HenGus
When I set up my Evohome for Opentherm use, the HW kit was bound under STORED HOT WATER; that is, a CS92A bound to BDR, and BDR bound to Evohome. I cannot speak for Intergas boilers but the Atag needs to receive feedback that there is a hot water demand. Normally this is via a diverter valve. In my case, I have the standard motorised HW zone valve and an inline open motorised valve that closes whenever the HW zone valve opens. The risk of getting this set up wrong is, with some boilers, that when Opentherm demands 90C for HW re-heating the boiler flow temperature will shoot off in this direction. With my set up, the boiler itself limits the max boiler temperature for HW re-heating to 70C - irrespective of what Opentherm demands - as set in the boiler profile. If I recall, the Viessmann 100 is something of a 'bad boy' in this respect.