Not for the first time, my Evohome system is driving me nuts.
As i understand it, if you set a 'local' override on one of the HR92 radiator valves (that is, by turning the knob on the radiator valve itself) then the new temperature should apply until the next setpoint in the programme.
In other words, if at 9.30 I turn the radiator knob up to 21deg, and my daily programme sets the temperature as 15deg from 10.00, then the HR92 should target 21deg until 10.00 and then revert to the programmed 15deg.
Is that right?
This seems to happen fine in two of my zones, but not the third. Come the 10.00 setpoint, it simply stays at 21deg. It stays there until I either change it locally again, or do a manual override from the main controller. If I do a manual override from the controller, then everything works as it should: that applies until the next setpoint and then it reverts to programme.
I've tried:
- resetting and rebinding the HR92
- deleting the 'trouble' zone, making a new one, rebinding to that
- swapping the HR92 itself with one from another zone (the problem persists in the same zone, so it seems that the zone is the problem, not the particular HR92)
- moving the location of the controller (eventually to within 2m direct line of sight of the HR92)
None of this helps.
The HR92 can communicate with the boiler relay, because turning the local control brings the boiler on almost immediately.
The HR92 seemingly can send signals to the controller, because the controller seems to receive and display the measured temperature from the HR92
The HR92 seemingly can recieve signals from the controller because it responds to the programme setpoints fine when there *isn't* a local override active
The controller can communicate with the boiler relay fine because everything else works.
I'm baffled... any ideas?
As i understand it, if you set a 'local' override on one of the HR92 radiator valves (that is, by turning the knob on the radiator valve itself) then the new temperature should apply until the next setpoint in the programme.
In other words, if at 9.30 I turn the radiator knob up to 21deg, and my daily programme sets the temperature as 15deg from 10.00, then the HR92 should target 21deg until 10.00 and then revert to the programmed 15deg.
Is that right?
This seems to happen fine in two of my zones, but not the third. Come the 10.00 setpoint, it simply stays at 21deg. It stays there until I either change it locally again, or do a manual override from the main controller. If I do a manual override from the controller, then everything works as it should: that applies until the next setpoint and then it reverts to programme.
I've tried:
- resetting and rebinding the HR92
- deleting the 'trouble' zone, making a new one, rebinding to that
- swapping the HR92 itself with one from another zone (the problem persists in the same zone, so it seems that the zone is the problem, not the particular HR92)
- moving the location of the controller (eventually to within 2m direct line of sight of the HR92)
None of this helps.
The HR92 can communicate with the boiler relay, because turning the local control brings the boiler on almost immediately.
The HR92 seemingly can send signals to the controller, because the controller seems to receive and display the measured temperature from the HR92
The HR92 seemingly can recieve signals from the controller because it responds to the programme setpoints fine when there *isn't* a local override active
The controller can communicate with the boiler relay fine because everything else works.
I'm baffled... any ideas?