Originally posted by DBMandrake
View Post
All radiators either on or off
Collapse
X
-
-
-
Originally posted by HenGus View Post
Comment
-
-
Originally posted by DBMandrake View PostAgreed, 10 minutes is too long. Try a hot water overrun of 1 minute or at most 2 minutes. I still don't think a long overrun could cause an overshoot of nearly 20 degrees though, as the boiler would be off during the overrun...
Comment
-
-
Originally posted by G4RHL View PostKeep it at 60c. It does not have to be on long, but that of course depends on use. Mine is on for an hour in the morning and 30 minutes at night and I find it quite sufficient. There is always cold water to cool it down. Currently my app says the tank temperature is 35c. It will come on at 18:00 for 30 minutes but I know it will be up to 60c in a very short time.
Comment
-
-
Originally posted by willdonal View PostThanks, I have turned the temperature up :-) :-) I have it coming on for and hour in the morning and an hour at night. Perhaps this is a bit of an overkill if you say you only have it on for 30 minutes at night
Occasionally, I might have a shower in the evening and there is still more than enough hot water in the cylinder without re-heating it first.
Comment
-
-
Originally posted by HenGus View PostI think that the ON time demands on your needs and HW usage. My system is set up for HW priority. HW heating comes on at 6am (actually 5.57 as the Evohome clock is 3 minutes out). To get the cylinder up to 60C takes 40 to 45 minutes with my boiler flow TMax Set at 70C. The ON demand window closes at 8.30am which means that if either my wife or I have a bath/shower in the morning, the cylinder will re-heat to 60C.
Occasionally, I might have a shower in the evening and there is still more than enough hot water in the cylinder without re-heating it first.
Comment
-
-
Good morning everyone, After the trial and tribulations the heating is working as advertised and I even have it programmed in to alexa so by saying 'alexa turn living room up to 25' Alexa then turns the temperature up. Brilliant this modern technology. However I still have one problem and that is the hot water. It has gone from been hot to taking the skin off your hands hot. This morning the evohome controller was reading 77 even though I have the water set to 50 on the controller. As someone has said earlier it could be that the water is been heated when the heating comes on. I have checked and the relay box green light for the water does not come on when the heating is on. Only the green light for the heating relay box comes on. I need help before I give myself third degree burns. If someone does suggest a reset and rebind then can you tell me exactly how to do the full reset on the wireless relay box and the hot water box/thermostat. thank-you :-) :-) :-)
Comment
-
-
There is a possibility that your HW BDR hasn’t been wired in correctly. The cylinder temperature should never get above the temperature set on the cylinder thermostat irrespective of what Evohome is demanding. I posted a link to the Honeywell video on clearing the binding on a BDR. It involves a 15 sec button press on the BDR.
See the advice here:
Have you checked that the zone valve isn’t stuck in the open position?Last edited by HenGus; 4 October 2017, 10:48 AM.
Comment
-
-
Originally posted by HenGus View PostThere is a possibility that your HW BDR hasn’t been wired in correctly. The cylinder temperature should never get above the temperature set on the cylinder thermostat irrespective of what Evohome is demanding. I posted a link to the Honeywell video on clearing the binding on a BDR. It involves a 15 sec button press on the BDR.
See the advice here:
Have you checked that the zone valve isn’t stuck in the open position?
Comment
-
-
Originally posted by willdonal View PostHello Hengus, reading the above link it states that the wireless relay boxes must be at least 300mm apart. as can be seen from the picture they are right next to each other. Could this have caused the problem? When the installer fitted everything he made all 3 valves to be permanently open, 1 valve controlled downstairs heating, 1 was for upstairs and the 3rd was for the hot water. Could be the problem? The picture shows the 2 boxes plus the blanking plate to where the heating control box was. Thanks[ATTACH=CONFIG]1090[/ATTACH]
If the Hot water zone valve has been wired to be permanently open then you have found your problem - of course the hot water will get too hot as soon as the boiler is running. Kind of hard to believe that the installer would make that sort of schoolboy error ?
If so, what is the hot water BDR91 wired to ? Nothing ? The hot water zone valve needs to be under the control of the hot water BDR91 or the system will have no control over hot water temperature at all. It's also worrying that you don't seem to have a safety thermostat for the cylinder (usually wired in series) functioning either - if you did it wouldn't get as high as 77 - that is hot enough to cause burns and is of grave concern especially if you have children in the house. This seems to be bordering on negligence and incompetence on the part of the installer if this is true.Last edited by DBMandrake; 4 October 2017, 12:19 PM.
Comment
-
-
Originally posted by DBMandrake View PostYes, the relays should be 300mm apart so they don't interfere with each other causing unreliable wireless comms and this should be sorted out, however this is probably not your specific issue.
If the Hot water zone valve has been wired to be permanently open then you have found your problem - of course the hot water will get too hot as soon as the boiler is running. Kind of hard to believe that the installer would make that sort of schoolboy error ?
If so, what is the hot water BDR91 wired to ? Nothing ? The hot water zone valve needs to be under the control of the hot water BDR91 or the system will have no control over hot water temperature at all. It's also worrying that you don't seem to have a safety thermostat for the cylinder (usually wired in series) functioning either - if you did it wouldn't get as high as 77 - that is hot enough to cause burns and is of grave concern especially if you have children in the house. This seems to be bordering on negligence and incompetence on the part of the installer if this is true.
Comment
-
-
Originally posted by Dan_Robinson View PostThat picture is a disaster waiting to happen.
I predict that it will end up in a PowerPoint presentation in bracknell soon
thanks for you expertise and help :-) :-)
Comment
-
-
Originally posted by willdonal View PostThe BDR91 is connected to the thermostat that came with the hot water pack and is connected to the tank.
That would explain why the temperature was 77 this morning when I had the heating on, now the heating is off the temperature has dropped to 60.
As I had 3 zones would it be ok just to wire up the water valve and leave the two heating valves open?
Another option would be to wire both heating zone valves together to run off your heating BDR91 which would make it a standard S-Plan configuration. The advantage of this is that if you have any radiators without an HR92 like a towel rail, they would not get hot when only hot water is turned on - if the heating zone valves are always open when the system is on you will get some heat to towel rails in summer when only hot water is enabled.
Some people like that idea, some don't. I have HR92's on all my radiators and also (somewhat redundantly) a heating zone valve as well, so I don't get any radiators heating at all if I only have hot water enabled.
The hot water zone valve of course does need to be wired to both the hot water BDR91 and the cylinder safety stat if it has one. (If its unvented it will definitely have one, vented may not)
Unfortunately the installer had never installed one of these systems before but he did contact Honeywell for advice and so I assumed he had done it properly. we live and learn :-) :-)
In such a system the hot water zone valve is always what regulates the hot water temperature - previously it was probably controlled with a cylinder stat and a timer, now it is controlled by the hot water BDR91. (And a temperature reading from the Evohome cylinder sensor is sent back to the Evohome controller wirelessly so it knows when to switch that relay on and off)
Leaving the hot water zone valve wired or held open wouldn't be something you'd ever do on an S-Plan system.Last edited by DBMandrake; 4 October 2017, 01:49 PM.
Comment
-
-
Originally posted by willdonal View PostHi Dan, Didn't think it looked too good. I have now contacted an official Honeywell installer who is going to come next week and sort it all out. It is way beyond what I can do myself.
thanks for you expertise and help :-) :-)
Comment
-
Comment