    Evohome + Opentherm v Evohome + Boiler Outside Weather Compensation

    Hi all,

    Been browsing this site for while but this is my first post (and apologies as it is quite long!). Great forum with loads of useful information.

    My query relates to my set up. I have an Ideal Vogue System 32 boiler in a traditional S plan set up for heating and hot water cylinder.

    The Evohome controls the heating 2 way valve via a BDR91 relay box. The hot water 2 way valve remains controlled by the original timer unit.

    I have HR92's fitted to approximately half of the rads in my house which is quite large (approx 260 square metres) with the other half on TRVs (landing, hall, etc) and a couple (bathrooms) with no TRV at all. Some rooms with TRVs are affectively are basically on frost protection settings as they are not currently used.

    The system works pretty well but some of the posts on here have got me thinking about helping my boiler run in condensing mode more of the time.

    I currently have the output flow set at 65°C to ensure it can sufficiently heat the hot water.

    This means that when just running the heating I think the boiler will spend a fair amount of time with a return temperature in the mid 50s and not condensing so well.

    I'm still playing around with balancing rads to get reasonable temperature drops for the return but but am now also thinking about adding an outside temperature sensor or the opentherm bridge so the boiler can modulate the flow temperature automatically.

    I would estimate that a CH flow of approx 65° is only really needed when it is approaching 0°C outside and the house would comfortably warm up with lower CH temperatures as external temperature increases.

    My initial thinking was therefore to add the outside temperature sensor to my boiler as it is all set up to take one and they are only £25. The boiler would then modulate the CH flow temperature accordingly with me picking whichever curve is most appropriate.

    The only potential issue here is that the Evohome system will not be aware of this and therefore can't take into account the fact that the CH flow temperature is being changed. However this affect might be self cancelling i.e. on a cold day the boiler will give high temp CH flow and evohome will control from it's perspective as it does now. On a warmer day the boiler will lower the CH flow temp which evohome will not be aware of but at the same time, because it is warmer outside, the heat loss from the rooms will be lower and therefore the rooms might warm at the same rate regardless of the fact that the flow temperature has reduced..............

    I've tried researching the opentherm option (as my boiler has the input for this too) but I'm struggling to understand exactly what the evohome system will do differently if I replace the BDR91 with an opentherm unit. I understand the principle of opentherm and that it should allow the opentherm controller to control boiler burner modulation for exampl but some of the feedback around the web seems mixed.

    At the minute I'm leaning towards the outside temperature sensor option but any advice on either option would be much appreciated.

    Thanks
    Steve
  • top brake
    Automated Home Legend
    • Feb 2015
    • 837

    #2


    Will explain

    Originally posted by scut0 View Post
    Hi all,

    Been browsing this site for while but this is my first post (and apologies as it is quite long!). Great forum with loads of useful information.

    My query relates to my set up. I have an Ideal Vogue System 32 boiler in a traditional S plan set up for heating and hot water cylinder.

    The Evohome controls the heating 2 way valve via a BDR91 relay box. The hot water 2 way valve remains controlled by the original timer unit.

    I have HR92's fitted to approximately half of the rads in my house which is quite large (approx 260 square metres) with the other half on TRVs (landing, hall, etc) and a couple (bathrooms) with no TRV at all. Some rooms with TRVs are affectively are basically on frost protection settings as they are not currently used.

    The system works pretty well but some of the posts on here have got me thinking about helping my boiler run in condensing mode more of the time.

    I currently have the output flow set at 65°C to ensure it can sufficiently heat the hot water.

    This means that when just running the heating I think the boiler will spend a fair amount of time with a return temperature in the mid 50s and not condensing so well.

    I'm still playing around with balancing rads to get reasonable temperature drops for the return but but am now also thinking about adding an outside temperature sensor or the opentherm bridge so the boiler can modulate the flow temperature automatically.

    I would estimate that a CH flow of approx 65° is only really needed when it is approaching 0°C outside and the house would comfortably warm up with lower CH temperatures as external temperature increases.

    My initial thinking was therefore to add the outside temperature sensor to my boiler as it is all set up to take one and they are only £25. The boiler would then modulate the CH flow temperature accordingly with me picking whichever curve is most appropriate.

    The only potential issue here is that the Evohome system will not be aware of this and therefore can't take into account the fact that the CH flow temperature is being changed. However this affect might be self cancelling i.e. on a cold day the boiler will give high temp CH flow and evohome will control from it's perspective as it does now. On a warmer day the boiler will lower the CH flow temp which evohome will not be aware of but at the same time, because it is warmer outside, the heat loss from the rooms will be lower and therefore the rooms might warm at the same rate regardless of the fact that the flow temperature has reduced..............

    I've tried researching the opentherm option (as my boiler has the input for this too) but I'm struggling to understand exactly what the evohome system will do differently if I replace the BDR91 with an opentherm unit. I understand the principle of opentherm and that it should allow the opentherm controller to control boiler burner modulation for exampl but some of the feedback around the web seems mixed.

    At the minute I'm leaning towards the outside temperature sensor option but any advice on either option would be much appreciated.

    Thanks
    Steve
    I work for Resideo, posts are personal and my own views.

    Comment

    • scut0
      Automated Home Jr Member
      • Mar 2016
      • 10

      #3
      Thanks for the link. Has anyone had good experience of the opentherm bridge and can confirm that it does regulate flow temperature in conjunction with the evohome controller? Just that some of the feedback on the internet implies it may not?

      And has anyone used a boiler outside weather compensation system in addition to the evohome doing the zone control, if so did it work well together with the weather compensation not negatively affecting evohomes ability to control the room temperatures in each zone?

      Comment

      • top brake
        Automated Home Legend
        • Feb 2015
        • 837

        #4
        Originally posted by scut0 View Post
        Thanks for the link. Has anyone had good experience of the opentherm bridge and can confirm that it does regulate flow temperature in conjunction with the evohome controller? Just that some of the feedback on the internet implies it may not?

        And has anyone used a boiler outside weather compensation system in addition to the evohome doing the zone control, if so did it work well together with the weather compensation not negatively affecting evohomes ability to control the room temperatures in each zone?
        Careful who you listen to in the inter-webs. Any example?

        Will modulate your appliance no problems.
        I work for Resideo, posts are personal and my own views.

        Comment

        • The EVOHOME Shop
          Site Sponsor
          • Dec 2014
          • 483

          #5
          Originally posted by scut0 View Post
          Thanks for the link. Has anyone had good experience of the opentherm bridge and can confirm that it does regulate flow temperature in conjunction with the evohome controller? Just that some of the feedback on the internet implies it may not?

          And has anyone used a boiler outside weather compensation system in addition to the evohome doing the zone control, if so did it work well together with the weather compensation not negatively affecting evohomes ability to control the room temperatures in each zone?
          AS TB says, OT Bridge should work fine. I have a weather compensated ground source heat pump and evohome seems to work just fine with this. If I could, I would have the R8810A1018 OpenTherm Bridge on my system.

          Comment

          • StuartG
            Automated Home Jr Member
            • Mar 2015
            • 45

            #6
            I've replaced my BDR91 with an OpenTherm bridge this evening by adding a VR33 to a Vaillant boiler. It has all fired up ok and everything seems to be talking.

            It's too early to say whether this is a "good experience", but I've had Evohome for about nine months with the simple relay, so I'm interested to now see how things compare.

            Comment

            • scut0
              Automated Home Jr Member
              • Mar 2016
              • 10

              #7
              Thanks for replies all. Am tempted to try OpenTherm, going to hunt around for somebody with actual experience of the Open Therm Bridge

              Be good to here more from you Stuart after you've had time to compare pre and post Open Therm.

              I wonder how weather compensation via boiler would work together with Open Therm via Evohome...................

              Comment

              • top brake
                Automated Home Legend
                • Feb 2015
                • 837

                #8
                i have a similar setup to Stuart and its been working for 3 months plus and regularly see 46 deg flow temps
                I work for Resideo, posts are personal and my own views.

                Comment

                • StuartG
                  Automated Home Jr Member
                  • Mar 2015
                  • 45

                  #9
                  So far every time I've looked at the boiler status the target is 70+. I can see from the boiler diagnostics that this target is coming from open therm as it reports the value.

                  Comment

                  • top brake
                    Automated Home Legend
                    • Feb 2015
                    • 837

                    #10
                    Originally posted by StuartG View Post
                    So far every time I've looked at the boiler status the target is 70+. I can see from the boiler diagnostics that this target is coming from open therm as it reports the value.
                    Are you sure you have connected the VR33 correctly and removed the switched live?

                    It is rather cold at the moment so it might need to run the boiler flat out. All depends on your system, boiler size....
                    I work for Resideo, posts are personal and my own views.

                    Comment

                    • StuartG
                      Automated Home Jr Member
                      • Mar 2015
                      • 45

                      #11
                      Think it is all connected right. I've powered down the original BDR91 heating relay, and for good measure disconnected the switched live inside the boiler. The Vaillant diagnostics report the module as detected, and its picking up a target temperature as coming from the remote controller. In terms of comfort in the house everything seems pretty much as it was before, so the main thing is that we still have heating!

                      Update: boiler target currently 51C. House is warm and starting to shutdown for the night, so it's easing back. So it definitely looks like it's working as it should!
                      Last edited by StuartG; 10 March 2016, 11:13 PM.

                      Comment

                      • top brake
                        Automated Home Legend
                        • Feb 2015
                        • 837

                        #12
                        Originally posted by StuartG View Post
                        So far every time I've looked at the boiler status the target is 70+. I can see from the boiler diagnostics that this target is coming from open therm as it reports the value.
                        Originally posted by StuartG View Post
                        Think it is all connected right. I've powered down the original BDR91 heating relay, and for good measure disconnected the switched live inside the boiler. The Vaillant diagnostics report the module as detected, and its picking up a target temperature as coming from the remote controller. In terms of comfort in the house everything seems pretty much as it was before, so the main thing is that we still have heating!
                        It will modulate to max when there is a hot water demand. How long has it been installed with OT?
                        If you need help please refer to this doc http://www.honeywelluk.com/documents...rt_process.pdf
                        I work for Resideo, posts are personal and my own views.

                        Comment

                        • StuartG
                          Automated Home Jr Member
                          • Mar 2015
                          • 45

                          #13
                          Think we posted at the same time. Just went to see what it is up to, and it's now getting a target of 51C from evohome, so it is working fine. Thanks for the link. Will check it out!

                          Comment

                          • paulockenden
                            Automated Home Legend
                            • Apr 2015
                            • 1719

                            #14
                            It's good to know that the VR33 works with UK supplied boilers because there's other places on the Internet which suggest that because of different firmware on this side of the channel it won't work properly.

                            That always seemed like a silly argument. Nice to have suspicions confirmed.

                            Comment

                            • top brake
                              Automated Home Legend
                              • Feb 2015
                              • 837

                              #15
                              Originally posted by paulockenden View Post
                              It's good to know that the VR33 works with UK supplied boilers because there's other places on the Internet which suggest that because of different firmware on this side of the channel it won't work properly.

                              That always seemed like a silly argument. Nice to have suspicions confirmed.
                              I was told the same. It was even suggested that it may invalidate the warranty. Utter bilge.
                              Manufacturer's own part supplied within eu...
                              I'll let you draw your own conclusions why this misleading comment may have been made!
                              I work for Resideo, posts are personal and my own views.