    Default Flashing red light on BDR

    Hi

    Got a weird problem...

    I've recently changed from:-

    Generation 1 EvoHome + WiFi Bridge + 2 x BDR (Y Plan)

    to

    WiFi Evohome + Opentherm Bridge + Single BDR (Hot Water Only Valve)

    Everything is working perfectly. No comms errors, hot water valve opening and closing as it should. Yet despite this, the red light is illuminated on the BDR. I've done the full reset (long press) and re-bound it a couple of times. Still the light is red.

    Any thoughts?

    Steve

  2. #2
    Automated Home Legend paulockenden's Avatar
    Join Date
    Apr 2015
    Location
    South Coast
    Posts
    1,602

    Default

    I've had that when I thought I'd held the button for 15 seconds but somehow c*cked it up. So the BDR91 has the new binding, but also retains the original binding.

    Try the full reset again. It's obvious when it has worked because the LED flashes differently to the normal 5 second press.

    P.

  3. #3
    Automated Home Legend
    Join Date
    Sep 2014
    Location
    Scotland
    Posts
    1,843

    Default

    Constant red light means the BDR91 has lost comms for over an hour. What error does it report in the Fault Logbook ?

    When you say you've done a full reset, you held the button for at least 15 seconds until the light changed from a slow flash to a fast flash ? Only then are previous bindings cleared.

    If it still has a binding to the old controller this is the most likely cause of the error.

    I'm going to assume that the redundant BDR91 has been disconnected and removed so it isn't interfering ?

  4. #4
    Automated Home Jr Member
    Join Date
    Mar 2015
    Posts
    33

    Default

    Nothing in the fault logbook - all working fine.

    I think you're both right - an old binding is still in there.

    I'll try the long press again although I'm sure I saw the fast flash - perhaps not.

    Yes, the redundant BDR has been removed from the system - that's going to be used to control the UFH in about a month's time.