    Hi All,

    I'm about to install evohome in a property I've just renovated and in need of some advice to check I've chosen the right Evo home elements.

    Setup: I've got UFH on Ground (2 zones), First (2 zones) and 2nd Floor (1 zone).

    There are two manifolds: 1 ground; 1 first.

    I think I need:

    UFH controller x 2;
    Actuators MTX x 6;
    Evohome base controller;
    4 x Yxxxx thermostats (1 for 2 zones GF; can you use Lyric thermostats as a single zone controller?) they look nice than the others...
    I've got an unvented cylinder but I don't think there is a place to put the temperature sensor.

    Really grateful for any thoughts if this is correct setup and if I've missed anything.

    Thank you.

  2. #2
    Automated Home Legend
    Join Date
    May 2014
    Posts
    1,000

    Default

    Temperature sensor. My HW sensor is pushed up at an angle under the unvented tank insulation. Access is via the electrical access panel. Has worked well for nearly 3 years.