Because this is not a mandatory part of OpenTherm spec.
Help with Evohome / Opentherm / Intergas
Collapse
X
-
-
Originally posted by top brake View PostBecause this is not a mandatory part of OpenTherm spec.
Originally posted by blowlamp View PostAgreed. If it was my previous post that you had in mind, then what I meant to convey was that the flame would modulate by vertue of OpenTherm requesting a specific flow temperature from the boiler. & do.
It only reminded me that it had been mentioned by a couple of posters.Kind Regards - Dan Robinson (Jennings Heating Ltd)
Comment
-
-
I've cut & pasted a few things below from tinternet.
Quote:
While shopping for Opentherm equipment with home automation in mind, it can be useful to have some idea to which extent boilers and thermostats support the opentherm protocol. Only some messages are mandatory (ID's 0, 1, 3, 14, 17, and 25), all others may or may not implemented. (Yes Daalderop, support for MsgID 14 is mandatory.)
Which I think refers to things in this picture.
Capture.jpg
So is one to conclude that MsgID 14 governs the maximum flow temperature and is required in both boilers and controllers?
Comment
-
-
Originally posted by Dan_Robinson View PostPerhaps having the original question would have helped
Nobody ever said that it was that Evohome wouldn't pair with the internals directly. And someone, can't remember who, said on another forum that the problem was that Intergas couldn't support the data rate. And that it was to do with multiple vs single zones.
Comment
-
-
Originally posted by paulockenden View PostMany people asked what the Intergas problem was. I've seen the question several times now.
Nobody ever said that it was that Evohome wouldn't pair with the internals directly. And someone, can't remember who, said on another forum that the problem was that Intergas couldn't support the data rate. And that it was to do with multiple vs single zones.
It works well, but doesn't appear to modulate with multiple zones. Investigations and upgrades are in progress.
In the mean time (as OpenTherm is an upgrade anyway) you can use weather comp and Evohome together. Unquote
Read more: https://www.diynot.com/diy/threads/i...#ixzz4pYoucZn6
Comment
-
-
Originally posted by top brake View PostBecause this is not a mandatory part of OpenTherm spec.
That’s a recipe for disaster (reality in this case).
Leading me to observe either:
1. OpenTherm specifications are flawed (this is my current opinion)
Or
2. Certification and governance of OpenTherm products is flawed leading to incompatible products on the market
I did look at this when I was troubleshooting my Viessmann OpenTherm problem with max temps.
See my response on this page to Bruce where I have referenced the OpenTherm spec where I believe I found that Viessmann were probably not at fault (if I was understanding the spec document correctly - which I seems to be as I had confirmation from OpenTherm association):
I’ve reported these issues directly to the OpenTherm association and did not really get much out of them in the way of help or that they would liaise with Viessmann on the issue. They suggested I contact Viessmann who in turn told me to get their OpenTherm controller or go back to BDR91 on/off control.......
I got this in response to my report of interoperability issues:
“Dear Stephen,
I’m chairman of the Technical Committee of the OpenTherm Association. I do agree with you statement that the maximum supply set point is an option for a master device (room control).
The boiler should also work properly with a OpenTherm controller without the possibility to set the maximum supply temperature.
I propose you contact Viessman to solve this issue in a for you acceptable way.
Regards,
Twan Smets”
Stephen.
Comment
-
-
Originally posted by StephenC View PostIt seems to me that neither the boiler (slave), or controller (master) have this as mandatory to be able to set max ch flow temp.
That’s a recipe for disaster (reality in this case).
Leading me to observe either:
1. OpenTherm specifications are flawed (this is my current opinion)
Or
2. Certification and governance of OpenTherm products is flawed leading to incompatible products on the market
I did look at this when I was troubleshooting my Viessmann OpenTherm problem with max temps.
See my response on this page to Bruce where I have referenced the OpenTherm spec where I believe I found that Viessmann were probably not at fault (if I was understanding the spec document correctly - which I seems to be as I had confirmation from OpenTherm association):
I’ve reported these issues directly to the OpenTherm association and did not really get much out of them in the way of help or that they would liaise with Viessmann on the issue. They suggested I contact Viessmann who in turn told me to get their OpenTherm controller or go back to BDR91 on/off control.......
I got this in response to my report of interoperability issues:
“Dear Stephen,
I’m chairman of the Technical Committee of the OpenTherm Association. I do agree with you statement that the maximum supply set point is an option for a master device (room control).
The boiler should also work properly with a OpenTherm controller without the possibility to set the maximum supply temperature.
I propose you contact Viessman to solve this issue in a for you acceptable way.
Regards,
Twan Smets”
Stephen.
It is precisely to assure interoperability that the ch tmax is not mandatory
Twan advised you in the correct way
Customers need to lobby the boiler manufacturers to comply with the OT protocol spec and follow the spirit of OpenTherm standard rather than closing access or being protectionist by not selling OpenTherm compatible boilers in the UK market
It tends to be the German boiler manufacturers that are resisting adoption of OpenTherm in the UK.I work for Resideo, posts are personal and my own views.
Comment
-
-
Originally posted by top brake View PostInteresting thanks for sharing
It is precisely to assure interoperability that the ch tmax is not mandatory
Twan advised you in the correct way
Customers need to lobby the boiler manufacturers to comply with the OT protocol spec and follow the spirit of OpenTherm standard rather than closing access or being protectionist by not selling OpenTherm compatible boilers in the UK market
It tends to be the German boiler manufacturers that are resisting adoption of OpenTherm in the UK.
Comment
-
-
Originally posted by blowlamp View PostMy boiler & controller are from different manufacturers in the Netherlands. The boiler allows the controller to set the CH maximum temperature and the controller has the ability to do it. It seems logical to me - the boiler's the slave and the controller is its master. So it's an odd thing in my view when a CH boiler master controller can't set a maximum CH water temperature limit.
Comment
-
-
Originally posted by The EVOHOME Shop View PostAs top brake has said, the spec does not require the master to set Tmax. As much as we stamp our feet, Honeywell have followed the spec laid down by the OpenTherm Association. Don't you have an Intergas boiler and can set Tmax at the boiler anyway?
To answer your question: I do have an Intergas boiler and I set Tmax on the master controller in the hallway.
Comment
-
-
Originally posted by blowlamp View PostI've cut & pasted a few things below from tinternet.
Quote:
While shopping for Opentherm equipment with home automation in mind, it can be useful to have some idea to which extent boilers and thermostats support the opentherm protocol. Only some messages are mandatory (ID's 0, 1, 3, 14, 17, and 25), all others may or may not implemented. (Yes Daalderop, support for MsgID 14 is mandatory.)
Which I think refers to things in this picture.
[ATTACH=CONFIG]1059[/ATTACH]
So is one to conclude that MsgID 14 governs the maximum flow temperature and is required in both boilers and controllers?
Comment
-
-
Originally posted by The EVOHOME Shop View PostID 57 is Max CH Water Setpoint, not ID 14, which is the modulation of the boilers fan I believe...Kind Regards - Dan Robinson (Jennings Heating Ltd)
Comment
-
-
Originally posted by blowlamp View PostMy boiler & controller are from different manufacturers in the Netherlands. The boiler allows the controller to set the CH maximum temperature and the controller has the ability to do it. It seems logical to me - the boiler's the slave and the controller is its master. So it's an odd thing in my view when a CH boiler master controller can't set a maximum CH water temperature limit.
Remember the best selling OpenTherm thermostat in NL has a Honeywell logo on it... Honeywell are experts in OpenTherm as they invented it...I work for Resideo, posts are personal and my own views.
Comment
-
-
Originally posted by top brake View PostNot every boiler allows the ch Tmax to be set. So to avoid conflict Honeywell controls don't try to.
Remember the best selling OpenTherm thermostat in NL has a Honeywell logo on it... Honeywell are experts in OpenTherm as they invented it...
When both sides (master and slave) components of the control system are designed to set no value (which is possible and allowed within the specs - Honeywell/Viessmann) so the control system as a whole is not fit for purpose as has been shown. Finger pointing occurred in both directions in this case, and both were right unbelievably. (Honeywell vs Viessmann). That’s what led me to start assessing OpenTherm itself as a specification.
OpenTherm specification is flawed as it stands (the version I assessed)
What I’m saying is the OpenTherm specification must be updated to dictate that one or the other (master or slave) sets a value.
It’s irrelevant at this point taking about Honeywell EvoHome, Nest or Intergas or Viessmann etc. Fundamentally it’s a spec problem that will manifest itself again and again. Because the spec allows for it.
P.S. I still think EvoHome with BDR91 is great.
;-)
Stephen