    Evohome UFH question

    I have an Evohome install with all rads fitted with HR92s (9 in total). The boiler is a Potterton Ideal 50 as a sealed system with Megaflo for HW and all radiators on the same run of pipework.

    We are planning a kitchen renovation and one option I'd like to explore is to replace the existing rad with a wet UFH solution. From reading, it seem important (due to the flow temperature requirements) that the UFH and rads can be independently controlled.

    My simple question is would adding a wet UFH system to my exiting rad pipework in place of the kitchen rad, with a HCC80R work (assuming that all the other rads remain controlled by HR92s so that the UFH would be able to call for heat independently of the rads when required)

    Apologies for the naive question but my Honeywell installer is proving difficult to get hold of at the moment
  • top brake
    Automated Home Legend
    • Feb 2015
    • 837

    #2
    UFH needs a seperate blended temperature circuit, job for an experienced installer
    I work for Resideo, posts are personal and my own views.

    Comment

    • Cchris
      Automated Home Sr Member
      • Nov 2015
      • 95

      #3
      As above, its a seperate circuit. You can't use boiler or radiator temperature water in UFH.

      You have a manifold to control the temperature flowing round the pipes in the underfloor. They look like this:

      manifold.jpg

      At the bottom left you will see a white temperature control, this is where the flow and return to the boiler fit and the temperature of the water flowing round the underfloor part is controlled. The seperate pump you can see here then pushes water round the flow and return rails (orange and white heads in this picture) and controls the temperature by taking only the heat it needs from the boiler flow and return.

      The HCC80R controls this manifold, opening and closing valves to relevant zones (if you have more than one zone on the manifold).

      Comment

      • The EVOHOME Shop
        Site Sponsor
        • Dec 2014
        • 483

        #4
        Originally posted by Cchris View Post
        As above, its a seperate circuit. You can't use boiler or radiator temperature water in UFH.

        You have a manifold to control the temperature flowing round the pipes in the underfloor. They look like this:

        [ATTACH=CONFIG]670[/ATTACH]

        At the bottom left you will see a white temperature control, this is where the flow and return to the boiler fit and the temperature of the water flowing round the underfloor part is controlled. The seperate pump you can see here then pushes water round the flow and return rails (orange and white heads in this picture) and controls the temperature by taking only the heat it needs from the boiler flow and return.

        The HCC80R controls this manifold, opening and closing valves to relevant zones (if you have more than one zone on the manifold).
        For a single UFH zone you can also use a 'mixed' UFH circuit with mixed circuit controls (ideal when you have a radiator circuit at a higher temperature and want a much more accurate temperature control of an UFH circuit). The evohome system even has a mixed circuit controller that we sell (HM80) just for this particular job. This is normally a professional installers job as the flow rate for the UFH circuit needs to be calculated, mixing valve and actuator correctly sized, etc but certainly there are more (accurate) control options available for UFH control of a single UFH zone than a fixed UFH blending valve.

        Look at page 20 of the old evotouch Application Manual for a diagrammatic overview of a mixed UFH circuit - http://www.honeywelluk.com/Documents...ion_Manual.pdf

        Comment

        • philipW99
          Automated Home Lurker
          • Apr 2015
          • 8

          #5
          I'm in exactly the same position as the OP. With the exception that the boiler is a Valliant. My installer, who has done previous UFH installs, does not know evohome. My question is how does the HCC80R call for heat from the boiler? Is it to be hardwired or will it operate via a BDR91? If the latter will it trigger the existing central heating BDR91 or will I need a new BDR91? I know that the installer will be connecting the pipework for the HCC80R to the boiler prior to the zone valves for the CH and HW.

          Thanks for any insight you can give.

          Comment

          • The EVOHOME Shop
            Site Sponsor
            • Dec 2014
            • 483

            #6
            Originally posted by philipW99 View Post
            I'm in exactly the same position as the OP. With the exception that the boiler is a Valliant. My installer, who has done previous UFH installs, does not know evohome. My question is how does the HCC80R call for heat from the boiler? Is it to be hardwired or will it operate via a BDR91? If the latter will it trigger the existing central heating BDR91 or will I need a new BDR91? I know that the installer will be connecting the pipework for the HCC80R to the boiler prior to the zone valves for the CH and HW.

            Thanks for any insight you can give.
            Depending how evohome is configured both options are possible with the HCC80R. The BDR91 'boiler relay' approach is my preferred approach. How is your current BDR91 being used? With evohome or another Honeywell thermostat?

            Comment

            • philipW99
              Automated Home Lurker
              • Apr 2015
              • 8

              #7
              Thanks for the advice. Existing config is 1 BDR91 for HW (coupled with a CS92 sensor) and a further BDR91 for the CH system which has 9 HR92 valves/sensors on the radiators. Its an S plan system. So, should I bind the HCC80R to the existing BDR91 for the CH system? If I do then it will open the zone valve for the CH when the UFH calls for heat. Is that OK? Or should I have a new BDR91 bound to the HCC80R that will trigger the boiler but not the zone valve.

              Thanks again for your input.

              Comment

              • The EVOHOME Shop
                Site Sponsor
                • Dec 2014
                • 483

                #8
                Originally posted by philipW99 View Post
                Thanks for the advice. Existing config is 1 BDR91 for HW (coupled with a CS92 sensor) and a further BDR91 for the CH system which has 9 HR92 valves/sensors on the radiators. Its an S plan system. So, should I bind the HCC80R to the existing BDR91 for the CH system? If I do then it will open the zone valve for the CH when the UFH calls for heat. Is that OK? Or should I have a new BDR91 bound to the HCC80R that will trigger the boiler but not the zone valve.

                Thanks again for your input.
                No need to bind HCC80R to anything other than evohome when prompted at the correct time through 'ADD ZONE' (see page 24, 25 & 26 of the evohome Installation Guide). In your above configured situation, the Heating Motorised Zone Valve will open when there is UFH demand.

                Comment

                • Stan
                  Automated Home Lurker
                  • Mar 2018
                  • 2

                  #9
                  Hi guys, this might be correct thread but I am not sure. I have a question:
                  Is it possible to add an HR92 to a zone controlled by Honeywell Underfloor Heating Controller HCC80R? Literally I want to install a radiator in the kitchen heated by wet underfloor system. I need this to boost performance of underfloor system, as in cold weather I don’t get enough output. Thank you in advance.

                  Comment

                  • rvb99
                    Automated Home Sr Member
                    • Oct 2017
                    • 74

                    #10
                    Originally posted by Stan View Post
                    Hi guys, this might be correct thread but I am not sure. I have a question:
                    Is it possible to add an HR92 to a zone controlled by Honeywell Underfloor Heating Controller HCC80R? Literally I want to install a radiator in the kitchen heated by wet underfloor system. I need this to boost performance of underfloor system, as in cold weather I don’t get enough output. Thank you in advance.
                    Have you tried increasing the ufh mixing ( manifold ) temperature . You can usually increase to around 45-50deg , still keeping the floor temp itself to the max recommended 26-27deg. Also check the flow/s for the hydraulic circuits. As a rough guide they should be the loop length / 40. Eg 80m loop should be 2-2.5 litres/min. This is a good link for rule of thumb calculations http://www.heatweb.com/techtips/Underfloor/underfloorheating.html
                    Last edited by rvb99; 21 March 2018, 10:15 PM.

                    Comment

                    • Stan
                      Automated Home Lurker
                      • Mar 2018
                      • 2

                      #11
                      Originally posted by rvb99 View Post
                      Have you tried increasing the ufh mixing ( manifold ) temperature . You can usually increase to around 45-50deg , still keeping the floor temp itself to the max recommended 26-27deg. Also check the flow/s for the hydraulic circuits. As a rough guide they should be the loop length / 40. Eg 80m loop should be 2-2.5 litres/min
                      Yes tried, its on maximum. My plumber says unlikely I will get more heat by adjustments. Just want to explore possibility of installing trench radiator along the patio doors which will create a warm curtain in this area, but not sure how to connect it and control by Evohome controller. I will need to connect the trench heater to the main flow of the boiler as other radiators in the house in order to get high temperature and the output, and then I can put HR92 on it and will need a separate temperature sensor. Then I will need to keep the UFH zone and this additional zone on the same program, but I am not sure whether they will work in tandem (one can switch off earlier or another, or may have some other issues). I though if I could put UFH and trench HR92 on the same zone, then they will definitely work in tandem, like multiradiator zone. Can you tell whether this mixed mode is supported?

                      Comment

                      • rvb99
                        Automated Home Sr Member
                        • Oct 2017
                        • 74

                        #12
                        I don’t believe you can mix hcc controller and HR92s in the same zone. You could I guess use one of the hcc ports to control a wired radiator actuator , rather than use the HR92. This will ensure they come on together , but the overal problem mixing ufh and radiators to have a warm floor and hot radiator will be balancing the system . The radiatior will heat up quickly and possibly heat the zone before the ufh has a chance to get going.

                        Comment

                        • joolscog
                          Automated Home Lurker
                          • Apr 2016
                          • 4

                          #13
                          Originally posted by The EVOHOME Shop View Post
                          Depending how evohome is configured both options are possible with the HCC80R. The BDR91 'boiler relay' approach is my preferred approach. How is your current BDR91 being used? With evohome or another Honeywell thermostat?
                          Hi - I find myself in a similar situation to the OP I think. I have an Evohome setup with controller, two BDR91s (1x Boiler Relay, 1x DHW with sensor) and 8xHR92s on the rads. Following some recent building work and change to the plumbing, I am no longer able to control the DHW with Evohome (long story for a different thread) and so now have a redundant BDR91. However, I now have wet UFH installed in two newly built rooms. The UFH is to be controlled by an HCC80R, and the two rooms (as two zones) will have TR87 room temp sensors. So, do I simply need to bind the HCC80R with the controller and add the TR87s to the new zones - and the UFH will take advantage of the existing BDR91 Boiler Relay?? Or do I need to add a BDR91 just for the UFH (and I'll repurpose the 'redundant' one for that if needed).

                          Am I correct to think that no additional BDR91 is needed and the existing Boiler Relay is sufficient?

                          Thanks for any help you can give.