    Originally posted by Dan_Robinson View Post
    Precisely.

    Boiler logic varies, and the ignition rate is also different and can affect micro loads if the burner is chucking out 7kW into a rad that can only take 500w.

    Some boilers have return sensors, others do not. There are also all sorts of different heat exchanges, burners, fans etc.

    As such there is no way a universal controller would/should have direct control over the gas side of the boiler. It can/should only have influence over the flow temperature. The better boilers too will have their own ability to limit floor w temp - Intergas being one, Vaillant another, where Tmax can be limited in the boiler software.
    Mine is limited to max 55c flow temp thinking this would change the heating curve it still sits at 48c most of time even though how is upto temp and it’s cycling on and off and there’s an 8c diff between flow and return.

    Comment

    • Dan_Robinson
      Automated Home Ninja
      • Jun 2012
      • 347

      If it is any consolation, the savings a year from modulating much further down from 55 will be less than an afternoon down the pub.
      Kind Regards - Dan Robinson (Jennings Heating Ltd)

      Comment

      • dty
        Automated Home Ninja
        • Aug 2016
        • 489

        Originally posted by richardc1983 View Post
        It does modulate as I see a high flow temp when it first comes on, the issue at moment is it’s not modulating low enough and causes it to cycle off or overshoot.
        When you say “low enough”, is it getting to the lowest power it can? If so, there’s nothing more that can be done. If your boiler has a low power output of, say, 6kWh, and it’s a 5kWh day, it’s going to have to cycle.

        Comment

        • Dan_Robinson
          Automated Home Ninja
          • Jun 2012
          • 347

          Originally posted by dty View Post
          When you say “low enough”, is it getting to the lowest power it can? If so, there’s nothing more that can be done. If your boiler has a low power output of, say, 6kWh, and it’s a 5kWh day, it’s going to have to cycle.
          What is a 5kWh day?
          Kind Regards - Dan Robinson (Jennings Heating Ltd)

          Comment

          • robj20
            Automated Home Sr Member
            • Aug 2017
            • 76

            Originally posted by Dan_Robinson View Post
            What is a 5kWh day?
            A day where the outside temperature means your heating system needs to provide 5kwh to maintain the set temperature.

            My boiler tends to cycle in warmer weather, but since its been cold its bang on stays on at around 32c flow temperature.

            Comment

            • richardc1983
              Automated Home Sr Member
              • Nov 2016
              • 86

              Originally posted by dty View Post
              When you say “low enough”, is it getting to the lowest power it can? If so, there’s nothing more that can be done. If your boiler has a low power output of, say, 6kWh, and it’s a 5kWh day, it’s going to have to cycle.
              It can ramp lower down to 41c if I put it into service mode minimum rate which fires the burner at the minimum rate. Based on tonight’s heating conditions and outside temp.

              Comment

              • dty
                Automated Home Ninja
                • Aug 2016
                • 489

                Originally posted by richardc1983 View Post
                It can ramp lower down to 41c if I put it into service mode minimum rate which fires the burner at the minimum rate. Based on tonight’s heating conditions and outside temp.
                Without knowing what the delta-T across the heat exchanger and the flow rate are, that doesn’t say an awful lot.

                Comment

                • richardc1983
                  Automated Home Sr Member
                  • Nov 2016
                  • 86

                  What an absolute disgrace ideal are.

                  I’m still having the same issues, ideal are blaming the t6 and are wanting me to remove the the lyric and go for a diff opentherm controller from another manufacturer of my choice at their cost. However there is nothing else out there that will do the same (internet connectivity and the home location, as well as apple home kit enabled etc) and I’m fond of Honeywell and trust them as market leaders.

                  They have messed me around for over a year now, for the last 6weeks they have been testing a pcb modification to resolve my issues then on the day the engineer was due to come tried to cancel the appointment to which I refused and they managed to get him out. Then when their engineer came to fit it then it was realised he had the wrong PCB, they had been testing it for the wrong boiler - mines the gen 1 vogue and they had been doing it on the gen 2 - newer Vogue.

                  Furious about this and after all this messing about I requested they swap my gen 1 for a gen 2. Now at the thought the opentherm is likely not as compatible on the gen 1 as the gen 2 due to them having tinkered and messed about with opentherm on the boiler they are saying I need to choose a diff controller. All this because they are now saying them swapping the boiler for a gen 2 boiler will not resolve the issues I’m experiencing. For example undershooting and overshooting of set temp. The gas burner comes on at full throttle when it fires even though lyric is asking for a low flow temp meaning burner cycles on and off constantly cos it comes on too high meaning flow temp quickly exceeds what is being asked of it.... video links attached of this behaviour. For me the issue above is because it doesn’t fire at the minimum rate and then ramp up it fires straight away at maximum rate than tries to ramp down. Which is not how opentherm should be running - low and slow I believe is the key.

                  Yesterday they offered me a new opentherm controller of my choice from a company called Theben or the gen 2 boiler. I chose the gen 2 boiler to which today they now say they can’t do that as the director won’t sign it off cos research and development say it won’t fix my issues and are blaming the T6 again.

                  Now they are telling me they need me to choose any opentherm controller of my choice and they will pay for it.

                  Opentherm so far is an absolute farce and ideal are useless and know nothing about the products they sell.

                  Comment

                  • HenGus
                    Automated Home Legend
                    • May 2014
                    • 1001

                    Richard - I am struggling to understand why a different OT controller would work when the Lyric doesn’t? I thought that Ideal had accepted that it was a boiler PCB issue? Looking at the Theben site, I can see no specific mention of OT.

                    Edit: I didn’t look hard enough. There seem to be 2 models (Ramses)
                    Last edited by HenGus; 22 November 2017, 07:44 PM.

                    Comment

                    • Dan_Robinson
                      Automated Home Ninja
                      • Jun 2012
                      • 347

                      Kind Regards - Dan Robinson (Jennings Heating Ltd)

                      Comment

                      • blowlamp
                        Automated Home Sr Member
                        • Apr 2017
                        • 98

                        Originally posted by richardc1983 View Post
                        What an absolute disgrace ideal are.

                        I’m still having the same issues, ideal are blaming the t6 and are wanting me to remove the the lyric and go for a diff opentherm controller from another manufacturer of my choice at their cost. However there is nothing else out there that will do the same (internet connectivity and the home location, as well as apple home kit enabled etc) and I’m fond of Honeywell and trust them as market leaders.

                        They have messed me around for over a year now, for the last 6weeks they have been testing a pcb modification to resolve my issues then on the day the engineer was due to come tried to cancel the appointment to which I refused and they managed to get him out. Then when their engineer came to fit it then it was realised he had the wrong PCB, they had been testing it for the wrong boiler - mines the gen 1 vogue and they had been doing it on the gen 2 - newer Vogue.

                        Furious about this and after all this messing about I requested they swap my gen 1 for a gen 2. Now at the thought the opentherm is likely not as compatible on the gen 1 as the gen 2 due to them having tinkered and messed about with opentherm on the boiler they are saying I need to choose a diff controller. All this because they are now saying them swapping the boiler for a gen 2 boiler will not resolve the issues I’m experiencing. For example undershooting and overshooting of set temp. The gas burner comes on at full throttle when it fires even though lyric is asking for a low flow temp meaning burner cycles on and off constantly cos it comes on too high meaning flow temp quickly exceeds what is being asked of it.... video links attached of this behaviour. For me the issue above is because it doesn’t fire at the minimum rate and then ramp up it fires straight away at maximum rate than tries to ramp down. Which is not how opentherm should be running - low and slow I believe is the key.

                        Yesterday they offered me a new opentherm controller of my choice from a company called Theben or the gen 2 boiler. I chose the gen 2 boiler to which today they now say they can’t do that as the director won’t sign it off cos research and development say it won’t fix my issues and are blaming the T6 again.

                        Now they are telling me they need me to choose any opentherm controller of my choice and they will pay for it.

                        Opentherm so far is an absolute farce and ideal are useless and know nothing about the products they sell.


                        Accept their offer of a new controller - maybe a Nest v3? If the problem is cured then at least you know the boiler is capable of firing from a low flame and isn't down to the boiler software being designed to come on high and gradually ramp down.

                        Ideal must be confident the fault lies outside of their boiler, otherwise it won't reflect well on them if a substitute controller is no better.

                        Comment

                        • Dan_Robinson
                          Automated Home Ninja
                          • Jun 2012
                          • 347

                          I should point out that Theben make Ideal's OEM controllers.


                          Or at least they did up until recently.
                          Kind Regards - Dan Robinson (Jennings Heating Ltd)

                          Comment

                          • richardc1983
                            Automated Home Sr Member
                            • Nov 2016
                            • 86

                            Originally posted by blowlamp View Post
                            Accept their offer of a new controller - maybe a Nest v3? If the problem is cured then at least you know the boiler is capable of firing from a low flame and isn't down to the boiler software being designed to come on high and gradually ramp down.

                            Ideal must be confident the fault lies outside of their boiler, otherwise it won't reflect well on them if a substitute controller is no better.
                            The issue I have is they had accepted the issue was pcb software related but turns out now that this was for a completely different issue and for the boiler not turning the heating off if the potential dial was turned to off?

                            I know the boiler is capable of firing at low flame as when I go into the menu there is a service mode minimum rate which fires the boiler and runs the burner at minimum rate this maintains a flow temp for example tonight of 42c... out of this mode the minimum it seems to get down to running on the controller is 50c even though the t6 is asking for 43c.

                            Does anyone have any thoughts on Nest V3?

                            Comment

                            • richardc1983
                              Automated Home Sr Member
                              • Nov 2016
                              • 86

                              Originally posted by HenGus View Post
                              Richard - I am struggling to understand why a different OT controller would work when the Lyric doesn’t? I thought that Ideal had accepted that it was a boiler PCB issue? Looking at the Theben site, I can see no specific mention of OT.

                              Edit: I didn’t look hard enough. There seem to be 2 models (Ramses)
                              Yes how will a diff controller be any diff if this was unique to the t6 the issue would be with all manufacturers and people using the t6.

                              Comment

                              • blowlamp
                                Automated Home Sr Member
                                • Apr 2017
                                • 98

                                Originally posted by richardc1983 View Post
                                The issue I have is they had accepted the issue was pcb software related but turns out now that this was for a completely different issue and for the boiler not turning the heating off if the potential dial was turned to off?

                                I know the boiler is capable of firing at low flame as when I go into the menu there is a service mode minimum rate which fires the boiler and runs the burner at minimum rate this maintains a flow temp for example tonight of 42c... out of this mode the minimum it seems to get down to running on the controller is 50c even though the t6 is asking for 43c.

                                Does anyone have any thoughts on Nest V3?
                                Why would the folks at Ideal offer to buy you a controller of your choice if they weren't confident of it fixing the problem?
                                I'd take them up on it.