When you set the heating to off the low temp is passed to the HR92s (or whatever) sometime over the next five minutes. They then screw their valves down, then report back zero heat demand to the controller. Only when all zones are reporting zero will the controller tell the boiler relay to stop demanding heat.
In other words, it can take a few minutes - even longer if a transmission gets lost.