Thread: Boiler Pump/Fan cycling at random? Evohome at fault?

  1. #21
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,845

    Default

    Quote Originally Posted by paulockenden View Post
    Nope.

    I believe that's how it works. The controller doesn't manage every on and off, it sends a "keep switching on and off at this rate" to the BDR.

    P.
    Although I've done some anecdotal testing before I thought I'd do a thorough test of this to confirm once and for all whether BDR91's do in fact autonomously continue their last known TPI cycle and for how long, and whether HR92's can send heat demands directly to the relays or not.

    The answer is an equivocal yes on the first point, and no on the second point, as I had already believed. Here was the test that I did this morning which took a couple of hours, and which is interesting as it gives some insight into details of how the system works that Honeywell doesn't go into.

    The system is configured with FAILSAFE OFF.

    I started with a system that was running with a moderate heat demand on a few zones - boiler and heating relays on about 3 minutes out of every 10 minutes, no hot water demand. I deliberately held the controller in my hands for a few minutes to warm it up so that the system thought the hallway was 28 degrees (as the evotouch is the sensor for the hallway) to see whether HR92's will fall back to their built in sensors if comms is lost - the large discrepancy in temperature would make it obvious when the switch to internal sensor happened, if it did happen.

    I waited until about 2 minutes after the boiler relay turned off in its TPI cycle then ripped the batteries out of the controller to shut it down then waited and observed the behaviour of the rest of the system.

    As far as boiler and heating relays were concerned, they did indeed continue to run at a 30% TPI duty cycle for a full hour - 3 minutes on, 7 minutes off in every 10 minute cycle.

    During this time making manual adjustments to an HR92 (very low or very high set point) did not have any effect on the relay duty cycle which stayed at 30%. So HR92's definitely cannot communicate heat demand without the controller.

    After exactly one hour the red LED on all three BDR91's lit and stayed on solid. From this point the relays stopped firing altogether, and after my pump overrun timer expired the pump stopped and remained off. After the fault light was on and the relays had stop cycling on I again tried to induce demand by turning up an HR92 but there was no response from the relays, as expected.

    I would expect that if I had failsafe turned on that after this one hour period the relay's (hopefully only boiler and heating relays not the hot water one) would start cycling at the 20% failsafe duty cycle, probably with the red LED also lit. I intend to perform a followup test with failsafe enabled to confirm the exact operation of failsafe mode and when it kicks in.

    30 minutes after the controller was powered down all the HR92's in the house started cycling between SYNC and NO SYNC every few minutes, but still appeared to be "waiting" for temperature updates from the controller as the room temperature displayed on the HR92's were still stuck on the last known temperatures sent from the controller. This lead to the living room getting uncomfortably warm because it wasn't aware that the room was still warming up as it couldn't receive updates from the DTS92 in the room - evidence that a remote sensor is relayed through the controller to the HR92.

    (I also believe that even local HR92 measurements are relayed via the controller back to the HR92 in single room zone configurations - but I didn't set out to specifically test this on this occasion)

    After exactly 60 minutes of no comms the HR92's all appeared to revert back to using their internal temperature sensors directly - the hallway HR92 which had been stuck on a reading of 28 degrees for an hour (last known temperature from the Evotouch held in my hand) suddenly started displaying 18.5 degrees, which would have been correct temperature near the floor in the room after the heating had been off in that room for an hour.

    The living room HR92 which uses a DTS92 also suddenly went from 21 (last known temperature from the DTS92 relayed via the controller) to 23 degrees - measured beside the radiator after the room had got a bit too hot because it wasn't getting temperature feedback. The DTS92 by this time still only said 21.5 so I know the reading wasn't coming from there.

    This is conclusive proof that after an hours worth of lost comms HR92's will revert to an autonomous mode of operation where they use their internal temperature sensor even if the zone was configured to use a remote sensor. And they will use their internal sensor to try to maintain the last known set point.

    I then re-inserted the batteries and didn't touch anything else to see how quickly the system recovers from power loss without being manually "poked".

    Within a minute of booting the controller the red LED's on the BDR91's all started flashing for about a minute then went out.

    After 3 minutes three zones had already reported in, had some demand and the boiler and heating relays came on. As each HR92 reported in the NO SYNC disappeared on the HR92.

    After 15 minutes the hallway radiator that is supposed to use the evotouch as its sensor updated its temperature reading from the locally measured 18.5 degrees to the 19.5 measured by the evotouch.

    After 23 minutes the DTS92 in the living room reported to the evotouch - about 5 minutes after that the reading on the HR92 in the living room updated from a local reading to match the DTS92 reading.

    After 26 minutes all straggling heating zones had reported in and were functioning normally.

    After exactly one hour the hot water temperature sensor finally reported in. It appears that if the hot water temperature is not crossing the hot water set points and is also not changing the transmissions are very infrequent indeed. So it appears that hot water sensor transmissions are more frequent when the temperature is changing than when it is sitting idle.

    One further thing - by the time I rebooted the controller some of the zone scheduled temperatures were different, it appears that the set points of the HR92's were not "refreshed" after the controller first re-made contact with them - as two of the zones were still running at their last known set points rather than what the set point should be now, at the time the controller was booted.

    However I'm sure that the set points would get back into sync again at the next scheduled or manual set point change.

    So there you have it. I intend to repeat the test with failesafe enabled to see if that works how I expect it will, I also want to perform some tests with the heating off with batteries removed from an HR92 for a long time in both failsafe off and failsafe on modes, to see if there is any failsafe protection for loss of comms with an HR92, or whether failsafe only protects loss of comms between controller and relays.

    Also it would be interesting to see if loss of comms with a DTS92 automatically reverts to using the HR92's own sensor after an hour.
    Last edited by DBMandrake; 28th October 2016 at 02:39 PM.

  2. #22
    Automated Home Guru
    Join Date
    Oct 2016
    Location
    Bath, UK
    Posts
    151

    Default

    As ever a very thorough and detailed analysis which has now proved beyond doubt how the system operates, I wonder if they tell installers all this on training courses - I must go through the free on-line training myself too.

    I have reset my system again, it's a bit time consuming but I'm getting very adept at setting the up from a NOOB configuration, it takes a while to rest all the HR92's, probably the longest job of all.

    If would be good if a backup and restore for the schedule existed.

    We'll see tonight if the default everything settings results in the heating BDR91 cycling again. It could be a faulty BDR in my system or still the application software (1.03).

    Out of interest does anyone know if the Evohome copes with DST this weekend, I'm sure it does, there is no mention of it in the manual.

  3. #23
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,602

    Default

    There are some scripts on GitHub for backup and restore of schedules.

    Gimme a shout if you can't find them as I'm sure I'll have them bookmarked somewhere.

  4. #24
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,845

    Default

    Quote Originally Posted by g6ejd View Post
    Out of interest does anyone know if the Evohome copes with DST this weekend, I'm sure it does, there is no mention of it in the manual.
    Yes it does, at least if you have the time set to Auto Update over Wifi. I haven't tried it with that turned off.

    There is no country setting in the device, (unless it makes an assumption based on the language setting, which would be naughty) so I'm assuming that when you link the device to a total connect comfort account that it gets your country/timezone from there.

  5. #25
    Automated Home Guru
    Join Date
    Oct 2016
    Location
    Bath, UK
    Posts
    151

    Default

    I think your right, it must be based on language and as they sell Evohome in the US, perhaps there was a country suffix during the account setup and I missed English, UK. I think DST programming is one of the hardest problems to solve, I completed it recently for an Arduino project and decided to only do it for UK, USA and Australia on the basis that catering for all the countries is too difficult.

    I've found the scripts for schedule backup, thanks for the prompt.

  6. #26
    Automated Home Legend
    Join Date
    May 2014
    Posts
    988

    Default

    My location is set up in my router.

  7. #27
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,602

    Default

    The location is set in the web interface when you create the account, isn't it?

    Having said that, for some reason I can't seem to get in to check right now - can't get past the login screen.

  8. #28
    Automated Home Legend
    Join Date
    May 2014
    Posts
    988

    Default

    Quote Originally Posted by paulockenden View Post
    The location is set in the web interface when you create the account, isn't it?

    Having said that, for some reason I can't seem to get in to check right now - can't get past the login screen.
    Absolutely correct. My TCC account shows United Kingdom and the address of my device. Does time come from the Honeywell server though?

  9. #29
    Automated Home Guru
    Join Date
    Oct 2016
    Location
    Bath, UK
    Posts
    151

    Default

    Probably, few networks (LAN with a WAN access) have accurate time and Honeywell's time is slightly out, if it was coming from an NTP service it would be locked to UTC (Unix time) but it's not on mine which is 35-secs fast, which bothers me because I have OCD tendencies

  10. #30
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,602

    Default

    Just double checked (and noticed that I'm able to log in to TCC from a desktop browser, but not from either Chrome or Safari on an iPad), and not only does the TCC web interface have the full location details there's also a field for timezone.

    P.