If you combine the kids bedrooms (I assume you mean three bedrooms, to save on two zones ?) then as long as you set the zone to be a "multi-room" zone, it will work fine. They will all share the same schedule but they will each measure their own room temperature at their own radiators so work independently to maintain the same temperature in each room. (A standard single room zone with multiple HR92's only uses a single temperature sensor which naturally isn't workable across separate rooms)
The control panel will only be able to display the temperature of one of those three rooms, the other two will not be visible except on the HR92's themselves if you have them set to room temperature display mode. (The other two will be able to call for heat though) If you make a manual override to the zone via the controller or phone app it will apply to all three rooms. If you override the temperature by turning the dial on one of the three HR92's it will override only that one room and only until the next scheduled set point. In a multi-room zone any override made directly at an HR92 will not be displayed on the control panel however.
Yes, assuming the cables for the three zone valves all come back to the same place (your wiring centre) then you can just wire all three of them in parallel to be controlled by one BDR91 and they will switch together in unison. The HR92's themselves will provide the zoning on an individual room basis, so effectively having three heating zone valves is redundant, but not an issue as they will just open and close together with HR92's having final authority on which rooms are being heated.Will moving to Evohome pose a challenge for me because I have three zones? I want these all combinined to one big 'master' zone and then 12 'virtual' (Evohome) zones. Can I just wire all three zones together (so they're either all on or all off)?
If the H47XL controls both heating and hot water zone valves, then it would have two relays inside it, and this would be replaced by two BDR91's, (spaced at least 30cm apart for wireless signal reasons) one for the heating zone valve(s) and one for the hot water zone valve. You get a BDR91 in the starter kit and another one in the hot water kit so you will get two. BDR91's are a simple SPDT (single pole double throw) volt free relay that can supply up to 3 amps and can be used either at 240v AC or at low voltages as required.Assuming I can, I think I need the following shopping list:
1 x ATP921R3100 - starter kit (controller, plus BDR91)
18 x HR924UK
1 x ATF500DHW
Is that everything?
Will the BDR91 sit in place of the H47XL?
In this two relay scenario you would rely on the switch inside the hot water and heating zone valve relays to fire the boiler - this is probably how your system is wired now but you might want to check. As an alternative you can have a third BDR91 which acts only as a boiler control relay which is wired directly to the boiler - this is the configuration I have at home.
The hot water kit comes with a strap on sensor for vented and an insertion sensor for unvented - so there needs to be a pocket about 1/3rd of the way up the cylinder that will accept the sensor, and this needs to be in addition to the safety cutout sensors for an unvented cylinder that needs to remain in service as well.
Presumably they are wired in series with each heating zone valve - in which case yes, you would remove them. You'd either need to bypass them in the wall box or disconnect the wiring and bypass it elsewhere.Can I just remove the three thermostats and blank them off? (i.e. they're now surely totally redundant)
You can put HR92's on every radiator in the house if you want (that's what I have) provided that there is an automatic bypass valve installed in the system - before the heating zone valves, so that there is somewhere for the boiler flow to circulate in the event that all HR92's are closed, which can happen for a short time such as during boiler overrun when the system is shut down.For the rads which currently have no TRVs, with Evohome am I ok to put on the HR924UKs so EVERY rad in the house is smart?
Sort of. It's basically a whole separate system which means you'd have to duplicate the heating zone valve relay (you'd have another BDR91 belonging to the second unit for the heating zone valve) and you could only control some zones from one controller and some from the other. There would be no house-wide modes such as away - you'd have to put both into away mode etc.If I wanted to have 14 zones, would I 'just' need another controller?
Personally if you're only two zones over the limit I'd work to consolidate some less critical zones like hallways or zones that can share schedules using multi-room zones rather than go the two controller route.
That's certainly a big purchase - I have 9 TRV's in my system and I built it up over time. So best to get some other opinions as well in case I've missed something or got something wrong.Thanks in advance, obviously 18 x TRVs hikes the price up but I want to go the whole hog (don't understand the point of not doing it properly) - I just want to make sure I've left no stone uncovered before proceeding. I'll probably get my friendly Spark to fit it but I think it'll be the first Evohome he's done.![]()