  1. #21
    Automated Home Jr Member
    Join Date
    Nov 2017
    Posts
    12

    Default

    Quote Originally Posted by Felkin123 View Post
    So had a fiddle (technical term) reset rebound the water BDR specifying hot water valve only and the system has sorted itself out once up to temp the Vogue ticks over at 33-45 keeping the pump running and kicking in the burner/fan on 25% for about 20 seconds every 5m or so which maintains the 19 degree set point in the living room. Iíve noticed that this method sends less hot water round the bypass and maintains the setpoint more accurately. When the water demand kicks in Iíve had minor overshoots but Iím not sure they are any more so than when it was using switched live /full power. And itís been much milder the last few days. Have to say first impressions of OT in Evohome are very good indeed !
    Correct me if I'm wrong but burning for 20secs then cycling isn't what opentherm does.

    What you have is the boiler going into anti cycle because there's not enough load to dissipate the minimum fire/modulation of the boiler.

    There's a guy on here who had the same issue with the vouges.

  2. #22
    Automated Home Ninja
    Join Date
    Mar 2017
    Posts
    295

    Default

    I was also under the assumption too that there was a lot of issue with Opentherm and Ideals, as said above there is one guy on here who has had endless amounts of issues with them.

  3. #23
    Automated Home Jr Member
    Join Date
    Dec 2015
    Posts
    26

    Default

    Anti cycle ? Surely the boiler is circulating warm water around the radiators and ABV and firing on minimum when required ? Before it would fire on full then switch off with a few minutes of pump over run through the ABV. To my mind the current scenario is better in all ways. It does switch off sometimes when no heat is called. So what should it be doing ? What behaviour should it be exhibiting?

  4. #24
    Automated Home Jr Member
    Join Date
    Nov 2017
    Posts
    12

    Default

    Anti cycle is a timed pump overrun without burner to shed heat, it's doing this because it can't modulate any lower and has to turn the burner off to protect the boiler.

    On my vokera anticycle is 3 mins,

    What you have explained above is that the vouge will run at 20% every 5 mins for 20 seconds then turn off and go back into pump overrun.(anti cycle).

    The whole point of opentherm is that the boiler modulates at a flow temp that it needs for the circumstances, but what is happening is your boiler can't modulate any lower (maybe due to only 1 room needing very little heat) and simply can't burn any lower flow temp.

    I'd hazard a guess that the boiler is oversized for the load and it's cycling because only 1 room is needing very slight amounts of heat.

    The reason cycling is inefficient is because when the boiler fires it will normally run at 75% (my vokera) for the initial startup, and every time it does this it's using and wasting gas to get going again,

    there's also argument about components being used more from a wear and tear point but given how many times tpi starts and stops the boiler in a given hour I doubt it's relevant with evohome.

    I thought the whole point of opentherm was to keep a slow burn, rather than on and off like tpi does?

    Hopefully dbmandrake will chime in to put me right, as it's all my assumption and I'm not trained at all in this stuff.

  5. #25
    Automated Home Jr Member
    Join Date
    Nov 2017
    Posts
    12

    Default

    https://youtu.be/L8CcL7SafpE

    Here's the video from a fellow member on here regards to short cycling, is this what yours is doing?

  6. #26
    Automated Home Jr Member
    Join Date
    Nov 2017
    Posts
    12

    Default

    And here's said thread about vouge not modulating down and cycling.

    http://www.automatedhome.co.uk/vbull...wired-version)

  7. #27
    Automated Home Jr Member
    Join Date
    Dec 2015
    Posts
    26

    Default

    Yes thatís what mine is doing. His is at a set point of 14 degrees. Mine is exactly as you suggest not able to modulate the burner down low enough for it to be on to maintain the setpoint in one room. So it circulates hot water WITHOUT the burner. To my mind this is a good thing and an improvement over the previous TPI setup. Especially as the pump is included in the 10 year warranty should it fail. I did read some of the other thread you posted but life is too short to read all sorry if the OP is reading this but 8 pages 😀.

  8. #28
    Automated Home Jr Member
    Join Date
    Nov 2017
    Posts
    12

    Default

    My non opentherm vokera does it, I get it mainly when I'm heating the office only, but like you say it's not the end of the world, there's still heat being pumped round.

    I've toyed with opentherm and weather compensation, but to be honest when I replumbed our house I oversized every radiator by 3 times with double convectors.

    So my 24kw Combi is set to a max flow of 55c even in minus 4c temps outside, if I fitted weather comp sensor it would be trying to push 60plus flow no matter how low I set the heat curve.

    Sometimes I think there's a finite amount to be saved once you have decent controls already.

  9. #29
    Automated Home Legend
    Join Date
    May 2014
    Posts
    988

    Default

    Likewise. Once the zones are up to their set temperatures, then it is often the case that the pump is just circulating hot water around the system when there is just a single zone requiring some heat. In my case, this is usually my hall/landing/stairs zone. On the coldest days this Winter, I have seen settled flow/return temps of 52/47C which over the past couple of warmer days has been in the range 43/36C. FWiW, my zones not in use are set at 13C. Under OT, I am seeing some initial temperature overshoots with optimum start but, once settled, the temperatures hardly vary. I resist the temptation to fiddle as fiddling invariably results in a high flow temperature/high gas usage.