You only need the HCC80R is you are using a single manifold and trying to create zones. Even there you can be clever and use BDR91s with wired acutators if you just need a couple of zones.
Hello,
I'm fairly new here.
I am renovating (slowly) an old property and have Evohome.
The heating is a system boiler, 50kw approx. Unvented cylinder and radiators over 3 floors with 5 zones and HW controlled at the moment.
I have electric UFH in 3 room's which I plan to "trigger" using BDR91's, all circuits are under 1kw, so no need for a contactor. I would then use a room stat in that room, I trust this is a sound plan?
I am just doing the next 2 rooms which will be wet UFH, I purchased 2 x Y87RF2024 kits, to get the above room stats, so have 2 x BDR91 relays surplus to requirements.
Do I need to use the HCC80R? Or can I just use the BDR relays, connected to MT4/8 valves?
Does anybody have a good link for wet UFH manifolds?
Many thanks for any help.
Regards
Ricky
You only need the HCC80R is you are using a single manifold and trying to create zones. Even there you can be clever and use BDR91s with wired acutators if you just need a couple of zones.
Thanks a lot for your reply. I think this is the route I'll go, I will have one manifold for the 2 or 3 zones, but it'll be cheaper and better to use a couple of these kits,
http://www.screwfix.com/p/honeywell-...mpatible/2230h
I have the BDR and stat included.
I'll let you know how I get on.
But you still need to add the price of the wired actuators
But come to think of this. How would the bdr91 supply power to the wired actuators and the actuators need a way to sense partial open and close too, not just on and off. So I don't think connecting them to a BDR91 will work.