If it only happens when one radiator is running it's possible that you have an automatic bypass valve whose differential pressure is set a bit too low - with only one radiator running most of the hot water output of the boiler will go straight back into the boiler heat exchanger again via the ABV without the 10-15 degree temperature drop that you would get if it only travelled through the radiator and back, losing heat along the way.
So for a given flow output temperature the average temperature in the heat exchanger is higher, this would make it more prone to kettling if there is any lime scale buildup. I found through trial and error that my system is a lot quieter if I set the ABV differential relatively high - about 0.5 bars. Although it increases the flow rate through the radiators when only one or two are open and thus produces a little bit more "hiss", the tendency to kettle is reduced by the higher pressure and it gurgles far less often than it did when it was set to 0.2 to 0.3 bars.