Originally Posted by
Little Tinker
What I keep looping back to in my head is that setup: two relays bound as HW and boiler relay, plus HR92 heads - but the boiler relay is actually connected to the CH zone valve. As far as EvoHome is concerned you have HW zone valve, boiler relay and HR92 heads, which I expect must be a common configuration and therefore supported. If the assumption that having boiler relay bound is what gives the extra parameters is correct then that would seem to be an answer to Paul's original point re adding 3rd (possibly unnecessary) relay.
Incidentally, this would seem to address point 1 as well as long as the HW orange wire is disconnected. When HW is needed both valves will open, but unless there is an HR92 open no water will pass that on CH path. Contoller can then signal end of call for heat, closing CH valve and hence turning boiler off. But HW valve will allow overrun to pass until it is also closed by controller.