Securitybyte
I have been watching the boiler over the last few evenings however and observed some quite odd cycling problems.
It goes like this:
- BDR91 calls for heat
- Boiler starts
- Flow temperature quickly rises from about 49C through to 60C in about 10 seconds (this is after it's been on a while - I've not watched it from a cold start)
- Then over a period of say 15 seconds*:
- 64C flow, 56C return
- 65 flow, 56.5 return
- 66 flow, 57 return
- 67 flow, 58 return
- Status 204 - 'System waiting, primary flow temperature above setpoint'
- Burner stops
- Pump continues to run at about 60% for a few minutes, with a return of approx 50C
- After 5 or so minutes - Lather, rinse, repeat
*Sometimes it runs for longer - 5 minutes or more, but most frequently I've watched it stop after between 2 and 15 seconds.
The boiler setpoint is set to 63C - the economical temperature recommended for the boiler. I have tried turning it up but it made no difference - the flow temp still exceeded the setpoint.
During this time, the rooms are still below their set points and the BDR91 is still lit up.
Initially I thought it was because I only had one radiator on, however I've tested it with 5 radiators on this evening and it is the same story.