    With most of the other wireless devices there's instructions about how to clear any existing bindings (usually involving a 15 second button press), but I can find no such information for the CS92 hot water sensor.

    Does this mean it isn't possible to clear the existing binding and do a full reset?

    Thanks,

    P.

  2. #2
    Automated Home Legend
    Join Date
    Jan 2015
    Location
    NE UK
    Posts
    1,025

    Default

    I was not convinced holding down the button did it for me but taking the batteries out did for all contact had disappeared when I put them back until I re-bound. Evohome is a great product but instructions, certainly in the original documentation have not been user friednly. Honeywell probably thought people like us would not be doing the installation!

  3. #3
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,594

    Default

    There's a brilliant PDF out there giving binding details for all of the devices. But (despite being quite technical) it misses how to clear bindings. It assumes, for example, that HR92s are unbound. If this was added (for all devices) it would be just what we need.

  4. #4
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,829

    Default

    I might be wrong, but I don't think it's necessary to unbind a device that's a temperature sensor only. ("Unbinding" at the controller is sufficient) The "binding" is simply the controller being told to "listen" to the periodic broadcasts of that sensor - temperature sensors send their temperature as broadcasts to anyone who will listen. Binding just tells the controller to listen to this sensor for this zone.

    Any devices that are actuators or set point controllers (a DTS92 is both a temperature sensor *and* a set point controller) do need unbinding at both ends to properly clear things though.

    An example of this is if you use a DTS92 and then change the temperature sensor for the zone to another device (like an HR92) the controller and HR92 will now report the temperature measured at the HR92 while the DTS92 will continue to report its own measured temperature. However it can still control the set point of the zone and retrieve the current set point (by pressing up or down) even though it is no longer the nominated temperature sensor. (It is not aware that it is not - it is still broadcasting a temperature measurement that is just being ignored)
    Last edited by DBMandrake; 8th October 2016 at 10:19 PM.

  5. #5
    Automated Home Lurker
    Join Date
    Oct 2016
    Posts
    8

    Default

    Important to delete previous binding on BDR91 due to multiple binding slots. Is also possible on HCC80R, HR92 and RFG100 but seldom required. CS92, DT92 and Y87, overwritten on new binding.

  6. #6
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,829

    Default

    I'm not sure you're correct with the DTS92 - if you simply bind a different temperature sensor to the zone at the controller the DTS92 will still continue to act as a set point controller. So if you are taking it out of service you really ought to unbind it, and it does have a clear option to do so.

  7. #7
    Automated Home Lurker
    Join Date
    Oct 2016
    Posts
    8

    Default

    with all devices binding creates a 2 way comms, if you stop using a device it needs to be powered down or it has the possibility of flood broadcasting causing other issues. The DTS92 recognises what it is bound to, eg evo, BDR91, HCC80R and runs different firmware, hence the requirement to 'clr' previous settings before binding to something new. if you are re binding it is not necessary but is a good practice.