Originally Posted by
bruce_miranda
Yes, I agree with the sentiments about Viessmann, especially when this is such an easy fix. Allowing the boiler to ramp up all the way to it's physical max of +80C is just nuts.
I have a Vaillant, and there is plenty wrong with that boiler but at least I have control on the Max.
There is a way you can resolve this, if you are determined to use the Honeywell kit. But it involves sticking an OT gateway in between the boiler and the Honeywell OT Bridge. What that does is alters the Honeywell message to provide a Max flow OT message that the boiler is looking for, but one that Honeywell doesn't send, as it's optional in the OT spec.