    Mains power meters

    Hi.
    I have some non invasive clamp on power meters that I use to read mains current. I wanted to put one on each ring mains in my house so I can see localised power consumption.

    Something I don't understand is, if I put a clamp meter on single ring mains what stops me sensing the current on all the other ring mains for the entire house? Will I sense current beyond the MCB isolating that ring?
  • toscal
    Moderator
    • Oct 2005
    • 2061

    #2
    Interesting.
    I know when you are testing a single ring circuit you are supposed to turn off the others, to avoid for want of a better word cross contamination. One way would be to put in a din rail mounted energy meter after the circuit breaker for the ring, then clamp on the output side of this. Or use the blinking led to measure power consumption.
    IF YOU CAN'T FIX IT WITH A HAMMER, YOU'VE GOT AN ELECTRICAL PROBLEM.
    Renovation Spain Blog

    Comment

    • paulockenden
      Automated Home Legend
      • Apr 2015
      • 1719

      #3
      You only sense the current passing through the clamp or CT.

      Think of it a bit like measuring water flowing through a pipe and it might make more sense.

      Ring mains make things complicated.
      Last edited by paulockenden; 21 June 2019, 02:09 PM.

      Comment

      • Joe2003
        Automated Home Lurker
        • Jun 2019
        • 3

        #4
        Originally posted by paulockenden View Post
        You only sense the current passing through the clamp or CT.

        Things of it a bit like measuring water flowing through a pipe and it might make more sense.
        Ah! This explains why you only receive an appliances power usage as the power cable is basically a spur.

        Thanks for the help.

        Comment

        • paulca
          Automated Home Jr Member
          • Jul 2019
          • 31

          #5
          Something I was also looking into recently. Unfortunately you can't really just take the current output from the clamp and multiple it by your mains voltage to get power. This will give you a badly inaccurate figure. Simply because you are dealing with AC power. Nor infact can you even sample the current from the clamp and report the current being drawn. it doesn't work that way.

          To get true RMS current you need to sample the current waveform from the clamp many times per cycle, so, for example, assuming 50Hz mains, you might want to sample it at 500Hz or 1Khz. You need to take the RMS, Root, mean, square of those values. That will give you RMS current. It should be noted if you just add average the current over the waveform you will get 0 amps as half the current is negative. The squaring at the end ensures an ABS value, ie. positive.

          Then if you want a power value in watts it gets even more complicated as the voltage is also moving and here's the catch... it will not necessarily be "in phase" with the current. If you have any capacitive or inductive loads, such as motors (inductive) or high power devices with capacitors the current and voltage will be shifted out of phase. So you can't assume the voltage waveform from the current waveform. Smart meters which do this with just a current clamp are inaccurate and are assuming the voltage and current are in phase and that your mains voltage is exactly 240V RMS when it probably won't be. In the UK it can be anything from 230V to 250V.

          Thus, you need to measure the mains voltage as well. It also needs to be sampled and RMS'd. Only then can you get an accurate reading. Note, simply RMS'ing the current and assuming the voltage is in phase and guessing it to be 240V RMS, you might get within 10%.

          Measuring the mains voltage from a micro-controller or raspberry pi is not that easy either. You will need to step it down to something safe using a AC/AC wall adapter power supply, for example, that gives you maybe 9V AC. You need to buy one that has a good datasheet or somehow workout the phase shift caused by it's transformer and account for that shift in your calculations.

          All this said, I decided to not bother attempting to make all this myself and instead am looking at buying one of these:


          It has a MODBus interface which is fairly easy to integrate with via an RS485 to serial adapter and an arduino/esp or raspberry pi.

          If you hunt around I'm sure you will find plug in variants with some form of hackable interface.
          Last edited by paulca; 29 July 2019, 04:18 PM.

          Comment

          • paulca
            Automated Home Jr Member
            • Jul 2019
            • 31

            #6
            Also, just a quick, but VERY important warning about current clamps.

            NEVER EVER put the clamp around a live wire with it unloaded. Without a burden resistor on a current clamp (transformer) the voltage across the transformer ends can reach many thousands of volts and in the best case fry whatever device you then connect to it and in the worse case give you a nasty shock.

            Comment

            • MichaelD
              Automated Home Guru
              • Mar 2006
              • 167

              #7
              Originally posted by paulca View Post
              Also, just a quick, but VERY important warning about current clamps.

              NEVER EVER put the clamp around a live wire with it unloaded. Without a burden resistor on a current clamp (transformer) the voltage across the transformer ends can reach many thousands of volts and in the best case fry whatever device you then connect to it and in the worse case give you a nasty shock.
              This sounds like a very important piece of advice, unfortunately I don't understand it at all.

              What is an unloaded clamp, and what should we do to load it? Could you put this in more everyday terms? I have some devices that measure elec usage using clamps, I open the clamp, wrap it round a wire, shut the cupboard then go back every year or so to change the battery. Should I be doing something differently?

              Comment

              • Peterl3986
                Automated Home Lurker
                • Sep 2019
                • 3

                #8
                When CTs are fitted onto live cables they build up a current on their connecting cables. It is always advised to do the connections when the cable your wanting to read is dead.

                Comment

                • Paul_B
                  Automated Home Legend
                  • Jul 2006
                  • 608

                  #9
                  If you haven't already then have a look at OpenEnergyMonitor. The main unit, EmonPI, is based on a RaspberryPI and comes with two CTs with burden resistors, the unit has AC sampling to follow the AC frequency and give more accurate measurements. If you need to add more CT then you can add on EmonTX that provide an additional 4 clamps per unit.