turning on and off, but this could be another topic to open :-)
    Do you have any suggestion? Do you think that increasing the start time at more than 3 hours it could help?

    A.

  4. #4
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,625

    Default

    When your rooms aren't being used (at night) I'd be temped to sent them much lower than 16. What's the point of heating spaces that aren't occupied?

    P.

  5. #5
    Automated Home Sr Member
    Join Date
    Nov 2015
    Posts
    95

    Default

    Ive just set mine to optimum start, and I have set to allow up to 4 hours to warm up. Specifically because I have underfloor heating zones which may take longer to heat in the winter (as they would have to warm the whole slab and tiles etc). I would never anticipate that a single room would take that long to heat using radiators. (though other than holiday, I would probably not let those zones go overly cold overnight due to the energy required to heat the slab back up)

    If a room is taking that long to heat, then Id be looking at a list of things - boiler size, radiator size, pump size, is everything working as it should - are the locksheild valves closed too much etc... If its a domestic boiler putting out 30kw, then there is no reason that shouldnt be able to heat a very big room in well under 3 hours, and from a lot lower starting point than 16.

    I have an issue with a large room at the opposite end of the house taking a while to heat up, and a bedroom at the far end also taking a long time to heat. My issue is down to the pumps in the boilers not having enough puff to get the heat to that end of the house when other rooms are also calling for heat. If they are on on their own, and the only route for flow, then they are fine. Ive a low loss header and larger pump going in tomorrow, and will rebalance the system once the big pump is on.

    Im not a plumber, but Ive managed to learn a fair bit while having our house ripped apart and rebuilt including all new plumbing and elecs.

    What sort of size system are you running? Where is the room located in relation to the boiler? Are the radiators actually getting hot in that room when you expect them to be heating the room? Are they hot all over or are there cold areas on the radiators etc..

    My personal thought is that its not evohome that is the root of your problem here.
    Last edited by Cchris; 20th January 2016 at 05:45 PM.

  6. #6
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,894

    Default

    Quote Originally Posted by paulockenden View Post
    can you really tell the difference between 17 and 18 degrees? I'm not sure I could.

    The two temperatures are so close that Evohome will be operating in the TPI band, which is why you are seeing the boiler cycling. It's very hard to accurately get from 17 to 18, and if everything came on full-blast you'd almost certainly overshoot. As you'll have seen from other posts here, people don't like temperature overshoots.

    I suspect it's quite unusual to schedule such very subtle changes.

    P.
    I have to agree with this. If the radiator (and boiler duty cycle) was to come on full blast to try to increase from 17 to 18 degrees then it would almost certainly overshoot by at least 3 degrees. An easy way to demonstrate this is to have the room set at 17 degrees, (and up to temperature) and have at least one other room turned up high for a while so that the boiler is operating at 100% duty cycle and the system was hot.

    Then turn the HR92 in question up to 25 degrees for say 3 minutes to allow the valve to fully open and the radiator to fully heat, then set it back down to 10 degrees. In our bedroom in particular the thermal mass of the radiator is such that it will overshoot the current temperature by about 3 degrees performing a test like that.

    The only way the system can make an incremental change from 17 to 18 degrees is to open the HR92 valve slightly and run the boiler at a low duty cycle to cautiously increase the temperature of the room. My guess is that optimum start doesn't operate on 1 degree differentials on purpose. I do have some set point changes that step by 2 degrees, such as the bedroom, which comes on at 18 degrees at waking up time and then goes to 20 degrees after we are up but before we come back to dress for work, and optimum start does operate with this differential, and typically steps up the set point about half an hour before 20 degrees is scheduled, and does make it in time.

    Quote Originally Posted by paulockenden View Post
    When your rooms aren't being used (at night) I'd be temped to sent them much lower than 16. What's the point of heating spaces that aren't occupied?

    P.
    16 does seem quite high. One of the advantages of optimum start is that (in theory) you can set the overnight temperatures of unoccupied rooms as low as you want and it will be smart enough to turn the system back on in time to get it back up to the set point.

    I've settled on 12 degrees for unused rooms at night, partly as a poor mans frost protect as the boiler does not have frost protection (must do something about that...) and I've found that on moderate nights (down to about 0) the rooms do not get that low and thus the heating does not come on for those rooms, but if we get a really cold night like -5 the rooms get cold enough to trigger the heating to come on to maintain 12 degrees in some rooms - but they only require a low boiler duty cycle to do so, but enough to give some measure of frost protection...

  7. #7
    Automated Home Lurker
    Join Date
    Jan 2016
    Posts
    3

    Default

    Quote Originally Posted by paulockenden View Post
    When your rooms aren't being used (at night) I'd be temped to sent them much lower than 16. What's the point of heating spaces that aren't occupied?

    P.
    There are several discussions regarding if it is better to maintain a constant temperature and let work the system at minimum or turn off and on and have the system working at the max power for a certain period. Unfortunately, I am not able to say exactly which strategy is the best one.

    Quote Originally Posted by Cchris View Post
    I would never anticipate that a single room would take that long to heat using radiators.
    The room is a large room which communicate with other areas without a door to close. However, the problem I have is that the system during the start period is not running at maximum and I don't understand the reason. As I wrote, the system not open the valves at 100% and it is not a full blast, which means lukewarm radiators for at least the first hour. That's why is taking that long.

    I am now making a new experiment letting go down the temperature to 14 degrees during the night and turning on at 18 increasing the warm time up to 4 hours to see what's happen.

    But, I have now a doubt. All the other rooms work well but they are all rooms with a single sensor. The one having problems has two valves using the controller as thermometer. Is there any particular setting to do in this case?

    A.

  8. #8
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,894

    Default

    Quote Originally Posted by GAndrea View Post
    There are several discussions regarding if it is better to maintain a constant temperature and let work the system at minimum or turn off and on and have the system working at the max power for a certain period. Unfortunately, I am not able to say exactly which strategy is the best one.
    The answer is pretty clear - heat loss is proportional to the temperature differential between the inside of the room and the outside of the room.

    If it's zero degrees outside and you maintain the room at 10 degrees you use half the energy to maintain this 10 degree differential than you would to maintain the 20 degree differential of the room being 20 degrees and outdoors being zero degrees.

    Letting a room cool down over night and then having to heat it up again the next morning definitely uses less energy than keeping it warm all night.

    Condensing boilers do complicate things slightly because they tend not to run in condensing mode during the initial heatup phase if your flow temperature is set high, but the gain from operating in condensing mode is no more than about 20%, and to really gain the full benefit of a lower flow temperature when the zones are in "proportional" control mode would require an OpenTherm gateway which can actually specify a low flow temperature when demand is low.

    With a BRD91 it will use TPI control to attempt to approximate flow temperature modulation but it is not very accurate compared to using an OpenTherm bridge.
    The room is a large room which communicate with other areas without a door to close. However, the problem I have is that the system during the start period is not running at maximum and I don't understand the reason. As I wrote, the system not open the valves at 100% and it is not a full blast, which means lukewarm radiators for at least the first hour. That's why is taking that long.
    How are you determining that the valves are not fully open ? If you set the HR92 to more than 2 degrees above the current temperature then unlock it and remove it from the radiator after the motor has finished turning, can you manually open the valve significantly further by turning the black gear and hear the flow increase significantly in the radiator ?

    If so you need to use "Full stroke" mode, as you apparently have valves that require a greater pin travel for the valve to fully open. To do this hold down the button for 10 seconds until the configuration menu comes up, choose option 6, stroke, changing it's value to 1, then turn to the exit option and press the button again.

    After doing this I would recommend unlocking the HR92 and lifting it off the radiator, turn the black wheel fully anti-clockwise to fully open the radiator valve then lock the HR92 back on. After about a minute it will perform a calibration where it re-learns the full travel of the pin in the valve.

    From now on it will operate the valve pin over its maximum possible travel rather than about 70% of its travel that it uses by default, so when it opens it will open as much as possible and it will also close down a bit harder as well in the closing direction.

    It may take the HR92 a couple of days of normal use for it to calibrate itself to the new operating point for the valve - during this time it might overshoot or undershoot the target temperature a bit but it will adjust after a few days.

    Despite all my radiator valves being the same make and model, and only a year old, I have one valve where I have had to put the HR92 into full stroke mode because it doesn't always open sufficiently to allow enough flow to get up to temperature, like you describe. In full stroke mode it works fine, and none of my other valves need full stroke mode. (It's possible the pin is a little sticky)

    I am now making a new experiment letting go down the temperature to 14 degrees during the night and turning on at 18 increasing the warm time up to 4 hours to see what's happen.

    But, I have now a doubt. All the other rooms work well but they are all rooms with a single sensor. The one having problems has two valves using the controller as thermometer. Is there any particular setting to do in this case?
    Be careful that you aren't being fooled by that room having a remote sensor when all your other rooms use the HR92 for the temperature sensor.

    Measuring the temperature at the radiator gives a very different impression of how quickly the room warms up compared to measuring the temperature remotely. The remote sensor gives a "truer" indication of the temperature of the room and its warm up time, whereas measuring the temperature at the radiator will make the room appear to warm up much quicker than it really does, and seem warmer than it really is during that warm up time.. See the following thread for some discussion on this:

    http://www.automatedhome.co.uk/vbull...ng-temperature

    I bet that if you go back to using an HR92 as the temperature sensor in the room you currently use the remote sensor will make it seem like the room is warming up much quicker, but in reality it is just measuring the warm side of the room, like all your other rooms.

    If you have heavy, solid internal walls, it can take a long time for the entire room to truly warm up, and the remote sensor accurately indicates this.
    Last edited by DBMandrake; 21st January 2016 at 01:13 AM.

  9. #9
    Site Sponsor The EVOHOME Shop's Avatar
    Join Date
    Dec 2014
    Location
    Powys, Mid Wales
    Posts
    479

    Default

    Quote Originally Posted by DBMandrake View Post
    If so you need to use "Full stroke" mode, as you apparently have valves that require a greater pin travel for the valve to fully open. To do this hold down the button for 10 seconds until the configuration menu comes up, choose option 6, stroke, changing it's value to 1, then turn to the exit option and press the button again.
    Be careful doing and advising this. I have never had to use or advise using 'Full-stroke mode'. It is more than likely when the HR92 radiator controller was put on the valve baseplate initially, the black hand wheel was not all the way wound anti-clockwise - so when the radiator controller was put back onto the valve baseplate and has not calibrated correctly. I would suggest doing this first.

    The 'stroke' on the HR92 is set to 4mm governed by the stops on the valve baseplate and changing to 'full-stroke' just increases the torque settings of the motor and decreases battery life of the HR92 - nothing else. It is more than likely the radiator valve is faulty if you have to do this, so I suggest replacing the valve.

  10. #10
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,894

    Default

    Not wanting to contradict you (I don't do this for a living after all! ) but I don't think things are quite as clear cut as you are implying.

    Quote Originally Posted by The EVOHOME Shop View Post
    Be careful doing and advising this. I have never had to use or advise using 'Full-stroke mode'. It is more than likely when the HR92 radiator controller was put on the valve baseplate initially, the black hand wheel was not all the way wound anti-clockwise - so when the radiator controller was put back onto the valve baseplate and has not calibrated correctly. I would suggest doing this first.
    I have been through the calibration procedure many times and I can assure you that I do turn the black hand wheel fully anti-clockwise before fitting the HR92, so this is not the issue.

    The 'stroke' on the HR92 is set to 4mm governed by the stops on the valve baseplate and changing to 'full-stroke' just increases the torque settings of the motor and decreases battery life of the HR92 - nothing else. It is more than likely the radiator valve is faulty if you have to do this, so I suggest replacing the valve.
    Again, my testing suggests this is not the case.

    It's true that enabling full-stroke mode does increase the motor torque a small amount - you can hear it from the speed increase. However it does also increase the number of revolutions it will rotate from fully closed to fully open, in both directions. Eg it will close down harder when closing the valve (probably due to the increased motor torque) but it will also open further when opening the valve. It actually says this in the installation manual as well:

    Parameter 6 – Valve stroke
    The radiator controller operates with the optimum valve
    stroke set in the factory.
    If the entire valve stroke is to be used or if the valve does
    not open completely
    , activate the full-stroke mode.
    I have tested this back and forth multiple times now - in normal stroke mode it does not rotate the wheel fully anti-clockwise when opening, I can unlock it and lift it off and I still have another revolution or more available to turn the wheel. However in full stroke mode it does definitely open the valve fully until it hits the limit stop built into the HR92 base, as the installation manual implies. You actually hear it stop suddenly (and see a slight jump) when it gets to the limit stop in full stroke mode that you don't see in normal mode.

    As far as I can see there is nothing wrong with the valve, and it is only a year old anyway. Different makes of valves have different operating points, it stands to reason that on some valves that the fully open operating point might be close to the limit of travel of the HR92 base, just due to the precise pin dimensions on the valve... in fact that is the case on my valves when listening to the flow and manually turning the wheel. I'm sure on other models of valves with slightly different pins the fully open point is probably two or three turns away from fully extended and thus doesn't need full stroke.

    The operating point of some of the other valves in the house (all the same make, model and age) are very slightly different, but we're probably only talking half a millimetre difference in the tolerance of the pin extension.

    Draining down the system in the winter to replace a valve that isn't really faulty, (but might have marginal dimensional compatibility with the HR92 base, granted) is just not going to happen. I'm happy to just set it to full stroke mode. If it wasn't occasionally needed to cope with some 3rd party valves they wouldn't have added it as a user configurable setting...
    Last edited by DBMandrake; 21st January 2016 at 01:56 PM.