Hi Stephen,
Can you clarify why a Tmax setpoint is required from the controls?
The Intergas boiler I have at our training centre has the ability to set this manually (I designed our system with a 70 degree flow temp, so have limited it to this), but I understand that your Viessmann doesn't?
Most heating systems have a 75 degree flow temperature design point and I would imagine that once evohome is over its initial 'learning' phase, Tmax should certainly be no higher than this? I assume you are not seeing this?
I have a friend with an Intergas ECO RF 24 and a 10 zone evohome Wi-Fi and we are getting set points generated depending on the aggregate demand of the 10 zones (confirmed by an OpenTherm monitor and the boilers diagnostic software).
Capture3.jpg
I was testing several zones at the time, hence the demand was dropping off sometimes suddenly but should give you an idea of what is there and what should happen.
I am more than willing to invite Automated Home members over to our facility in Mid Wales to see this is action and discuss face-to-face? Maybe TB can even meet us there so you can ask questions directly?
Thanks,
Richard