Originally Posted by
bruce_miranda
I have pump over run set to 20 mins which matches my maximum wait time, so that the pump never switches off unless there is absolutely no heat demand. Also 20 mins is enough time to have the heat slowly ramp down.
The OT bridge assumes all boilers are Heat Only, so having studied the eBUS messages in detail, I can confirm they never send the HW demand flag which would make your d.22 show as 1. The only way to do HW priority is by wiring the BDR91 and the motorised valves appropriately. OT Bridge goes from 10 no demand to 90 full demand. Some Vaillant controllers start from 0, some go from 10.