Originally Posted by
DBMandrake
Something not right there... Any time the window function activates it you should get a window icon displayed in the zone on the controller and the set point will be shown as 5 degrees and in obvious blue. The phone app unfortunately does not have a window icon, however it will show the set point has changed to 5 degrees, and it will appear as if there is no override. (no override icon) If both are still showing the original set point instead of 5 degrees then it seems that the message from the HR92 reporting it went into window mode is not getting through to the controller.
Are you sure you didn't disable window mode in the zone configuration in the controller ?
There are several settings:
11-Win type. 0=window mode disabled, 1=window mode enabled using the built in temperature sensor, (default) 2=window mode enabled using the remote window sensor switch.
3-Win time. How long window mode remains active if the temperature stays cold - 30, 60 or 90 minutes, before going back to the previous set point.
4-Win Dec. How many degrees the temperature has to drop in a short space of time before triggering window mode. 0.2 - 2 degrees. Defaults to 0.6 degrees. I can't find any reference to what period of time is considered to be a "short time" but it's probably around 4 minutes. If you increase this value you make window detection less sensitive as it needs a greater drop in temperature to trigger it
5-Win Inc. How many degrees the temperature must rise again in a short period of time before window mode is cancelled early. (Before the timeout set in option 3) Defaults to 0.2 degrees. If you close an open door and this triggers the measured temperature to increase by 0.2 degrees or more in a "short time" window mode is cancelled immediately. Increasing this value makes it less sensitive to cancelling window mode.
If you want to desensitise window mode but leave it enabled so it works when a door or window is left wide open, increase the value in option 4 - I've done this in a few specific locations that were tripping too easily but where I still wanted it to activate if for example the back door was left wide open for a while. If you want to disable it altogether set option 11 to 0.