    I was thinking of building an interface but decided to try and save some time and bought this one

    https://www.esera.de/produkte/ebus/1...re-hub-platine

    which took almost a week to arrive and is working fine with no problems.

    My cylinder thermostat already uses low voltage to a relay which then provides DHW/ON/OFF mains voltage signals to the 3 port valve etc.
    I should easily be able to use that low voltage to signal the hot water state to the raspberry pi and have it issue the required ebus commands at intervals.
    Changing FlowsetHcMax to the required temp looks like the most likely solution at the moment.

    Getting ebusd running on the pi and learning how to use it is an ongoing learning experience.
    Last edited by Jackthom; 27th January 2018 at 02:01 PM.

  2. #32
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,571

    Default

    You are likely missing the Definition for the SetMode message. When I get home I will dig it out.

  3. #33
    Automated Home Jr Member
    Join Date
    Dec 2017
    Location
    Northumberland
    Posts
    16

    Default

    find result includes bai SetMode and when the V65 is also in operation on the bus it can be read,

    read SetMode
    auto;10.0;-;-;1;0;1;0;0;0

    find -w doesn't show SetMode in the list as writeable so I'm guessing there must be some other way of changing it.

  4. #34
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,571

    Default

    Ok so you are close. What you need to do is turn debug on and grab the actual hex message string and the write the command as a hex string.

  5. #35
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,571

    Default

    Are you sure the HW knob on your boiler is turned up to the max i.e. the LCD will read 60C when you turn it up. The reason I ask is that you don't appear to have the HW max temperature set in the 3rd field in your SetMode command.
    Your command looks a lot like when the VR33 has no demand. What I have noticed is that some vaillant controllers set the CH flow to 0.0 for off but others (including the VR33) set it to 10.0. The VR33 never sets that 3rd field which is the most important field to set to get the boiler to start heating HW.

    See the all important commands in different scenarios.

    With HW Off CH Off
    ----------------------
    update MS cmd: 1008b5100900000078ffff45ff00 / 0101
    or update MS cmd: 1008b5100900000078ffff05ff00 / 0101

    translates to
    update bai SetMode QQ=10: auto;0.0;60.0;-;1;0;1;0;0;0


    HW On CH Off
    ----------------
    update MS cmd: 1008b5100900000078ffff01ff00 / 0101

    translates to
    update bai SetMode QQ=10: auto;0.0;60.0;-;1;0;0;0;0;0

    HW On CH On
    ---------------
    update MS cmd: 1008b5100900006478ffff40ff00 / 0101

    translates to
    update bai SetMode QQ=10: auto;50.0;60.0;-;0;0;0;0;0;0

    The 2nd field is the dynamic flow temperature set by the controller depending on various factors like room temperature, external temperature etc.

    Now using the above information you can trigger the boiler into HW mode but only until some other device doesn't come in and give the boiler another SetMode command, which happens with the VR33. The VR33 issues a SetMode every 5 seconds or so. So I've been able to confirm that my messages are read and understood by the boiler but the boiler never has time to act on my commands because the VR33 sends a new one.

  6. #36
    Automated Home Jr Member
    Join Date
    Dec 2017
    Location
    Northumberland
    Posts
    16

    Default

    Thanks Bruce that's very much appreciated, those hex values are working perfectly as supplied.
    Although I generally like finding out stuff like this for myself I was getting close to tearing out some hair.

    Similar to the VR33, the Vaillant controller was sending out a Setmode every 10 sec or so but from now it's staying OFF.
    Its interesting that while the hex is definitely switching the boiler I now can't read SetMode

    localhost: read SetMode
    ERR: no data stored

  7. #37
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,571

    Default

    Any message you write to the bus is not read and stored in memory. It's a limitation of ebusd and John, the author, knows about that.

  8. #38
    Automated Home Jr Member
    Join Date
    Dec 2017
    Location
    Northumberland
    Posts
    16

    Default

    Now that I know which messages to look for I'll take another look this evening to find the hex values being sent by my controller so the ones I send can be tailored to the flow temperatures I'd prefer.
    TBH at first glance I'm not seeing exactly how the hex values relate to the individual fields.

  9. #39
    Automated Home Legend
    Join Date
    Jul 2014
    Posts
    1,571

    Default

    Study the way the message definitions and the various data types are put together and it suddenly starts making sense. That SetMode message started with my contribution a while ago and has grown since. But there are still a few bits and bytes that aren't translated and ignored.

  10. #40
    Automated Home Jr Member
    Join Date
    Dec 2017
    Location
    Northumberland
    Posts
    16

    Default

    What’s puzzling me now is I can’t see how or even where SetMode is defined in the csv files loaded on automatic configuration.
    Clearly there must be a definition that describes the conversion from hex bytes to decoded message, so far I haven’t found it.

    I suppose that if the decode is incomplete it might be difficult to reverse the process and construct a viable hex message from a given set of parameters.
    Last edited by Jackthom; 27th January 2018 at 10:00 PM.