I thought people might find it useful to hear about my experience...
I bought my Evohome system 2.5 years ago. Followed the binding instructions carefully due to dire warnings on this site and elsewhere. All went fine.
Since then a couple of the HR92 have failed. One was chewed off by the dog (who is older and wiser now I hope). The other was damaged by water leaking from a defective TRV body.
As a "temporary" fix I just replaced them with the old TRV heads. The controller has shown a little warning triangle against both zones ever since.
Recently I had a new radiator installed, and the leaky TRV replaced. So finally got round to replacing the other two as well as adding an HR92 to the new rad,. I read advice on here about various ways to remove all traces of previous bindings (eg delete the zone; clear binding from any HR92 to be re-used etc etc.)
One of the HR92's bound fine to its new zone.
BUT the other two turned into a bit of a nightmare. I tried umpteen different ways but kept getting the same result - the binding process would appear to go absolutely fine, but then the little red triangle would immediately appear saying there was a comms error with the actuator. RF check was fine. Also the controller & HR92 seemed to communicate just fine (easy to test by changing target temperature). So the system actually worked ok - but I couldn't get rid of the pesky error symbols.
Today I rang up the Evohome Shop, and they helped me sort it out in just a few minutes...
Turns out the binding process was fine (as it appeared to be) - the problem lay in the fault log itself.
He suggested I clear the fault log and the error symbols instantly disappeared!
As I understand it the log contains FAULT records from when a problem occurs. Then if it automatically resolves the problem it will create a corresponding record (RECOVER? RESOLVE? I can't remember exactly what it said). If there is an unmatched FAULT in the log it will continue to display the warning symbol. This is a nice idea - unless it gets out of synch. I guess the problem was caused by me throwing the broken HR92's away but not clearing down the log. You would expect this to get tidied up when a zone is deleted - but somehow it got its knickers in a twist.
Anyway problem appears to be solved now!
I hope this helps save someone from the hassle and frustration I went through till 3am last night!
I bought my Evohome system 2.5 years ago. Followed the binding instructions carefully due to dire warnings on this site and elsewhere. All went fine.
Since then a couple of the HR92 have failed. One was chewed off by the dog (who is older and wiser now I hope). The other was damaged by water leaking from a defective TRV body.
As a "temporary" fix I just replaced them with the old TRV heads. The controller has shown a little warning triangle against both zones ever since.
Recently I had a new radiator installed, and the leaky TRV replaced. So finally got round to replacing the other two as well as adding an HR92 to the new rad,. I read advice on here about various ways to remove all traces of previous bindings (eg delete the zone; clear binding from any HR92 to be re-used etc etc.)
One of the HR92's bound fine to its new zone.
BUT the other two turned into a bit of a nightmare. I tried umpteen different ways but kept getting the same result - the binding process would appear to go absolutely fine, but then the little red triangle would immediately appear saying there was a comms error with the actuator. RF check was fine. Also the controller & HR92 seemed to communicate just fine (easy to test by changing target temperature). So the system actually worked ok - but I couldn't get rid of the pesky error symbols.
Today I rang up the Evohome Shop, and they helped me sort it out in just a few minutes...
Turns out the binding process was fine (as it appeared to be) - the problem lay in the fault log itself.
He suggested I clear the fault log and the error symbols instantly disappeared!
As I understand it the log contains FAULT records from when a problem occurs. Then if it automatically resolves the problem it will create a corresponding record (RECOVER? RESOLVE? I can't remember exactly what it said). If there is an unmatched FAULT in the log it will continue to display the warning symbol. This is a nice idea - unless it gets out of synch. I guess the problem was caused by me throwing the broken HR92's away but not clearing down the log. You would expect this to get tidied up when a zone is deleted - but somehow it got its knickers in a twist.
Anyway problem appears to be solved now!
I hope this helps save someone from the hassle and frustration I went through till 3am last night!