    Default BDR91 reoccurring fault

    Evening all!
    First post, and i have a problem!
    Installed everything myself, two BDR91 for hot water and heating, 4 smart TRV's, wifi controller and hotwater tank sensor.
    All running ok until approx 1.30am each night when i get a "comms fault, heating valve actuator"
    Contacted Honeywell and the said it was because the wifi needed updating! the said they would push an update, nothing has been updated and the fault is now happening more often!
    Would appreciate any views!

  2. #2
    Automated Home Legend
    Join Date
    May 2014
    Posts
    998

    Default

    Hi. Did they ask you check whether the BDRs are separated by a minimum distance of 300mm from metal objects etc? I wasn't aware that there was a wifi update for the controller to BDRs. As I sure you know, this is not the same as the wifi connection to your router.

  3. #3
    Automated Home Lurker
    Join Date
    Jan 2017
    Posts
    7

    Default

    Hi HenGus, Thank you for your quick reply! No they didn't ask, they are approx double that distance though and far away from tank, pump and valve. They are located on the outside of the hot water tank cupboard at about a metre higher than the tank. The fault only happens with the heating BDR and not the hotwater and generally late at night. Going to see what happens tonight!

  4. #4
    Automated Home Legend
    Join Date
    May 2014
    Posts
    998

    Default

    When I had Evohome installed nearly 3 years ago, I had 6 months of comms faults initially on the HW actuator and then on both the Heating and HW actuators. They can be annoyingly difficult to solve. After moving the BDRs around the airing cupboard to avoid everything and anything electrical or metal, and metal in the line of site between the controller and BDRs, the BDRs were changed, and finally the controller.

    Just a thought. Do you have a smart meter? If the fault is occurring at the same time each night, it could be interference from another wifi source.

  5. #5
    Automated Home Lurker
    Join Date
    Jan 2017
    Posts
    7

    Default

    I initially installed them inside the airing cupboard but had a nightmare with comms faults so relocated them outside near the ceiling, all good then this started! I have the controller in the bedroom about eight feet away with only a plasterboard wall in between, no smart meter, Honeywell have advised me to go find a Connected Specialist after only two emails! hey ho! thanks once again for your help!

  6. #6
    Automated Home Legend
    Join Date
    May 2014
    Posts
    998

    Default

    My advice, FWiW, is keep photos of the fault logs. I wouldn't call in a specialist until you have evidence of a string of faults. You could end up paying someone quite a bit of money for a NO FAULT FOUND. I suspect that you know this already. Are you able to change the BDR?

  7. #7
    Automated Home Lurker
    Join Date
    Jan 2017
    Posts
    7

    Default

    Photos of all fault logs taken as you recommended, i've swapped the HW BDR and the heating BDR, my guess is that if the fault now switches to the HW valve i have a duff BDR, other than that it's a controller fault.
    As a side note that with the few emails i've had with honeywell they said that the wifi software wasn't the latest firmware and to disconnect and reconnect the wifi to get it to update.....the firmware is 01.00.02.00.....was like that when i bought it and still is, my understanding that this IS the latest firmware, naughty Honeywell!

  8. #8
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,917

    Default

    If you swapped the BDR91's over I hope you cleared the existing bindings on them before rebinding them to their new functions ? If not you'll create more problems than you solve as you'll end up double binding both relays.

  9. #9
    Automated Home Lurker
    Join Date
    Jan 2017
    Posts
    7

    Default

    BDR's cleared and rebinding carried out.......guess what fault i just had! Comms fault on the heating valve! back to the supplier in the morning!
    I really appreciate all the help and advice, thank you!

  10. #10
    Automated Home Lurker
    Join Date
    Jan 2017
    Posts
    7

    Default

    Well, cleared the fault after swapping BDR's over.....and nothing! no fault and all working as it should!