    I find your responses to be arrogant rather than helpful, the complete the opposite of those from DBMandrake, probably due to your low self-esteem and perceived knowledge in some areas, such that when your challenged you respond is this way.

    As to 'stomping in' and 'insisting' , perhaps you should learn to read and understand properly and understand a context then you will have seen that I used the word 'postulated' more than once, but clearly on this forum or the world according to you, no-one can challenge or discuss anything especially if you disagree with it.

    Now that you have resorted to that form of response and I hope others note your arrogance too, I will now ignore any of your responses on the basis they are unhelpful and from someone I do-not wish to converse with.

    Your the 'embarrassed' one...

  2. #22
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,828

    Default

    Quote Originally Posted by g6ejd View Post
    From what your saying it looks like only port 80 is open, or it is only the Honeywell cloud like server that accepts the connection then communicates either controller, but then that must use some form of routing protocol if not IP, could be keyed UDP as a connectionless process and rely on the underlying circuit reliability to achieve pseudo connected communications. I'll try to communicate with the controller using an ESP8266 or Arduino and see what it sends back to a client as a starting point. Getting the ESP8266 into minimal power consumption mode (I have found) requires a 10-min deep sleep otherwise quiescent average current consumption is so high that battery life of a year is impossible to achieve let alone 2 years! so I have empathy with the design choices made. As ever this technology needs to be a compromise.
    You still misunderstand - you won't be able to connect directly to the controller over IP. As I said earlier it exposes no open ports at all on its local IP address. (I just did a full port scan on it again last night to double check) It purely uses the IP connection over Wifi to make a persistent outgoing connection to Honeywell servers.

    It constantly reports all changes to the Honeywell servers including temperature measurements, set point changes, quick action mode changes (off, eco etc) and also any changes made to schedules. So the state stored at the Honeywell servers seems to be at most only a few seconds behind.

    API access is done over a standard HTTPS connection to Honeywell servers, so all API interactions are via Honeywell's online servers.

    This online API is now well understood and there are library bindings for many languages - the one I'm familiar with is watchforstock's python library which you can find here:

    https://github.com/watchforstock/evohome-client

    watchforstock is a forum member here although he doesn't seem to have posted recently. About 5 lines of python code will retrieve and display all the zone temperatures for example:

    Code:
    #!/usr/bin/python
    
    from evohomeclient import EvohomeClient
    
    client = EvohomeClient('email@domain.com', 'password')
    
    for device in client.temperatures():
        print device
    Will result in something like:

    Code:
    {'temp': 20.29, 'setpoint': 16.0, 'thermostat': u'EMEA_ZONE', 'name': u'Bathroom', 'id': 1377389}
    {'temp': 20.18, 'setpoint': 20.0, 'thermostat': u'EMEA_ZONE', 'name': u'Hall', 'id': 1643302}
    {'temp': 20.35, 'setpoint': 16.0, 'thermostat': u'EMEA_ZONE', 'name': u'Kitchen', 'id': 1643296}
    {'temp': 20.86, 'setpoint': 20.0, 'thermostat': u'EMEA_ZONE', 'name': u'Living Room', 'id': 1378782}
    {'temp': 17.15, 'setpoint': 5.0, 'thermostat': u'EMEA_ZONE', 'name': u'Main Bedroom', 'id': 1438045}
    Anything that the iPhone/Android apps can do can be replicated via the API. A notable shortcoming of the API is that heat demand information from HR92's cannot be obtained. (There is a field in the data structure returned from the server that looks like it should provide this, but it is not updated)

    The only way to communicate directly with the controller without going through Honeywells servers is using an HCI80 which will talk the same 868Mhz Rameses II protocol as the controller and other devices.

    This is a lot more complex to program for but it makes additional information available, such as heat demand being sent from HR92's to controller, and from controller to BDR91's. It also provides raw temperature measurements that aren't rounded to half a degree, although it's now possible to get that from the V1 Web API as well. It's possible to get temperature readings from all devices in a zone rather than just the "nominated" sensor that the controller has bound. It's also possible to simulate devices. I don't think it's possible to examine or modify schedules via HCI80 though.

    So depending on what you want to do, those are your two options. For many uses the Web API is sufficient and is very easy to use thanks to the libraries that are available now.

  3. #23
    Automated Home Guru
    Join Date
    Oct 2016
    Location
    Bath, UK
    Posts
    151

    Default

    Thank you once again for a very helpful response and your further explanation.

    I'd gathered the only direct communication with the Controller is via the Honeywell server, that's why I presumed they are using a UDP connection to the controller or something like that, as there must be an open port somewhere as it communicates on Wi-Fi network using IP but it will only respond to information with the correct key information, the Network Owl works like this for their Home heating system and I can now communicate with their controller via UDP but it took me some time to reverse engineer the connection and client calls.

    Your Python call examples will help me quickly get to the place I'd like to be, except I shall be using the Arduino and ESP8266 and C.

    Later today I'll set my network analyser running and then (indirectly) connect to the Controller and see what traffic is flowing to the IP address of my controller as I'm intrigued to see if it's in the clear (text) or what form it takes.

  4. #24
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,594

    Default

    There are no open ports on the controller. It opens an outbound https (TCP port 443, no UDP involved) connection to Honeywell's Alarmnet servers. The local source port is usually in the 30000 range, and is incremented with every new request (if the connection is broken). The local controller is a client, not a server.
    Last edited by paulockenden; 16th October 2016 at 01:28 PM.

  5. #25
    Automated Home Guru
    Join Date
    Feb 2016
    Posts
    212

    Default

    Hi,

    I just wanted to add a response to Bruce's comment:

    So my impression is that the protocol is a largely broadcast, acknowledgement free, idempotent protocol which relies heavily on very short infrequent scheduled transmissions to avoid collisions. When I one day get an HGI80 I'm curious to analyse the protocol in a bit more detail.
    I agree 100% with Bruce's description of the controller <-> device communication. I've spent a few months this year extending the Domoticz Evohome code which uses the Honeywell HGI80 usb device to communicate directly with all other Evohome devices within the home via the Ramses II protocol and Honeywell's own proprietary command language which is a little like going back to machine code. It seems designed to heavily minimise wireless messages and there is no handshaking or acknowledgement. The devices send out their status messages on an infrequent timed and event driven basis and there's also an occasional keep-alive message which is used to maintain a common time clock. If the controller hasn't heard from a device for a few hours then it eventually flags this as a device communication problem, but this takes many hours.

    Dan

  6. #26
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,828

    Default

    Quote Originally Posted by DanD View Post
    I just wanted to add a response to Bruce's comment:
    Who is Bruce ?

    I'm not sure if I've ever said my real name on this forum but for the record it's Simon.

  7. #27
    Automated Home Guru
    Join Date
    Feb 2016
    Posts
    212

    Default

    Oops, sorry Simon.

    You've confirmed something that I suspected, that I'm not really safe with a keyboard at the moment . I've got plenty of spare time just at the moment as I'm recovering from illness, but unfortunately I don't make a lot of sense . I definitely think that I should stay away from the Domoticz code for the next few weeks......

    Regards,
    Dan

  8. #28
    Automated Home Guru
    Join Date
    Oct 2016
    Location
    Bath, UK
    Posts
    151

    Default

    My Evohome controller reports itself on a network analyser as 'Gateway A130EE'. There is no IP traffic on the network from the Controller, but a huge amount of broadcast, which is what I expected. Here's a transcript of when I used my iPhone to increase a room temperature:
    62995 12:04:06 17/10/2016 1853.3337782 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    62997 12:04:06 17/10/2016 1853.3345366 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    62999 12:04:06 17/10/2016 1853.3356227 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63001 12:04:06 17/10/2016 1853.3362728 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63002 12:04:06 17/10/2016 1853.3367326 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63004 12:04:06 17/10/2016 1853.3401153 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63006 12:04:06 17/10/2016 1853.4258111 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -71 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63013 12:04:07 17/10/2016 1854.1426895 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -71 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63014 12:04:07 17/10/2016 1854.2450706 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -72 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63015 12:04:07 17/10/2016 1854.3469516 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -72 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63018 12:04:07 17/10/2016 1854.4498143 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -71 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63019 12:04:07 17/10/2016 1854.5522528 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -73 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63020 12:04:07 17/10/2016 1854.6546877 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -72 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63021 12:04:07 17/10/2016 1854.7565720 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -73 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63023 12:04:07 17/10/2016 1854.8594841 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -72 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63024 12:04:08 17/10/2016 1854.9618112 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -71 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63025 12:04:08 17/10/2016 1855.0642457 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -73 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63026 12:04:08 17/10/2016 1855.1666948 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -71 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63028 12:04:08 17/10/2016 1855.2299626 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63029 12:04:08 17/10/2016 1855.2307746 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63030 12:04:08 17/10/2016 1855.2312010 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63032 12:04:08 17/10/2016 1855.2318461 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63034 12:04:08 17/10/2016 1855.2698673 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -76 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63035 12:04:08 17/10/2016 1855.3771118 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63036 12:04:08 17/10/2016 1855.4795274 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63038 12:04:08 17/10/2016 1855.5576717 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63042 12:04:08 17/10/2016 1855.5600442 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63044 12:04:08 17/10/2016 1855.5615762 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63046 12:04:08 17/10/2016 1855.5622744 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63050 12:04:08 17/10/2016 1855.5700040 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63052 12:04:08 17/10/2016 1855.5798950 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63053 12:04:08 17/10/2016 1855.6866324 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -76 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63054 12:04:08 17/10/2016 1855.7846396 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63055 12:04:08 17/10/2016 1855.8352165 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63057 12:04:08 17/10/2016 1855.8549422 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -74 dBm, Rate = 24.0 Mbps
    63058 12:04:08 17/10/2016 1855.8559991 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63060 12:04:09 17/10/2016 1855.8848957 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63061 12:04:09 17/10/2016 1856.0036910 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63062 12:04:09 17/10/2016 1856.0036910 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63064 12:04:09 17/10/2016 1856.0957282 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63065 12:04:09 17/10/2016 1856.1531107 [C03E0F A33669] [ADEMCO A130EE] WiFi WiFi:[ ControlBlockAck] ....... RSSI = -73 dBm, Rate = 24.0 Mbps
    63066 12:04:09 17/10/2016 1856.1921059 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -78 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63067 12:04:09 17/10/2016 1856.2438275 [C03E0F A33669] [ADEMCO A130EE] WiFi WiFi:[ ControlBlockAck] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63068 12:04:09 17/10/2016 1856.2438275 [C03E0F A33669] [ADEMCO A130EE] WiFi WiFi:[ ControlBlockAck] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63069 12:04:09 17/10/2016 1856.2440382 [C03E0F A33669] [6466B3 FAF228] WiFi WiFi:[ ControlRTS] ....... RSSI = -74 dBm, Rate = 24.0 Mbps
    63072 12:04:09 17/10/2016 1856.2966467 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -75 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63073 12:04:09 17/10/2016 1856.3334282 [C03E0F A33669] [ADEMCO A130EE] WiFi WiFi:[ ControlBlockAck] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63074 12:04:09 17/10/2016 1856.3339430 [C03E0F A33669] [ADEMCO A130EE] WiFi WiFi:[ ControlBlockAck] ....... RSSI = -72 dBm, Rate = 24.0 Mbps
    63075 12:04:09 17/10/2016 1856.3973960 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -76 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63076 12:04:09 17/10/2016 1856.4998007 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -77 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63077 12:04:09 17/10/2016 1856.6043422 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -78 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63078 12:04:09 17/10/2016 1856.7089752 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -78 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63080 12:04:09 17/10/2016 1856.8115584 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -78 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63081 12:04:10 17/10/2016 1856.9140345 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -78 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63082 12:04:10 17/10/2016 1857.0161745 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -75 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63083 12:04:10 17/10/2016 1857.1185293 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -78 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1
    63084 12:04:10 17/10/2016 1857.2165969 [C03E0F A33669] [*BROADCAST] WiFi WiFi:[ ManagementBeacon] ....... RSSI = -76 dBm, Rate = 1.0 Mbps, SSID = SKY6D12C, Channel = 1


    You can see no IP traffic during the exchange on my network, certainly no port 443 traffic expected of an HTTPS connection. Try it for yourself download and install MS Network Analyser, start the analysis then watch the Evohome controller network traffic.

    The Sky Router is transferring packets directly to the Evohome gateway because the routing information has a header to indicate its destination (A130EE), then on receipt the Gateway (Evohome Controller) distributes the packets (internally and externally) as its final destinations.

  9. #29
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,001

    Default

    I too had an HR80 that wouldn't take a setpoint. It would report its temperature back to the controller but not accept the setpoint from the controller. No matter what i did, the situation didn't change. In the end I just put this down to a defective HR80 actuator circuit. But because it can still send a temperature reading back to the panel I installed this dud HR80 in the loft where all the boiler and unvented cylinder are located. If the temperature in the loft goes below 7C, I have a script that starts the boiler even if the rest of the house doesn't need any heating. So the faulty HR80 didn't land up in the bin.

    Back to your issue. You arent going to solve anything analysing the wifi or network traffic. If you really want to figure out what might be causing the issue between controller and HR92 then you need to analyse the radio traffic between them. You can do this with a stand alone receiver, a HGI80 or by sniffing the packets on the BDR91. You will have to shut everything else off and unpower them, else you wouldn't be able to tell the woods from the trees. Get your system to simply include the controller and that faulty HR92. Alternatively try that HR92 with another controller.

  10. #30
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,594

    Default

    Did you perform your capture using promiscuous mode (might need new drivers)? Without that you won't see all traffic - only broadcast traffic plus anything directed to your particular machine.

    I normally use Wireshark. Plenty of us have seen the https traffic this way.