Is your old boiler a modulating boiler or does it only have an on/off flow temperature thermostat as mine does ?
If so, keep in mind that the boiler is already cycling on and off every few minutes to maintain the flow temperature. Just because your wall thermostat is on constantly doesn't mean the boiler is. The burner will run constantly during the initial system heat up but once the radiators are up to temperature and the boiler can hit the flow temperature target it will be cycling on and off every few minutes anyway, probably with a differential of about 8 degrees if it is an old mechanical flow thermostat. (I've retrofitted a digital flow stat onto my boiler to get more accurate and repeatable flow temperature control as well as allowing me to see what it is)
In this situation the additional TPI switching of the BDR91 doesn't result in that much more switching per hour (in general) it just ends up modifying the proportion of on time, since both BDR91 and flow stat have to cycle on at the same time for the burner to fire (logically AND'ed) so if their cycle times are about the same, total number of switches per hour will be only a little bit higher statistically. (I've measured it) If TPI was so damaging for boilers I don't think all the manufacturers would have moved to it.