It sounds like something that happened to me early on. One of the HR92 is asking for heat; you need to figure out which one it is, and why. In my case the TRV valve was stuck shut, so the HR92 kept asking for heat because the room was colder than it wanted it to be and it wasn't warming up because hot water wasn't flowing.
Second thing, do you have any radiators without TRV/HR92? If so, then the water should still be able to flow through there, in which case your ABV may be set too "weak" and is triggering too easily, if that makes sense. I just recently tightened my ABV, which fixed a very noisy bathroom rad on the top floor -- I suspect the weight of the water was overcoming the ABV. It's now set to 5.2-ish (meters H2O).
Even if you tighten the ABV, you can still tell it is working when your Heating valve closes down. In my case, the pump on the boiler keeps going for another 15-20 seconds, and you can hear the water flowing through the ABV at that point.
The way I figured out how tight to make the ABV, was late at night (nice quiet house), with my ear right next to it (don't touch it with your ear, it's hot!), with the CH and boiler going, I started closing it until a hissing sound stopped. I then re-opened it a bit, and the hissing started again. So essentially I tightened it so there was no hissing, and hopefully that's job done.
My logical view is that there should be no water flowing through the ABV under normal operation, but rather only when flow is severely restricted (e.g. when all the TRVs are closed, the CH valve is closed).