Thing is, Evohome demands 100% most of the time. It’s only when ALL zones are within one degree of setpoint that it'll scale the boiler demand back. And the it just needs one zone to stray outside that (or start oscillating around the setpoint) and it’s back to 100% again.
Boiler with separate HW and CH max and OpenTherm
Collapse
X
-
There may be more to it, but from what I can see from the system update - the OT bridge asks for the same percentage as the highest percentage radiator call.
It doesn't matter if one rad or ten rads are calling for 100% - it still asks for 100%. Or am I missing something?
If OT takes the control and smart logic away from the boiler, then it should be Evohome that provides it.
Comment
-
-
Originally posted by dty View PostOpenTherm requests specific temperatures from the boiler, not percentages, so it would be even easier!
You’d just set two maximum temperatures in Evohome - one for hot water, one for heating. This would only work for OpenTherm controlled boilers, of course. Unfortunately, I doubt the OT bridge has this capability right now and I don’t believe it’s field-upgradable. So it would necessitate buying a new OT bridge (unless Honeywell were remarkably generous and offered a swap-out programme. I expect they can reprogram the bridges once they receive them back and send them out to another customer.)
So the OpenTherm bridge must map that 0-200 heat demand range to a flow temperature range of something like 10-90 degrees. (Not sure what the bottom end of the range is, but I think the top is 90) Somebody with the right equipment (both Domoticz and Opentherm logging) would need to measure it to see what the relationship between the two is but I'd put money on it being a fixed, pre-programmed relationship in the OpenTherm bridge, perhaps even a straight line. Therefore the Evotouch could indirectly specify a flow temperature by knowing what heat demand maps to what flow temperature. No hardware upgrade needed.
Originally posted by dty View PostActually, I’ve been wondering how some of this affects the learning algorithms. I have one or two particularly cold rooms in my house so at the moment Evohome is requesting the full 90C a lot of the time - even though the boiler modulates down to 6kW to achieve that with only those two rooms asking for any significant heat. However, the boiler limits the flow to 75C. But Evohome thinks it’s getting 90C. Then I see it step down to 85C, but of course nothing changes at the boiler - it’s still producing 75C. Then again at 80C. It’s not until it requests less than 75C that anything useful actually happens. This has surely got to confuse the learning algorithm?
Currently when you limit the maximum flow temperature on an OpenTherm system at the boiler (for boilers that allow it!) you are simply truncating the requested flow temperature. So you end up with dead band in the top end of the control range where increased demand from the Evotouch does nothing. Worse still, the lower you set your maximum flow temperature the more dead band there is.
This can't be optimal for the control algorithm as it won't be aware of any deadband the boiler has introduced except very indirectly by noticing that when it increases the heat demand from (say) 70% to 100% that nothing happens! It would be better if the boiler's flow temperature maximum scaled the requested temperature instead of truncating it, but that doesn't seem to be the way OpenTherm boilers work.
Probably beating a dead horse because I've already suggested it before a couple of times but what really needs to happen is for the Evotouch to have a maximum flow temperature setting in the system installer menu (which would only be applicable and visible if an OpenTherm bridge was bound, as the feature couldn't be implemented with a BDR91 - nor does it need to be!) or perhaps even in the normal settings menu. By setting this the maximum heat demand called for from the OpenTherm bridge could be reduced to the value that would map to that flow temperature.
There's several advantages to this:
1) Because the maximum flow temperature limit is set in software in the Evotouch it is fully aware of it, and is able to scale in software the calculated heat demand. In other words the control algorithms still work out a 0-100% (0-200) heat demand based on inputs from zones, but at the last step before sending to the OpenTherm bridge this value is then scaled down by a factor such that an original 100% heat demand maps to a lower heat demand and thus the target maximum flow temperature. Because of this there is no dead band in the control loop which should result in better control.
2) People with boilers which do not allow setting a maximum flow temperature limit with OpenTherm will finally be catered for. The inability of so many boilers to do this right seems very problematic (just look at the posts on here where people have had to go back to a BDR91!) and instead of pointing the finger of blame at boilers where it rightly belongs, just accept the fact that many boilers don't do it right and provide the maximum flow temperature setting in the Evotouch.
You're literally talking about adding a division or multiplication of the heat demand and a UI element to let you set a maximum flow temperature. Not difficult to implement as far as I can see!
It might be desirable to set a maximum flow temperature for hot water demand as well. For example if you have your CH max flow set to 60 you may not want or need it asking for 90 degrees to heat hot water on a system without hot water priority! It might be more reasonable and acceptable to ask for say 75 degrees - hot water will heat a little bit slower but your room temperatures wont overshoot much. For those with hot water priority they could leave it set at the default so hot water calls for the full 90 degrees and heats as fast as possible.
Controlling the maximum flow temperature in the evotouch (and scaling it instead of truncating it!) also opens the door to software based weather compensation where that maximum flow temperature can be configured to depend on the outdoor temperature - which we now have available on the latest firmware. I'm very doubtful that we'll ever see this though as the company line from Honeywell with Evotouch is that weather compensation isn't needed or useful in any way. But as someone who still has to adjust the flow temperature manually with the seasons despite having Evohome I beg to differ.
The problem with combining OpenTherm and Weather compensation at the moment is that no boilers appear to do this correctly, and even if they do apply the weather compensation max flow temperature to the opentherm requested flow temperature they are almost certainly still truncating instead of scaling, which means the Evotouch is subjected to a constantly varying and unknown deadband! If it was all done in the Evotouch there would be no need for truncation and it could be properly scaled and I believe it would work very well as long as it has both slope and offset adjustments that are set correctly.Last edited by DBMandrake; 25 January 2018, 10:44 AM.
Comment
-
-
Originally posted by fergie View PostThere may be more to it, but from what I can see from the system update - the OT bridge asks for the same percentage as the highest percentage radiator call.
It doesn't matter if one rad or ten rads are calling for 100% - it still asks for 100%. Or am I missing something?
Comment
-
-
What DBMandrake suggests (I think a few of us have suggested similar, in the past) also has the advantage that without the dead band (great name for it!) there would be finer control at the top end, so the boiler probably wouldn't be running at 100% quite so often. It would allow for better control.
Providing the extra parameters needed is really no different from exposing the cycle-time values when a boiler relay is configured. So there is precedent here.Last edited by paulockenden; 25 January 2018, 11:07 AM.
Comment
-
-
Originally posted by DBMandrake View PostThat's what it does, yes.
Comment
-
-
Originally posted by paulockenden View PostWhat DBMandrake suggests (I think a few of us have suggested similar, in the past) also has the advantage that without the dead band (great name for it!) there would be finer control at the top end, so the boiler probably wouldn't be running at 100% quite so often. It would allow for better control.
Providing the extra parameters needed is really no different from exposing the cycle-time values when a boiler relay is configured. So there is precedent here.
This would open up the possibility for Viessmann boilers to be controlled as per the native Viessmann OT controller (and as that manufacturer at least appears to have designed their side of the OT interface to work this way).
Lack of max CH flow temp control with a Viessmann 111-W is the only reason I had to go back to BDR91 control from OT..
Comment
-
-
Originally posted by DBMandrake View Post
...The problem with combining OpenTherm and Weather compensation at the moment is that no boilers appear to do this correctly, and even if they do apply the weather compensation max flow temperature to the opentherm requested flow temperature they are almost certainly still truncating instead of scaling, which means the Evotouch is subjected to a constantly varying and unknown deadband! If it was all done in the Evotouch there would be no need for truncation and it could be properly scaled and I believe it would work very well as long as it has both slope and offset adjustments that are set correctly.
Could you expand a little on what you mean by this please?
Martin.
Comment
-
-
Originally posted by paulockenden View PostIsn't that likely to just be the time delays inherent in the system?
That said, the max zone demand at the moment is 24% which matches the boiler demand. I have noticed this event too often to believe that what I am seeing is just system lag.
Comment
-
-
Originally posted by HenGus View PostAfter I posted, I went and made a cup of tea and returned about 20 minutes later. There was no change in the heat/zone % demands.
That said, the max zone demand at the moment is 24% which matches the boiler demand. I have noticed this event too often to believe that what I am seeing is just system lag.
Comment
-
-
Originally posted by blowlamp View PostCould you expand a little on what you mean by this please?
As far as I know no boiler does this. All boilers seem to set flow temperature maximums by capping the requested flow temperature - in other words say Weather compensation calculated that in 10 degree weather you only needed a flow temperature of 60 degrees, it would honour the requested flow temperature from the Evohome via OpenTherm up until 60 degrees but beyond that it would cap it to 60 degrees if the Evohome requested 70, 80, 90 degrees... this introduces a lot of deadband (yes this is a thing) where the Evohome varying the requested flow temperature doesn't actually do anything.
Worse still the amount of deadband would vary with the outside temperature as the flow temperature cap changes. This is far from optimal.
But it's even worse than this - from reports we've seen on here almost no boilers allow you to combine their weather compensation module with OpenTherm control - as soon as you use OpenTherm the weather compensation module basically gets disabled and the OpenTherm request overrides the flow temperature limit that the weather compensation would normally apply. I think we have one confirmed report of a boilers Weather compensation module and OpenTherm working together peacefully (although still with the undesirable deadband) and all the other reports are saying that they can't both be enabled at once as one overrides the other.
Doing it all in software in the Evotouch would get around all these problems - the heat demand can be scaled properly when you set a flow temperature limit in the installer menu instead of being capped which means no deadband, and if they went as far as to incorporate weather compensation (I don't think they ever will) then you wouldn't even need a weather compensation module for your boiler - it could just use the weather report temperature that is now displayed in the top left corner as the input to calculate the maximum flow temperature and then scale the heat demand to not exceed that temperature, but avoiding introducing any deadband. Win win.Last edited by DBMandrake; 25 January 2018, 02:43 PM.
Comment
-
-
Originally posted by fergie View PostIn a perfect world it would all be done as a software update to the existing controller, but if required a new evotouch, I would certainly buy it.
It's both easy to implement purely in a software update (and as Paul points out they already expose cycle rate and minimum on time for BDR91 installs, so there is precedence for having this kind of setting available) and more importantly I would argue it is actually pretty necessary for all those boilers that disable their built in maximum flow temperature setting when being controlled with OpenTherm - which is a lot of them.
Any system using OpenTherm where the boiler maximum flow temperature setting is disabled will be running very non optimally as by running at the boilers maximum temperature every time a zone is below the proportional band it will probably be experiencing room temperature overshoots and oscillation, interaction between rooms where one room coming online causes other rooms to overshoot, may not be condensing very well (if at all) and will be just unnecessarily stressing the boiler and pump by running them at maximum temperatures for a significant period of time.
One thing is for sure, if I was considering an OpenTherm compatible boiler I would not buy one that does not allow me to set a maximum flow temperature when used with OpenTherm, and if I already had such a boiler I would not bother buying the Honeywell OpenTherm bridge, I'd just stick with the BDR91.
However if they implemented this feature I would have no qualms about using Evohome OpenTherm with any (?) OpenTherm boiler.
Comment
-