Originally posted by bruce_miranda
View Post
The 'official' way is to wire the CH BDR91 to the CH zone valve, as you've described, but then bind as as the heating demand valve, not the boiler relay.
Alternatively, wire that BDR directly to the boiler, and bind it as a boiler relay. But if you do this you MUST latch the CH valve open.