OK so the HGI80 has allowed me to find at least one issue with my installation. My Kitchen UFH is configured as a separate zone using a Y87RF temperature sensor and a BDR91 relay as the actuator zone valve. What I noticed is that when I turn on the other zones, in Domoticz along with that Zone Relay going ON, the CH Valve Relay turns on and one of the two Boiler named Relays turn ON.
When on the other hand I turn the Kitchen Zone on. There is no Zone Relay that turns on, instead the other Boiler Relay Device turns on. So Domoticz seems to read the zone valve BDR91 as a device named Boiler. But what I was surprised to see was the CH valve, the other Study named device relay and the other Boiler named device Relay also turn on. When I looked at my 3 BDR91s, sure enough the UFH BDR91 was on, but what I wasn't expecting was for the CH Valve BDR91 also to come on.
My CH Valve relay seem to be double bound to both the CH Valve as part of the S plan set-up and the Kitchen UFH zone valve. I'll fix that in the morning. I think this is what seems to be causing the duplicate entry called Study Relay.
What I still haven't been able to explain are the 5 devices called Zone. 4 of them are constantly showing ON (value 200). And one seems to move around from OFF to 90 to 106 to 122. With seemingly no co-relation to what else is going on.
When on the other hand I turn the Kitchen Zone on. There is no Zone Relay that turns on, instead the other Boiler Relay Device turns on. So Domoticz seems to read the zone valve BDR91 as a device named Boiler. But what I was surprised to see was the CH valve, the other Study named device relay and the other Boiler named device Relay also turn on. When I looked at my 3 BDR91s, sure enough the UFH BDR91 was on, but what I wasn't expecting was for the CH Valve BDR91 also to come on.
My CH Valve relay seem to be double bound to both the CH Valve as part of the S plan set-up and the Kitchen UFH zone valve. I'll fix that in the morning. I think this is what seems to be causing the duplicate entry called Study Relay.
What I still haven't been able to explain are the 5 devices called Zone. 4 of them are constantly showing ON (value 200). And one seems to move around from OFF to 90 to 106 to 122. With seemingly no co-relation to what else is going on.