Originally Posted by
kevinsmart
I have a single zone twin loop UFH setup controlled via Y87RF and BDR91 in my new well insulated extension. BDR91 activates the pump and manifold valves are left open.
As it’s in combination with 26 rads, there is a thermostatic mixing valve to reduce the flow temperature. Boiler is Intergas HRE40 SB with OpenTherm module, and an outdoor sensor (unfortunately weather compensation doesn’t work with Evohome OpenTherm support though).
I’m not happy with the UFH setup for a few reasons:
1. The mixing valve intermittently emits a high pitched whine, appears to be when the flow temperature matches its set point.
2. Wife complains about 1!
3. Poor temperature control. Evohome indicates a 40-60% demand for the zone even when the set point is reached, as a result there is an overshoot. Optimum start typically pre-heats for 1.5 hours, temperature increases to more than 1 degree above the set point after a few more hours, still with <20% demand, then optimum stop kicks in 1 hour before set back. I’ve tried reducing the mixing valve set point temperature but Evohome seems unable to adapt.
Primarily because of 2, I’m going to replace with an HM80 controlled rotary actuator and flow temperature sensor. I hope this will work better with OpenTherm and provide more accurate temperature control.